  1. Hi Callum,

    Quite often buildings have doors designated as fire resisting doors when actually if they were to carry out a suitable fire risk assessment they would find that not so many doors need to be fire doors. A huge amount of money can be spent keeping fire doors in good working order, so its important to understand why they need to be fire resisting doors.

    Feel free to use content from my fire door blogs at www.firedoorscomplete.com 

     

  2. Composite fire resisting doors are required to be tested to the same standard as timber based fire doors, BS 476 part 22 and/or BS EN 1634-1.  If the composite fire doors are new and you have a doubt about the installation contact the manufacturer for the product data sheet including installation instructions.

    Common faults, in my experience, are incorrect fixing positions (of fixing screws door-set to wall), inadequate fire stopping (BS 8214:2016) and excessive door leaf to frame gaps.  Use of the correct intumescent gaskets to lock-sets, door-viewers and hinges is very important in regard to these types of fire door too.

  3. Ask for a copy of the fire door inspection report.  If the inspection has been carried out correctly, the report should detail all non-compliances separately for each door and describe the remedial works required.

    It could be that the door leaf to frame and door leaf to threshold perimeter gaps are incorrect.

  4. I would advise you to contact a Certificated Fire Door Inspector.  A competent inspector would be able to come to site and inspect the fire doors and then recommend the exact method for the remedial works. There are a few methods that may be employed to reduce the perimeter gaps to within the necessary tolerances.

    They would also be able to provide the details you require in their inspection report.  Once the works have been completed they could provide a second report and, if the door is by then compliant, to confirm compliance.

    Clearly though, where the inspector's inspection reveals any other issues, these would also require remedial works.

  5. The fire rated glazing will have been fire performance tested in a furnace using a suitable beading and gasket system for the retention of the glass in a fire situation. 

    From that test a fire resistance report will have been written and within that report will be stated the requirements for gasket materials, beading materials and fixing pin or screw requirements. The manufacturer of the FR glass will be able to advise you on the particular requirements for that FR glass product. 

    It is not uncommon for some contractors to install FR glass using non-compliant gasket/retention systems! 

    I recommend that you seek advice from the manufacturer / supplier of the glass.

  6. No recent changes to gap requirements.  These should be in accordance with the door leaf manufacturers installation instructions, product data sheet or technical manual. 

    Usually, that means the gap between the door leaf and door frame at the vertical edges and top edge should be minimum 2mm and maximum 4mm.  At the threshold the gap between the door bottom edge and the floor covering or threshold plate should be 3mm maximum where cold smoke protection is a requirement. Clearly, HMOs will require cold smoke protection.

    Where a max 3mm gap cannot be achieved it is permissible to fit a threshold smoke seal to fill the gap, but the gap between the door bottom edge and the floor covering or threshold  plate should not be more than 10mm.  Where cold smoke protection is not a requirement the bottom gap should not exceed 10mm.

     

  7. The installation instructions or product data sheet for the fire door leaf will advise which fire seals are necessary.  Be careful to adhere otherwise performance certification may be void. 

    BS 8214:2016 Timber based fire door assemblies Code of practice provides further guidance also check out the website of the Intumescent Fire Seals Association at   https://www.ifsa.org.uk/  for best practice guidance.

  8. Purchase a fire rated door blank with suitable evidence of performance.  The blank can be cut to size and at the edges and lipped with suitable hardwood.  Follow the technical manual for the door blank with regard to sizing and installation.

    Alternatively order a custom-made fire door to the size you require and install in accordance with the door leaf installation instructions/product data sheet.

×
×