  1. The problem is that many of the standard sized fire doors cannot be trimmed above approx 3mm off each vertical edge and 6mm off the bottom. 

    There are minimum requirements in terms of the thickness of the hardwood lippings and because many fire doors have small section framing around a chipboard core the trim allowances are very limited. If you trim too much then the door will be weakened and therefore not provide the required performance. 

    You could possibly fit new fire door frames to suit standard door leaf sizes, depending on the structural openings. If the structural opening sizes won't work for standard sized doors then, sorry looks like its gonna be door blanks.

  2. As Tom says, the RR(FS)O defines Competent Person as somebody with sufficient training and experience or knowledge and other qualities. It does not require that the Competent Person has a dedicated qualification.

    Whether or not it should is subjective and in my opinion depends on a number of factors.  Certification is not always a guarantee of quality and with regard to fire door installation the end result depends, as much as anything, on the diligence of the installer.

  3. The seals should fill the gap between edges of the door leaves and the reveal of the door frame at both vertical edges and the top edge. On double leaf doors the seal should fill the gap between the meeting edges too.

    The seals must not hinder the self-closing action of the doors. You may need to install a smoke seal at the threshold too.

  4. There are two basic types of intumescent strips 1) The type that fits flush and tight into a groove in the edge of the door leaf or into a groove in the door frame reveal and 2) Self adhesive types that fit to the door fame reveal 

    https://www.safelincs.co.uk/fire-and-smoke-seals/?fga=true&msclkid=7837a0ed87c316adc67bfd1a66c4e42c&utm_source=bing&utm_medium=cpc&utm_campaign=SL Text%3A fire door seals&utm_term=intumescent seals&utm_content=intumescent fire door seals   See images below. 

    I expect your door is the entrance door to your flat, in which case smoke seals will also be a requirement.

    image.png

    image.png

  5. So long as the hinges are made from steel, suitable to carry the weight of the door, securely fixed and in good condition then there's no legal requirement to replace them.

    They might sometimes be marked BS7352 which was the standard before the current EN1935.

    If the hinges are worn or damaged replace all three with CE marked fire rated hinges to minimum grade 11, use a good quality hinge as you may find some modern hinges will wear more quickly than others. If the current hinges have lasted twenty years it would be sensible to replace them, when necessary, with good quality hinges.

    Just as a matter of interest, current building regulation requirements for hinges for fire doors can be found in paragraph C10 on page 151 of Approved Document B at https://assets.publishing.service.gov.uk/government/uploads/system/uploads/attachment_data/file/832633/Approved_Document_B__fire_safety__volume_2_-_2019_edition.pdf

  6. Where replacement fire doors to flat entrances or in communal areas is necessary, the survey work is an important job.  It should be done by somebody that understands what types and sizes of fire doors are available and how they should be installed. 

    Just for example: Do you replace the door leaf and frame, or just the door leaf?   How much can be trimmed from the edge of the door leaf for installation?   What is the best type of door leaf construction for the job?    What type of lock should be fitted?      What are the best types of smoke seals for the particular job?    What type of threshold plate and seal should be used?     Can a door-viewer or letter-plate be fitted?

    The better the survey, the better the end result.

  7. Generally yes, OK to add hardwood lipping but not added to the existing lipping. Cut off the existing lipping and replace with a thicker one. Hardwood lipping should be minimum 6mm thick and maximum 18mm thick.

    Generally, the door frame rebate stop should be 12mm or more and intumescent fire seals are necessary. 

    Updating your fire risk assessment will help in identifying which doors need to be fire doors.

  8. Fire doors and escape doors are fire safety devices and assuming you are in England or Wales the requirements of Article 17 of the Regulatory Reform (Fire Safety) Order 2005 must be met http://www.legislation.gov.uk/uksi/2005/1541/article/17/made

    If your fire doors are in good order, as you say they are, then its reasonable to expect they comply with the legal requirements.

    With regard to perimeter gaps, these should be between 2mm and 4mm.

    With regard to fire door-set (rather than fire door assembly) and certification labels, these are not legal requirements.

    On the subject of fire safety, I would recommend that you seek advice only from 'suitably competent persons'. 

  9. So if restricted cold smoke spread is not a requirement for your design, FD30 doors may be used instead of FD30s doors.  Many FD30 doors permit a 10mm gap at the threshold, check with the particular fire door manufacturer.

  10. If the door leaf is new with installation instructions or an existing door leaf with a manufacturers label, you can check to find out the door frame sectional size and material requirements, hinge and hinge position requirements, intumescent seal requirements, fixing requirements (these should also be contained within the door frame kit) and fire stopping requirements. 

    Smoke seals may likely be required too.

×
×