Jump to content

AnthonyB

Power Member
  • Posts

    2,324
  • Joined

  • Last visited

Everything posted by AnthonyB

  1. No. Calculations for horizontal evacuation are separate from those for vertical. Stage 1- assess escape from the room Stage 2- assess escape from the floor Stage 3- assess escape from the building All seperate
  2. That's still a property dispute, the lease should determine the boundaries, and go from there.
  3. Yes, but it must be the correct type for the premises. BS EN 14604: 2005 & BS 5446-2 smoke and heat alarms for a BS5839-6 alarm system for dwellings only EN54 smoke & heat detectors, call points, sounders and control panels for a BS5839-1 system for buildings other than dwellings.
  4. Where the evacuation of a disabled person may slow evacuation such as to case a log jam, pushing, crushing, trips, etc it is accepted practice to refuge them in a temporary waiting space until the escape route is clear. This is however only usually applicable to buildings with stairs, not single storey halls. Fire safety in premises outside dwellings is dealt with by Business Fire Safety/Protection units within the fire service, any Community Fire Safety department isn't trained in this area hence not being able to instantly reply to you. Here is the current guidance: https://www.gov.uk/government/publications/fire-safety-risk-assessment-means-of-escape-for-disabled-people
  5. No, your tenancy and the deeds to the property will determine ownership & control. Not a fire safety matter.
  6. Assuming in England or Wales: Regulatory Reform (Fire Safety) Order 2005 Fire Safety Act 2021 Fire Safety (England) Regulations 2022 A fire risk assessment will be required for the common areas (including flat front doors and the external structure of the building) which will determine the general fire precautions required and point towards the appropriate evacuation policy. Specified fire safety information & procedures will have to be provided to residents. Depending on the height of the building various other explicit statutory requirements apply. Conversions can be tricky to correctly risk assess so care should be taken in choosing a risk assessor. Any flat that is rented out has it's own obligations for the landlord under the Housing Act and Smoke & Carbon Monoxide Alarm (England) Regulations.
  7. You could argue if the cupboard has a fire door fitted this protects the escape route from the electric meters and boxing in as well is unnecessary duplication. The boxing in is usually reserved for meters on corridors/hallways that aren't in a room.
  8. Modric is a brand used by Allgood for their products in certain markets such as North America. The 9156A is OK for fire door use as detailed here: https://www.allgood.co.uk/product/9156a-allgood-hardware-swing-free-overhead-door-closer/
  9. Yes they are. They date back to early forms of modern fire safety and building regulations, which when applied to existing buildings would require an additional escape route. Some buildings had the footprint to add external steel escapes - others in city centres terraced with adjoining buildings couldn't and so escapes across roofs and through party walls became a common solution. As these are escapes into adjoining fire compartments they comply (although if you were building the terrace of buildings today you wouldn't usually be permitted to do this) but you do then fall into civil law regarding right of access. Without an agreement in the form of an easement, deed of variation, means of escape license or similar one party can lawfully remove right of access and potentially physically remove it too. Even where such an arrangement exists they sometimes expire on change of owner (which one client fell victim to resulting in selling up rather than doing the work to provide new alternatives). If you get a decent fire risk assessor (not a tick box champion) they can measure travel distances, exit and stair widths, take occupancy figures and determine if you actually need these adjoining escapes anymore - sometimes I've been able to justify removal without the need to add new stair cores or anything dramatic. Note that in other cases this hasn't been possible without major works if at all so it isn't a given.
  10. It's now BS7177:2008+A1:2011 BS 7177:2008 was a full revision of the standard, and introduced references to mattress pads and changes arising from revisions to related standards. References to legislation were also updated. The principal changes introduced by Amendment A1 are to the wording of the fabric specifications in Annexes A, B and C. These changes are to make the fabric specification identical to that stated in the Furniture and Furnishings (Fire) (Safety) (Amendment) Regulations 2010 [3a]. The technical specification of the fabric, and the results of any ignitability tests in which the fabric is used, are not affected by the changes.
  11. Not needed to be a fire door unless they have to pass directly past the door as their only means of escape.
  12. No. Whilst in similar fields Health & Safety and Fire Safety are different and the syllabus of most H&S courses (including IOSH Managing Safely) would not be suffcient for them to understand their duties under fire safety legislation. This is a better starter course https://iosh.com/employees/awareness-courses/fire-safety-for-managers/
  13. Domestic smoke detectors are not suitable for non domestic premises (other than some very limited situations in very small premises). The legal minimum standard of alarm is a manual alarm upon a person discovering a fire. In the smallest premises this can be the human voice, but where this cannot be immediately and clearly heard throughout the building an electrical system of manual call points and alarm sounders off a central panel is required. If required by layout and risk you would then layer categories of detector coverage (part of the main system, not separate) in addition as required. Your fire risk assessment will determine what you need - official guidance is here: https://www.gov.uk/government/publications/making-your-premises-safe-from-fire https://www.gov.uk/government/publications/fire-safety-risk-assessment-offices-and-shops
  14. It should be the other way around on a loop. Voice alarm systems should generally operate in the following repeating sequence (BS5839-8): Attention-drawing signal – lasting 2 s to 10 s followed by Brief silence – lasting 1 s to 2 s followed by Evacuate message followed by Silence – lasting 2 s to 5 s
  15. The maintenance regime comes from the Facilities Management British Standard BS 8210:2012 for building fabric and equipment and is not specific to a particular elementso would be equally applicable to any stair. It says: "Frequency of inspection Inspections should be carried out as follows: a) routine: consultation with occupants and other users of the facility to determine the existence of any maintenance matters that might require action and, where such work has been undertaken, measurement of users’ satisfaction with the outcomes; b) general: visual inspections of the main elements carried out on an annual basis that informs an organization’s budgets for maintenance programmes and other maintenance; c) detailed: a full inspection at intervals of not more than five years. An inspection should be carried out by using a checklist made up of facility elements/sub-elements and arranged in way that supports safe working." In essence this is usually translated to annual formal visual inspection & 5 yearly detailed structural survey. Whilst the British Standard is not itself law, following it is a good way to demonstrate compliance with actual legislation, such as The Workplace (Health, Safety and Welfare) Regulations 1992, The Occupiers' Liability Act 1957 (as amended) and similar.
  16. It's not set in stone but for current active records for fire safety related stuff the minimum would usually be the last full year of PPM plus the year that is being worked through the theory being that most PPM are no less than once a year so this would always capture the latest test. Other records need to go back longer, such as fixed wiring EICR as they are usually 3-10 years apart. Completely binning at 24 months may be extreme - it may be worth archiving stuff outside the current active cycle for a bit longer.
  17. Cost is no justification if the level of risk involved is intolerable. There are however potentially other solutions that may enhance safety that are more achievable instead that can mitigate the original issue, depending on what it is. PVC windows are not a 1958 thing so someone may already have made matters worse than the original build in the past already so you can't use the 'original spec' reasoning. Current legislation removed the statutory bar that older legislation contained so just because something complied in the past doesn't mean it does now. The risk assessor should look at the legacy precautions, compare them to the current approach and then determine if the difference in protection between the two is such as to present an unacceptable risk. Some old approaches & technologies are indeed still acceptable, but others have been disproven over the years as dangerously ineffective compared with current knowledge. It is wrong to automatically expect a legacy building to have to fully meet the standard and specification of somewhere built today just as much as it is wrong to say just because it met spec originally (which could be 20, 40, 60 or more years ago) it's automatically OK now. I'd need to know a lot more before I can give you options, but they may be out there (there are however some issues for which there are none).
  18. It's all required unless the fire risk assessment can put forward a case as to why omitting one method is still safe. You aren't legally responsible for the exit so have no authority to request the contractor does anything - it has to come from the landlord. I'm not saying its impossible, just there is a process to go through.
  19. AnthonyB

    Mr

    If the build was to the recommendations of Approved Document B and adopts a stay put approach based on: - 60 minutes fire separation between shop & flats, flats and common space and between each flat - Smoke control system to stairs & lobbies then it needs no common alarm system beyond a silent detection system to open smoke vents and thus nothing in flats other than their local domestic systems. If the conversion was not to Approved Document B (as a deliberate design decision or in error), omitting one or more of the above (or some of the other ADB recommendations) then a simultaneous evacuation approach may be necessary and this requires an audible common system that, to alert flat occupants even when asleep, requires a sounder and detector from it inside each flat. Whilst on paper it should be 75dB bedhead in practice it's almost universally accepted for the domestic standard to be used of 85dB at the bedroom door so normal size and layout flats only require a heat detector and sounder base to the flat's internal hallway. Building Regs sign off is almost universally accepted as being meaningless from a fire safety point of view due to how often incorrect or defective builds get through the system (Grenfell being the worst example) so if the actual situation is non compliant and unsafe so as not to meet fire regulations then any competent assessor will flag it for action. So they could be right.....but without seeing the site I couldn't be sure.
  20. It's not secured by metal clips within manufacturer's instructions (almost always 300mm/400mm depending if wall or ceiling) so that's the first major non conformity which will affect both the integrity of the system and the safety of firefighters and others "Methods of cable support should be non-combustible and such that circuit integrity is not reduced below that afforded by the cable used, and should withstand a similar temperature and duration to that of the cable, while maintaining adequate support. NOTE 10 In effect, this recommendation precludes the use of plastic cable clips, cable ties or trunking, where these products are the means of cable support. NOTE 11 Experience has shown that collapse of cables, supported only by plastic cable trunking, can create a serious hazard for firefighters, who could become entangled in the cables." As for sharing with other cables: "To avoid the risk of mechanical damage to fire alarm cables, they should not be installed within the same conduit as the cables of other services. Where fire alarm cables share common trunking, a compartment of the trunking, separated from other compartments by a strong, rigid and continuous partition, should be reserved solely for fire alarm cables. To avoid electromagnetic interference with fire alarm signals, any recommendations by the manufacturer of the fire alarm equipment in respect of separation of fire alarm cables from the cables of other services should be followed." Is the cable printed with manufacture/product info - it looks a bit thin for FR cabling (its probably just the photo making it look so, but it wouldn't be the first system sneakily cabled in non-FR red PVC cable!)
  21. Cluster kitchens and sample of bedroom doors (viewed from both sides) in shared cluster flats and common areas and bedsit entrance doors (viewed from both sides) for these. This is if you are doing Type 1 FRAs to satisfy the minimum requirements of the fire safety legislation. If you want your responsibilities as a landlord under the Housing Act assessed as well (Type 3 FRA) then all rooms would be viewed in the samples
  22. Is this a PRU/ELC type environment? Does it have automatic fire detection throughout and/or sprinklers? It's possible within the bounds of BS5839 & your risk assessment (unlike raising call points which isn't) to do the following: - Omit call points entirely from public circulation areas (only have them in staff areas and high risk areas); or - Move to a two stage alarm, the first being a silent staff alarm (you could programme the system to operate selected sounders and all your visual warning devices rather than relying on just the panel buzzer to alert staff to investigate) operated by call points and the second being an audible evacuate signal operated by detector, sprinkler flow switch, manual 'evacuate' call point (you'd need to fit one of these) or by the stage 1 investigation period timing out) I've carried out fire risk assessments and fire safety design consultation for a number of schools including PRU/ELC's and can help further off forum if required.
  23. The furniture regulations date back to 1988, so it predates these - it may still be OK, but some may be put off by being pre-88
  24. Quite possibly. What is the fire detection & alarm provision?
  25. Have you tried hinged covers or alarmed covers yet? Unless the Watch Commander is actually from the fire safety department and not just a local station their go ahead is meaningless - I was chatting with a client about situation where non enforcement officers had given the OK to a situation that was actually dangerous and against all guidance and when the client challenged this with the actual specially trained enforcement officers whose remit fire safety is they agreed it was completely unacceptable and reversed the OK. As the fire service no longer have a role in specifying fire safety requirements under current legislation your own fire risk assessment should detail what is needed and why it's legal - fire officers come and go and saying 'x said it was OK' is no defence against future action. If they made the wrong decision they have no liability - it's your organisation that would still carry the can. If the covers don't work there are several other options available. What height were they thinking of moving them to? As it won't readily work as I've seen CCTV of children using chairs or each other to get to fire safety equipment supposedly 'out of reach'
×
×
  • Create New...