  1. FDIS does not claim to be a "third party accredited scheme".  In my experience, as a member of a UKAS accredited third party certification scheme, it is not usual practice for the scheme to "review the reports in order to verify your results".  However, it is worthwhile that Prometheus makes contact with FDIS in relation to the question about sharing the inspection data as I am sure they can help.

  2. The fire doors should comply with BS 8214: 2016 in terms of their FD30(s) status.

    Door leaf to door frame gaps should be 2mm to 4mm for best performance.  Smoke seals must be effective, the brush, blade or fin should close the gap but not impede the self-closing action.

    Threshold gap should be 3mm max or where this is not possible the gap should be 10mm max between the bottom edge of the door leaf and the floor. It may be possible to fit a flexible seal / threshold plate to close the gap in the door-closed position.  The seal must not cause the door to bind on the floor and so impede the self-closing action.

  3. Where the gap between the door frame and the surrounding wall is too large to suit the new door-set or door assembly it is, within reason, acceptable to use a timber subframe.  

    Clearly, it will be necessary for the subframe and door-set / door assembly to be an intimate fit with each other once installed.   Given this, it would be interesting to understand why the timber subframe should not be fixed to the door frame - only to the wall!  Maybe, in this particular case, the subframe is quite thick?

    The structural openings for replacement fire doors should be measured carefully and the door-set / assembly made to suit, so as to avoid adding timber subframes where possible.

  4. The inspector should be able to provide you with details of the necessary remedial works and as they have inspected the door you should contact them in the first instance.

    However, Georgian Wired polished plate is considered acceptable for vision panels in fire rated doors but there is more than one type. So in terms of installing a suitable glazing system you should seek advice from a fire door / fire rated glazing specialist.

  5. A new fire door-set is always preferable to a new fire door leaf-only in terms of suitability, compatibility and compliance.  Before you order your replacement check that the inspector has checked ALL evidence of fire resistance performance for the glazed door. Some manufacturers test with more than one provider and therefore it could sometimes be possible that additional data may exist.

  6. There is no quick and easy way to do this.  Remove the door and loosen the door frame fixings so that the door frame hanging jamb can be moved-over and then re-install.  You will need to check the gap between the surrounding wall and the doorframe is correct and make good the fire-stopping between the wall and door frame.

    Depending on the gap issue, you may have to completely remove the door assembly and re-install.

×
×