  1. There is no reference to the use of PVC architraves in the BS 8214: 2016 Timber-based fire door assemblies - code of practice.

    So with reference to Flat Entrance Doors (often composite construction) I would consult the door manufacturer.

    Doors in communal areas are likely to be timber-based doors, therefore I would use timber-based architraves.

  2. If you are changing the door from the house to the integral garage it would be advisable to install a self-closing fire resisting door with restricted smoke spread.

    If you don't want to do that, you could contact a competent consultant to see whether the works you are undertaking fall under the scope of building regulations https://assets.publishing.service.gov.uk/government/uploads/system/uploads/attachment_data/file/901517/Manual_to_building_regs_-_July_2020.pdf

  3. When replacing the lock cylinder, to a timber-based fire resisting door, ensure that the new cylinder is suitably fire rated and that the mortice work around the cylinder is tight with no gaps. If it isn't, repair with timber/rock wool/intumescent mastic as necessary.

    There is no legal requirement to obtain certification particular to this this work.

    OTHER BRANDS ARE AVAILABLE

    image.png.870652a21e615051900c3258efad61e9.png

    image.thumb.png.d99cdeabd8c831e3a9f649db89e55809.png

  4. Lipping must be of a suitable hardwood and fixed with an adhesive appropriate to the door fire rating and type of timber core/rail.

    Lipping should be one piece, rather than two pieces used double thickness.

    For FD30 minimum 6mm thick and maximum 19mm thick with maximum 2mm profiling at the corners.

    For FD60 minimum 6mm thick and maximum 15mm thick with maximum 2mm profiling at the corners.

  5. When the doors are fire resistance tested the intumescent seals would be continuous in one piece.  Therefore they should be installed the same way.

    Gaps should be between 2mm and 4mm generally, but abide by the particular requirements for the installation instructions for that door. The smoke seal should close the gap but the tip of the smoke seal brush/blade should only lightly contact the surface of the door leaf edge or door frame reveal in the closed position.

    Intumescent strips, if installed correctly, should not become worn. If they become damaged, replace them with the correct strip.

    Smoke seals may become worn so replace them with the correct seals.

  6. So the issue appears to be certification of the work.

    Normal practice would be to completely and tightly pack the gap with mineral fibre and then seal to a 10mm min depth to both sides with the Fire Acoustic Sealant. Refer to BS 8214:2016 for minimum requirements. 

    If the architect will not allow the use of Blue 60 and the dedicated packers in place of the sealant/fibre combination, then you have two options:

    1) Ask the Blue 60 manufacturers what evidence of fire performance is available for use of Blue 60 in full accordance with the fire test evidence but with an additional depth of Fire Acoustic Sealant to both sides. Note, we are saying 'in full accordance' so that the sealant is an extra-over to the fire stopping requirements. Clearly door frame material type, depth of foam and gap size is a major factor here.

    2) Use mineral fibre and fire acoustic sealant in accordance with BS 8214:2016.

  7. When inspecting the gaps between the edges of the fire door leaf and the door frame:

    1) Check the gap is between 2mm minimum and 4mm maximum, generally (consult the door leaf data sheet for certainty about the requirements).

    2) Ensure that the smoke seal brush or blade (where required) is in light contact with the surface that it sweeps or compresses against, in the door fully-closed position.

    3) Ensure that the door leaf does no stand proud of the door frame (and not proud of the other leaf of double doors).

    The door frame rebate does not provide significant protection against the spread of cold smoke, therefore smoke seals should be fitted where smoke protection is necessary.

  8. Obviously floor conditions can be outside the control of the fire door installer.  Where the 3mm gap cannot be achieved options are fitting a threshold plate to the floor or fitting a drop-down seal to the door leaf bottom edge.

    Where fitting of those is not possible then the person or organization that has control of the building and responsibility for fire safety should make a risk based decision about whether the excessive gap is acceptable.  If deemed not acceptable then remedial action to the floor condition will be necessary.

    The following is from ASDMA on BS 8214:

    image.png.cc2384927dc925679772257630dd86bb.png

×
×