Removal of Fire Safety Equipment
Flat internal doorways (other than toilet/bathroom) have to be fire doors (FD30 and in the old days FD20 when such doors existed) even as single private dwellings, they just do not need self closers. P50 extinguishers are not maintenance free, that's sales talk - they require annual maintenance, but rather than using an extinguisher service company the owner of the equipment can complete it themselves - https://www.britannia-fire.co.uk/wp-content/uploads/2025/05/How-to-maintain-the-P50-.pdf
-
Wholesale replacement of Fire Doors
You need to elevate this to a First Tier Tribunal as it sounds excessive and not justifiable. Your FRA and F Door Inspection seem to side with you as does the official Government Guidance. If this isn't enough to overturn the s20 replacement you may need a report detailing what compliant repairs in line with the FRA are viable, but this cost is dwarfed by the amount you will all have to pay. Leaseholders can and do win Fire Safety FTTs, I have been involved in these before, it's worth a try. The agent will benefit from a full replacement through the s20 management fee process so they are bound to prefer it- after all its not their money!
-
Removal of Fire Safety Equipment
If it's provided in a premises to which the FSO applies the law clearly states in Article 17 it must be subject to a system of maintenance. If it doesn't apply because its now a private dwelling again it doesn't but from a liability point of view it might be wise to dump it other than the fire blanket
-
Removal of Fire Safety Equipment
In theory as long as you return it to the original condition as single dwellings with the fire doors as originally required (especially the front doors if to internal common parts) and have the correct minimum type and grade of automatic fire detection for the part of the UK your flat is in then, as they are outside the FSO and only under the Housing Act and subsidiary legislation (such the various UK countries' rental smoke alarm regulations) as you are not making it worse than the original Building Regs approval
-
Legal requirements for a Fire risk assessment.
I'd agree with the above - are you being asked for one by someone (e..g insurers?)
-
Fire risk assessments on unoccupied residential buildings.
Because they don't understand the law. There is no such thing in law as a pre-occupancy FRA, this matter is controlled by Building Regulations separate fire safety requirements. However it is true that Building Regulations only cover a small part of the fire safety regime required for an occupied building and if the Responsible Person does not have the knowledge or competency as to the management of a building (training, maintenance, policy & procedures etc) and the aspects not covered by Building Regulations (signage, extinguishers, etc) then they need guidance and steering. From this the lucrative pre-occupancy FRA is born. You can't do a proper FRA on an empty building & it becomes worthless the moment the first people, furniture & equipment are moved in, so you need to quickly do it again. General consultancy & a pre-occupation checklist achieves the same thing (& would cost less) but instead an FRA is being requested as a quasi 'certificate of occupancy' which it isn't intended to be.
-
Do fire alarms have to be linked to fire brigade?
That's poor - whilst it's not legally mandated (other than in Scotland) it's accepted that it is appropriate as one of the findings of the inquiry into the Rosepark Care Home fire in 2011 where 14 people died was that the lack of ARC monitoring and reliance on staff raising the alarm in part contributed to the deaths and that ARC monitoring should be provided. Any decent FRA would as a minimum suggest that such monitoring be fitted even if not a high priority rating in the report. To not even mention it is unwise and shows a lack of consideration of sector specific technical progress.
-
Front door of terraced house
Absolutely unreasonable and not anywhere in guidance - if this were true every terrace of houses in the country would have to have a fire door as it's front door
-
Fire Door vision panels
For fire safety they are only required where doors on escape routes sub-divide corridors, or where any doors are hung to swing both ways, others will have been likely fitted under Approved Document M for general accessibility.
-
Leaseholder concerned about risk rating and fire alarm system being recommended
If it's a stay put block it wouldn't have the communal call points and smoke alarms (in fact Building Regs & Fire Safety guidance says it absolutely should not) and would have smoke control (or at least openable windows to the stairs). Where is it? If it is in Wales the sprinklers are mandatory regardless of the evac strategy, if England they could be compensation for a departure from the normal guidance which may be pertinent to your problem. I can see how the assessor got mixed up - your current set up, using standard benchmarks, is incorrect for both stay put & full evacuate. The build is modern enough for it to be a legal requirement for the fire strategy & fire safety information relating to the design to be handed over on completion to the freeholder/owner/RMC who has a legal duty to maintain that information and pass it over if they sell the premises - this would answer the questions about the design. If the flat detection is linked to the common detection then you are set up correctly for an evac policy as it is with no changes. Fire doors do not need closers other than to the flat entrance doors where no relaxation exists in any build guidance. If the electrical board is made with a non combustible housing (metal) then it can be argued no further enclosure is necessary (opinion is sometimes divided on this). The Emergency Lighting has to be tested and the test switches make this easier - it's a sign of a poor build that they are not there as they are pretty standard and should have been there from new! Building Regs sign off is no guarantee of full compliance with the Regulations, nor of the fire safety legislation that takes force on completion - plenty of modern builds have been found to be defective despite this, sometimes with total loss fires or fatalities as a result. Building Control have no liability and it rests instead with the developer. If your FRA did not attempt to access at least a proportion of flats to examine the front door fully (both sides, top & closing) and see if the common alarm extends inside it is not compliant with current Government guidance for a suitable & sufficient FRA (as part of this, if readily accessible the roof void should also have been accessed) so you haven't had what you paid for. Housing is far more specialist than many assessors assume and this is an example of a site where a careful eye is needed! I can't give you a more definitive answer without seeing the site, remote advice can only go so far!
-
Fob locks on internal doors
The correct guidance for supported living is on here: https://nfcc.org.uk/our-services/building-safety/protection-building-safety/specialised-housing/
-
Leaseholder being forced into front door replacement without valid justification
I suggest you take the Government Guidance as evidence and take the matter to a First Tier Tribunal for review as an excessive and unjustifiable requirement, also you need to get a copy of the block Fire Risk Assessment which, if competent, should detail the grade of fire doors required and if notional doors (those to the standard at the time of installation) are acceptable, which unless there is something really left field with your block it should. Too many 'zero to hero' poorly trained door assessors are out there chasing volume inspection work or remedial/replacement work with minimal knowledge and can't handle anything more complex than a brand new door to brand new standards. I've advised countless leaseholders on this and given evidence for FTT's as this is not an isolated issue!
-
Fire Risk
If your premises is 'Stay Put' it should not be a critical defect, although one that should still be promptly resolved. If it had been a High Rise Residential Building in England over 18m/7 stories then, as a fault lasting over 24 hours, there would be a legal requirement to report this to the Fire Service, however no such duty exists for your size of block, but if you are concerned you can still consult the Business Fire Safety department of your Fire Service (where enforcement officers are based including those covering flats) or for general home fire safety guidance the Community Fire Safety department
-
Assisted Living Fire Safety - Door Spec Recommendations
As stated a swing free closer is the best solution. Whilst bathrooms are traditionally low risk from a fire door and detection point of view (unless containing unusual risk not itself enclosed like a boiler) there is precedent in England & Wales for some care premises bathrooms to be considered higher risk when electrical mobility equipment is present (particularly if with back up batteries on trickle charge which with modern equipment could be lithium ion batteries) and I have seen enforcement action down here requiring detection & self closing fire doors so it's not unprecedented.
-
Plastic Socket inserts
The sockets themselves contain all required safety mechanisms - https://www.fatallyflawed.org.uk/
-
MEK storage/usage
How easy would you be able to walk into another job? If it's a bad as it sounds & they don't seem to care then it's time to consider 'dropping a dime' to the HSE (as we have process fire risk and H&S issues so sits more in their camp than the fire service) but even with whistle-blower protection if they think it was you then things may get awkward. Is the mixer and it's compressor ATEX as well?
-
Electric s Cupbaod.
If you are going to add an extra detector, then to be of any use it should be part of the main system, not self contained. If it's a licensed HMO it's worth checking with the Local Authority that they accept an upgraded door in their fitness standards- traditionally upgrading with board as you suggest was an official method in many LA's local guides for many years but times change and it's worth double checking as standards do vary between LAs
-
Fire doors slamming with chain closer
Could you please post a picture of the closer?
-
Landlord flat, Battery or hard wired smoke detectors?
Ah - Wales! Very different then!
-
Landlord flat, Battery or hard wired smoke detectors?
1 - A stair landing with no rooms on/off it does not need a detector to meet The Smoke and Carbon Monoxide Alarm (England) Regulations 2015 (as amended) 2 - You can't usually link Grade D (mains) & Grade F (battery) alarms. However it sounds like the flat already has the legally required detection & under answer 1 does not need the additional one.
-
Inward opening fire exit door for a shop
An inward opening door cannot, by it's very nature, have a push bar or push pad type fastening (pushing & pulling at the same time is asking for disaster)- but if used by less than 60 persons it need not and a BS EN 179 type A (lever handle operated emergency device) fastening would be appropriate. If you need panic proof escape then the door would need to be rehung. If it opens directly onto the escape stair then unless it is the top floor of the escape it needs to be a fire door (of which metal ones are available)
-
Open staircase through middle of building
Firstly you need (it's a legal requirement) a Fire Risk Assessment by a competent specialist who will address this and any other issues. Stairs are, by their very nature, open shafts, but this is not an issue is the stair is a protected route with 30 minute fire resisting construction and 30 minute self closing fire doors with intumescent strips (or depending on a variety of factors possibly even original fire doors with a 25mm rebate). If the offices were fully legally compliant the stairway should already have this protection as well as a suitable fire detection & warning system and emergency lighting. This will give you an overview as well as links to detailed guidance: https://www.london-fire.gov.uk/media/7155/gn_03_lf_format.pdf
-
Window in protected stairwell.
If this is on an outer wall it does NOT need to be fixed and fire resisting unless there is an external escape stair within a 1.8m envelope. Furthermore if this is a small block of flats it could form part of the smoke control arrangements if a 'stay put' block (as openable windows are a permitted option for certain small 1991-date blocks and some small-medium legacy pre 1991 blocks)
-
Bright emergency light in studio flat
There is no requirement for the lighting in this area, it seems to be increasingly common to install EL in dwellings, bedrooms, etc despite the guidance not requiring it. Can you borrow a stepladder so you can at least obscure the LED?
-
BS 476 phase out for fire testing in favour of European standards (BS EN 13501/1634-1)
If correctly built to the standard of the day, risk assessed & maintained it shouldn't affect existing buildings, but will impact new ones and significant changes to existing ones