Safe passage to an assembly point?

Featured Replies

Hi,

We have a large college building (built in 2011) in Belfast of about 100 metres in length with about 12 fire exits on the ground floor. Staff have asked - when the fire alarm is activated is it safe for them to walk along the full length of the foot path directly beside the building to get to the assembly point at the other end of the building? There is a busy road beside the building and we recommend that people do not cross this road when walking to the assembly point.

Formerly we had an assembly point at either end of the building but virtually no one used the smaller assembly point near the rear of building so we no longer use it.

Many thanks.

If the footpath is

≥2m wide then it would be considered acceptable in most case

≥1.2m and the external wall is non-combustible then it would be considered acceptable in most case

< 1.2m then it would be considered unacceptable in most case

  • 3 weeks later...
  • Author
On 27/08/2026 at 10:29, Mike North said:

If the footpath is

≥2m wide then it would be considered acceptable in most case

≥1.2m and the external wall is non-combustible then it would be considered acceptable in most case

< 1.2m then it would be considered unacceptable in most case

On 26/08/2026 at 20:23, AnthonyB said:

How close is the path to the building & what width is it?

The path runs immediately adjacent to the building and is more that 2 metres in width. The external wall of the building is non-combustible.

  • Author
On 27/08/2026 at 10:29, Mike North said:

If the footpath is

≥2m wide then it would be considered acceptable in most case

≥1.2m and the external wall is non-combustible then it would be considered acceptable in most case

< 1.2m then it would be considered unacceptable in most case

Re the above proviso "in most case" just wondering when it would NOT be considered acceptable in most case?

It would not be the case if there was a Signiant hazard

·         Plant room opening

·         Fuel tanks

·         High risk workshop doors

·         Glass walls

·         Stored materials

·         Cars

·         Wheelie bins

·         Pallets

The list is endless, you will need a risk assessment

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.