  1. Whilst there is currently no legal requirement for fire door installers and maintainers to possess a dedicated qualification, competence is necessary. The Regulatory Reform (Fire Safety) Order 2005 requires those that provide fire safety related services to be ‘Competent Persons’.  Approved Document 7 of the Building Regulations covers workmanship and materials. Many clients such as housing associations, healthcare organisations and education providers now require that those that install or maintain fire doors have a qualification or certification as proof of competence to perform those works. 

     

    Subsequent to the Hackitt Report there are industry led working groups looking at what competence should look like and you may find the recent report ‘Setting the Bar’ interesting at   https://cic.org.uk/setting-the-bar-annexes.php

     

  2. 40mm / 50mm gaps are too large to be filled.   Assuming the door assembly is timber, refer to section 9 of BS 8214: 2016.

    I would reduce the gap to 20mm max using tightly fitted solid timber lining screw fixed to the back of the door frame. The lining must be continuous, full width and of similar material to the existing door frame. Alternatively, you could install a new door frame. 

  3. This depends on the type, size and position of the concealed self-closing device.

    From what you say about the advice given by the certified carpenter it seems you may be referring to an uncontrolled Perko type chain-closer with a small footprint?

    If its a controlled device (with a much larger footprint) it could be that the certified carpenter is advocating that the door can be returned to a suitable condition if the concealed self-closer is removed and the void completely and tightly filled, to a high standard of workmanship, with the same materials as the door is made from.  In this case, the repair would most likely be outside the scope of the door manufacturer's certification and therefore such certification would be void.

  4. In the UK, various materials are used for the core of a fire resisting door.  The most common is timber and/or chipboard but some composite fire doors have a core of foam within a timber frame.  Metal fire doors are also available.

    British Standards for fire doors are for fire resistance performance tests rather that construction materials.  Refer to BS 476 part 22 : 1987 and BSEN 1634-1 : 2014

  5. In the case of timber-based fire doors, the certificate of approval and data sheet (or equivalent documentary evidence of fire resistance performance) for that particular fire door leaf will set out the requirements for the door frame.  Usually softwood with minimum sectional dimensions of 70mm wide x 30mm thick plus the thickness of the rebate stop.

    Eg: image.png.86eb77b14a12b496161c034c37a3f474.png

  6. You are correct there are issues surrounding lipping min & max thicknesses, type of adhesive and density of timber.  A good maintenance training course will deal with these issues.

    Also, if the door is in scope of a 'third party product certification scheme' such work may cause the certification to be void.  Mind, it already is when the gaps are too large!

    Best practice would be to remove the door leaf and door frame, adjust the door frame to suit the door leaf and re-install the door assembly compliant in all dimensional requirements including all gaps and alignment.

×
×