Jump to content

Neil ashdown

Power Member
  • Posts

    427
  • Joined

  • Last visited

Posts posted by Neil ashdown

  1. There are two options here, the problem being that many timber-based fire doors have an integral top rail that should not be over-trimmed:

    1) Always replace existing door frames rather than fitting a new door leaf only. This is most often necessary to achieve compliant installation.

    2) If you must retain the existing door frame, then the door leaf must be custom made to suit the door frame. 

    Furthermore, if you must retain the existing door frame ensure the following:

    A) The framing material is in good condition and of suitable dimensions and density. 

    B) The existing hardware (hinges/locks) positions are suitable for the new door leaf.  Any redundant cut-outs to the door frame must be competently repaired. 

    C) The size and sealing of gap between the door frame and the surrounding wall meets the requirements of BS 8214.

  2. The Standard 'BS 8214 Timber-based fire doors assemblies - Code of practice' states that a typical gap to achieve good fire performance is 2mm to 4mm.  A code of practice provides guidance and recommendations and should be applied by those that install and maintain timber based fire doors.

    Whether the gaps have become "larger than they should be due to natural shrinkage" might be the subject of a debate.

    Might they have been "larger than they should be" at the time of installation, five years ago?

    Clearly, work to make the gaps compliant to the Standard would improve the likely performance of the doors in a fire situation.

    Whether the price is good value might also be the subject of a debate.  Does the fire risk assessor at the building have a view about this and might some doors be more critical in terms of fire safety at the building than others?  Remedial work should first focus on the most life-safety critical fire doors.

    In terms of replacing instead of remediating the doors, there will be various door types such as Flat Entrance doors, Cross-corridor doors, Stair lobby doors and Cupboard doors. Some latched, some unlatched, some self-closing and some locked.  You should therefore consult a fire door expert for advice about suitability of 'different materials'.

  3. For FD30(s) timber-based fire doors the intumescent seal size is usually 4mm thick x 10mm or 15mm wide so and the seal should fit tightly in the groove and flush with the edge of the door leaf.  The integral brush or blade should only lightly contact the opposing surface, ie. the one that it sweeps or compresses against.

    So if the groove is too deep, it would be necessary to cut a fillet from thin hardwood or MDF to fit tightly into the groove behind the intumescent seal. Ensure that the fillet is continuous and that there are no voids behind the seal. 

  4. No you can't make a fire door and offer it as 'Nominal or Notional'.  If you put a fire door on the market it must have evidence of fire resistance performance but that's not a problem because you can use the evidence provided by the door blank manufacturer.  Clearly, you have a duty to fabricate and install the door in strict accordance with the door blank manufacturer's technical manual and fire resistance assessment report.

  5. The problem is that composite fire resisting doors are designed for flat entrance doors, not for fully exterior situations.

    So unless you can provide a shelter to sufficiently protect the door from weather, you will need a timber-based fire door.  This means the core is made from timber but with the recent technology of engineered timber the door should be stable even in fully exterior situations.

    The best way forward is to make an enquiry to the technical departments of the door-core manufacturers and ask them where you can buy the door you need using the engineered core that they manufacture. Try these https://www.halspan.com/products/solid-timber-core  &  https://www.falconpp.co.uk/contact/

    Also, remember the thicker and denser the timber the more likely it is to perform well in exterior situations, also ask them about finishes for best edge and face weather protection and whether multi-point locking is permitted.

  6. If an intumescent strip is missing from the edge of the door leaf or from the head or jamb of the door frame, it should be replaced with the correct sized strip and of the same type as the other strips fitted.

    The reason that intumescent strips are not fitted to both door leaf and frame, is that the intumescent strip is designed to expand to form a seal against a solid surface rather than against an opposing intumescent strip.  It is not uncommon to find intumescent strips fitted to both door and frame opposing each other and this has usually been done in ignorance of the fire door installation requirements. Some people often say that having strips fitted in this way could cause the doors to open in a fire situation due to the expanding pressure from both seals and therefore the door would fail to provide the required fire separation performance.  However, there are some double leaf fire doors with edge protectors that have been tested with opposing strips to the meeting edges of both door leaves. 

    Clearly, a fire door fitted with intumescent strips in a manner contrary to the door manufacturer's installation requirements could behave in an unpredictable way in a fire situation, that's why the fire door industry trade associations go to such lengths to promote correct and compliant fire door installation.

    More on this at https://www.ifsa.org.uk/ 

×
×