July 2Jul 2 comment_56002 I am hoping someone can give some advice here, as I can't find any anywhere else!I am fully aware that gaps around modern fire doors should be 3mm (+/- 1mm) and this is because the intumescent strip and smoke seal are rated for gaps that size. However, I conduct a lot of fire risk assessments for residential blocks of flats built in the 1970s and 1980s where the CP3 standard applied, requiring 25mm rebates. The requirement for that standard was the door to be flush against the rebate, to prevent smoke and fire from getting past. In accordance with the LGA guidelines, and also BS 9794 (Clauses 9 and 10.4) I am happy to accept these doors in principle, including the two hinges, on the basis that they are fully self-closing. However, my questions is about the gaps around, and what are the tolerances permitted, but nobody seems to know about this.It seems to me, that the 3mm requirement should only apply to fire doors where there is a reliance on an intumescent strip and smoke seal, so what tolerance should I accept for these "notional" fire doors? Would say a 5mm gap be acceptable? Or maybe larger one, provided the door frame fits tightly against the rebate (ie up to 25mm)?Thanks in advance for any advice Report
July 6Jul 6 comment_56011 Before the use of intumescent edge seals fire door tests were carried out to early versions of the BS476 test. The test preceeding the 1987 Part 22 test, we still use today, was BS 476 Part 8 of 1972 and door leaf edge to door frame gaps were 3mm without using intumescent edge seals. There has never been an absolute requirement for a 3mm (or indeed 4mm max gap) but test results have been successful using that gap on a first principles basis and guidance in BS 4787 'Internal & External Wood Doorsets' Part 1 Table 1 recommends a 1.5mm to 3mm gap but these are not necessarily fire doors and scope for adjustment is included to accommodate smoke seals. However, a very limited number of fire doors are permitted with larger gaps.So two things to bear in mind:1) Where smoke seals are necessary these are sometimes fitted to the edge of the door leaf and will usually be effective at 2mm to 4mm. But there would be a gap that could be exploited by cold smoke if the gap is larger. Where compression type smoke seals are used to seal between the rebate stop and the face of the door leaf, this larger gap should not cause a problem.2) BS 8214: 2016 section 9.5.2, without making explicit reference to intumescent seals, states that a typlical gap to achieve good fire performance is between 2mm and 4mm. Therefore, it is possible that larger gaps may adversely affect fire performance. These gaps refer to test conditions though. Edited July 10Jul 10 by Neil ashdown To add more info Report
July 22Jul 22 Author comment_56038 Hi NeilI have reviewed BS 476 Part 8 of 1972 and I see that clause 7.1.2 reads: "the gap shall be at least 3 mm between door edges and the frame."So why can the door not have a 4mm gap, 5mm or 6mm?Moreover, I just don't see the logic of the door needing to have a particular gap, as long as the gap is not so big to 'miss' the rebate and that the door sits flush against the rebate.Daniel Report
July 27Jul 27 comment_56044 Gaps around the door are prescribed by the door manufacturer following a burn test. Anything outside the burn test, the door may not perform as expected giving less that the required protection. Report
July 27Jul 27 comment_56047 As Mike said, the door leaf edge to door frame gaps are specified by the door leaf manufacturer and based on evidence from fire resistance peformance tests to BS 476 Part 22 and BS EN 1634-1. Commonly, the gap is 4mm maximum for timber-based fire doors.BS 8214: 2016 section 9.5.2 notes that failure of fire resisting doors under fire performance test is often due to burn through at the gap between the door leaf edge and the door frame. A typical gap for good fire performance is between 2mm and 4mm. There is no guidance, as far as I am aware, that suggests the gaps can be larger for older fire doors already installed in the built environment. Although many existing fire doors do have gaps outside the recommended 2mm to 4mm tolerance. UK Gov guidance may be useful for example at https://www.gov.uk/government/publications/fire-safety-england-regulations-2022/fact-sheet-fire-doors-regulation-10 and https://www.gov.uk/government/publications/making-your-small-block-of-flats-safe-from-fire The Responsible Person has a duty to make sure the fire doors are capable of providing adequate protection. Report
July 31Jul 31 Author comment_56055 thanks Neil I hate to be argumentative, but BS 8214: 2016 relates to modern fire doors; indeed the note that you refer to under 9.5.2 (which is not a normative standard) has text underneath it which relates to intumescent strips and smoke seals. It's clear to me that this standard is not appropriate for assessing period fire doors, Darren Minton's article in the RICS journal is interesting for me; whilst it doesn't give specific guidance on door gaps, it does warn of the dangers of assessing old doors against modern standards. The conclusion I am coming to is that there are no standards for door gaps for period doors, and it's just left up to the fire risk assessors judgement...which doesn't really help me much, as a fire risk assessor!So given the lack of an independent standard, I am forced to think through the logic of the period door "technology", in that the critical element is that the door face needs to form a strong seal with the rebate. And on that basis, unless anyone can show me evidence otherwise, I plan to accept doors with bigger gaps. Report
August 4Aug 4 comment_56059 Basically, as a Fire Risk Assessor, you can dictate what ever gap you feel that you can justify. There are many ways to make a building fire safe, doors are only item in the equation, but one of the most important for protecting the escape routes.However, you may find yourself in front of the man with the funny wig trying to explain why you went against the consensus of 2 – 4mm. Report
August 4Aug 4 comment_56060 "I hate to be argumentative, but BS 8214: 2016 relates to modern fire doors"No problem at all with that but, the point is that BS 8214: 2016 in the context of the 2mm to 4mm gaps, refers to doors being subject to the BS 476 Pt 22 or BS EN 1634-1 fire resistance performance tests. Its not that the doors are modern. Old doors and new doors are both made from timber-based materials and fire conditions in reality might not follow the same fire curve as the standard fire resistance performance tests. Report
August 4Aug 4 comment_56063 I've dug out data from the 1951 fire door standard and even back then the normal fit for a fire door was a gap of up to 3mm with the door closing on a stop of 25mm (no intumescent back then).To say the gaps don't matter because it's a pre BS8214:1990 (first edition date) door fails to appreciate there have been fire door standards for 75 years which were also very specific on measurements Report
Tuesday at 12:342 days Author comment_56095 Hi AntIt's good to hear from you!And I see now that I was wrong on the door gaps for period doors. But the research has been useful for me, and I feel I have more "backup" when I am writing my recommendations on my FRAs. Thank you.I couldn't find BS 459 Part 3:1951, but I did find a really useful Fire Research Note no 855 from 1971 by W A Morris "An investigation into the fire resistance of timber doors" showing the critical importance of the 3mm (or less) gap in doors with 25mm rebates. Neil, thank you, too, for your advicesDaniel Report