Fire door sign on door leading edge
https://assets.publishing.service.gov.uk/media/67d17064a005e6f9841a1d50/Approved_Document_B_volume_2_Buildings_other_than_Dwellings_2019_edition_incorporating_2020_2022_and_2025_amendments_collated_with_2026_and_2029_amendments.pdf Appendix C Fire Doorsets C11: Fire Door Signs. Complying with BS 5499-5. All fire doorsets should be marked on both sides, except fire doorsets to cupboards and service ducts, which should be marked on the outside. https://www.firecode.org.uk/Code_of_Practice_hardware_for_fire_and_escape_doors_issue_5.pdf Fire Safety Signs page 104 to 112.
-
Compliant self-closing devices suitable for the elderly in blocks of flats
You could search for a local fire door inspector at https://afdi.org.uk/category/find-a-fire-door-inspector/ and https://fdis.co.uk/approved-fdis-inspector/
-
Is there a legal requirement to retrofit CE marked hinges to existing fire doors?
It would very likely be possible to upgrade the fire resistance and smoke spread restriction of your flat entrance door but the term FD30(s) can only refer to either a door with product certification (which yours probably doesn't have) or a door that has been inspected/assessed by a suitably competent person as a Notional FD30(s) or Nominal FD30(s) door. Before you decide on any action, it would be worth consulting the UK Gov guidance whilst considering the location of the door in the block, fire evacuation strategy and potential risk from fire to the occupier(s) of the flat and other residents at the block. https://www.gov.uk/government/publications/making-your-small-block-of-flats-safe-from-fire/a-guide-to-making-your-small-block-of-flats-safe-from-fire-accessible and https://www.gov.uk/government/publications/fire-safety-in-purpose-built-blocks-of-flats
-
NFR Rated Door - Remedial Works
- NFR Rated Door - Remedial Works
Make some intrusive surveys of a sample percentage of the 40 doors. If the cores are the same as fire doors, it may be possible to retain them and upgrade as necessary. "NFR" on a sticker on top of the door doesn't mean the core is unsuitable, it may be the same core as the fire doors.- Smoke seals
https://www.lorientuk.com/products/architectural-seals- What gap under fire door
Generally, the maximum threshold gap for a fire resisting door is 10mm. For a door that is required to restrict the spread of cold smoke its 3mm. 3mm is often difficult to acheive due to imperfect floor conditions, so a 10mm gap is acceptable so long as its sealed with a flexible seal. Ref. BS 8214: 2016 Timber-based Fire Door Assemblies Code of Practice. UK Gov fire door safety guidance reconises this difficulty. https://assets.publishing.service.gov.uk/media/677fbe166f01ae28ab5c0554/A+guide+to+making+your+small+block+of+flats+safe+from+fire+2024.pdf Page 18- Management co demanding new flat doors
As Mike says, the managaing agent may have had some sort of survey or inspection including the flat entrance doors. So they should be able to provide details about why the doors are non-compliant and why they should be replaced. If they have defects, why can't these be remediated instead of replaced?- Yale smartlock
Bryony at https://www.ironout.co.uk/ can help- Fire door with double chain closer
Samual Heath at https://concealeddoorclosers.com/powermatic-r100-concealed-door-closer/ New Star at https://www.new-star.co.uk/products/agb-eclipse-self-concealed-hinge-with-door-closer?_pos=1&_psq=self-closer&_ss=e&_v=1.0 Contact them and the door manufacturer to check suitability for your type of door, fire rating and end use.- Can a nightlatch on a fore door be made complinat
Fire resistance performance test evidence does exist for some night latches. But compliance also depends of the core-type for the timber-based fire door in question. An experienced fire door inspector should be able to assist you. Failing that, an experienced fire risk assessor may be able to help.- Flat fire doors - under 11m
If that's the only reason why the latest inspection has found the door to be unsuitable, the inspector would need to back up their finding with the relevant documentation.- Flat fire doors - under 11m
If the installer says the door is non-compliant due to the thickness being 42mm or 43mm (rather than 44mm) and requires replacement, they should back that up with the relevant documentation (guidance/certification/product data sheet etc). If they can't, then what basis do they have for making that recommendation?- Flat fire doors - under 11m
So, has the Installer said why the door needs to be replaced? At residential blocks below 11m in height, there's no statutory requirement to inspect fire doors to a particular schedule but there is (under Article 17 of the Regulatory Reform Fire Safety Order 2005) a legal obligation, as you would expect, to ensure fire doors "are subject to a suitable system of maintenance and are maintained in an efficient state, in efficient working order and in good repair". See https://www.legislation.gov.uk/uksi/2005/1541/article/17- Fire door fillers
End to end butt jointing of intumescent seals is acceptable if done tightly and well fitted. But don't mix different types. This website is worth visiting https://www.ifsa.org.uk/- Flat fire doors - under 11m
The thickness of the door depends on the relevant certification / evidence of fire performance for the door. Also see Also see https://www.howdens.com/joinery/doors/howdens-spey-35mm-plywood-flush-fd30-fire-door-obj-sku-family-25409973 Refer to the relevant UK Gov fire safety guidance for the type of resirential block inn question eg: https://www.gov.uk/government/publications/fire-safety-in-purpose-built-blocks-of-flats https://www.gov.uk/government/publications/making-your-small-block-of-flats-safe-from-fire- BSR v Local Building control & Internal Flat fire door
You could consult https://wilkinsoncc.co.uk/ for certainty about your responsibilites.- Dryad Simplan Door Closers
You could try https://www.ironout.co.uk/- Fixing Fire Door Gaps
Sorry I don't, you could try third party certificated companies for example https://www.blueskycert.com/installation-maintenance-and-inspection/- Timber Doors in Aluminum Frames
Based on my experience it might be from this company? https://www.komfort.com/products/timber-doors-frames/?portfolioCats=173- Spy hole
Does the door security viewer (spy-hole) have an intumescent gasket between the viewer and the core of the door. If it has, that's a good sign that its compliant. If the door is on an escape route, the lock should be a keyless egress (thumb-turn etc). Removal of the viewer and gasket will enable you to inspect the core of the door too.- 44mm fire doors fd 30
42mm minimum Check out Certifire certificates of approval for intumescent edge seals.- Cross corridor doors
"As I have mentioned before we have Windsor Type doors with 10 panels per door, 5 at the bottom, up to 80cm x 10 cm wide." Difficult to see a safety issue with clear wired glazing in a door when the glazed panels are only 100mm wide.- Fire door fillers
Generally speaking, product performnace certification for fire doors does not cover repairs to the fabric of the door. There are certification schemes for repairs and they have limited scope for the extent of a repair. If you are unsure about whether a repair is appropriate, consult a specialist. They can issue a report stating whether the repair is fit for purpose..............or not.- Roller bolt bolt nigh latch on nominal fire doors
Hi Stu, These are quite common for Flat Entrance Doors but in practice are often locked when the resisdent is at home to avoid an uninvited visitor. From a fire resistance perspective, only doors with evidence of fire performance in an unlatched configuration are suitable. Flat Entrance Doors of course are also held shut with a self-closing device. My understanding in terms of CPR, is that such night latches are outside the scope of CE & UKCA marking. https://www.legislation.gov.uk/uksi/2013/1387/contents However, many fire door manufacturers require that locks fitted to their fire doors are CE or UKCA marked. Therefore, product performance certificate would, in these cases, be invalid. - NFR Rated Door - Remedial Works