  1. A fire rated suspended ceiling will normally be positively fasten into the grid, this is no guarantee of the fire rating, the OEMs should be consulted.
  2. What is in the cupboards, are they full height or stopped top and bottom at each floor? It is possible that nothing is needed
  3. BS 5839 - 1 – 2017 refers to non domestic, part 6 refers domestic 75 @the bedhead and 85 the 3m from the alarm are two different locations and make sense if you consider that in a none domestic setting the alarm is usually in a corridor and the bedhead is behind a fire door which and lower the sound be 20dBs
  4. every 18 months for a new RA seems excessive, however for a review it should be 12 months (no changes, quick look, tick the box). Without knowing the layout, there should be as a minimum a fire escape sign on every change of direction and level, don't forget it will be dark and smoke filled in a fire. However, what is confusing is why they are insisting on more signage when the property was assessed by the same management company and signed off 18 months ago. Are they admitting they got it wrong?
  5. If it is a new build, ask the builders to rectify. If they say there is nothing wrong I would suggest a word with the local fire authority.
  6. Most modern 30 and 60 doors are manufactured as non-smoke doors, it only the inclusion of the smoke seals in the intumescent strips that make it a (S) door. The use of a FD30 door is not in accordance with Approved Document B Vol 2 2019 Amendment 2020 for a flat entrance door, and BC would in all probability not sign it off, if however, it is an existing door that has been picked up in a FRA I suggest that you read Communities and local government. Determination on the suitability and sufficiency of a fire risk assessment in a hotel in respect of the adequacy of the existing bedroom fire doors. You may be able to argue that there is no requirement until the door needs replacement.
  7. It is always preferable to lip the bottom of a door as in a fire the most sever conditions can usually be found at the top opposite the hinges, this is one of the reasons why the certification mark is put here. If you do lip the top of a make sure you take images of the certification before you modify the door.
  8. Technically adding a decretive moulding to the door should not be a problem. You need the global assessment for the door so that you use the correct moulding in the correct position and adhesive.
  9. As a general rule flat entrance doors should be fire rated. The basic exception are when there is no door or window above them (top floor) and a person can get 1.8m away from the building without passing another door (a balcony for instance)
  10. The fact that the lipping on both leaves appear to be the same would suggest to me that that this was how the doors where manufactured. The door we can see through the vision panel, does it have the same band at the head? and what about the bottom of the doors?
  11. Given the fact that these doors contain Georgian wire, I suspect that they do not conform to the latest standards, however, unless there is a fault or defect with the door, they will do a job. I would suggest you mark them down as nominal fire doors and leave it up to the building owner as to if the wish to replace the door. There is no expectation to replace something under Approved Document B unless there is a material alteration to the building
  12. All depends on what it is protecting. If there is no smoke requirement then I would say that steel door would offer greater protection than a wooden door.
  13. If this is the only sign, then it does not satisfy the RRO. Fire action notice signs should be designed to clearly people with various instructions to make during a fire, including how to raise the alarm and where the closest assembly point is.
  14. This is a building management issue not a fire issue
  15. I would be more concerned about the possibility of asbestos
  16. You can use a “similar repair technique” you just can not claim it is TRADA approved repair
  17. Look at building regs, doc B, 2019. Table C1 11 b. The doors should be FD20, which are no longer available, so you need a FD30. There is no smoke requirement. There should be intumescent, have you checked they are not in the frame
  18. I would have expected that the glazing was compliant with the regulations at the time of installation. There is no requirement to bring the glazing up to date unless it is defective. BR stipulates no worse than existing.
  19. If there are >59 people expected to use the door in a fire condition, then the door must swing in both directions. otherwise as long as the global assessment for the door allows it and the person carrying out the modification is competent then yes
  20. I would ask the requester what type of fire door inspection certificate they require, been well versed is completely different to having passed a course. The inspection scheme may fail a door because it is not up to the current standard but there might be nothing wrong with the entire installation and over all fire measures throughout the building. I am sure that doors in Buck house would not pass a full inspection, but would you replace them all?
  21. So your client want an inspection to a 3rd party accredited scheme, but is unwilling to allow the scheme to review the reports in order to verify your results. Seems to be a bit of a contradiction
  22. Also see BR 2019 Escape over flat roofs Para 2.31 - 2.32
×
×