  1. Regulations are not so specific as to deal with a door knocker/ornament in terms.  However, the fire doors must be maintained as adequate to provide sufficient fire and smoke protection to keep relevant persons safe from the effects of fire.  Whether or not the knocker/ornament is suitable for fitting to a fire door would be a matter for a fire door specialist. 

  2. Although not specifically mandated, it would be good practice for a competent person to inspect the new fire doors and the installation works for compliance with the relevant standards. Otherwise, how do you know they are suitable and adequate to provide the necessary fire & smoke protection? Guidance from HM Gov for fire safety in residential buildings can be found here https://www.gov.uk/government/collections/fire-safety-legislation-guidance-for-those-with-legal-duties#guidance-for-residential-buildings-under-the-fire-safety-order

  3. Section 2 of this HM Gov guidance document  https://assets.publishing.service.gov.uk/government/uploads/system/uploads/attachment_data/file/1147631/A_guide_to_making_your_small_block_of_flats_safe_from_fire.pdf   covers the responsibilities of those that own/manage small blocks of flats.

    Note that fire safety legislation requires a suitable and sufficient Fire Risk Assessment to be carried out and kept up to date. Checking the adequacy of the fire doors is part of that Fire Risk Assessment and the document provides guidance on this matter. Refer to page 25 for HM Gov guidance about inspection & maintenance of fire doors.

  4. I have seen similar situations in care homes.  Some FD60(s) and another FD30(s) with no apparent reason for the difference in door specification.  So where FD60(s) doors have been fitted, surely the question would be:  'Is the added fire resistance that these doors have, any material benefit in terms of the safety of the persons at the building and the safety of the fire services entering the building?'

  5. Its most likely that because these are double-leaf doors, the fire resistance performance test included wider intumescent seals at the top edge to mitigate the effects of the extra width (eg. two leaves rather that one)  at a point where the intensity of the heat is greater (eg. heat rises and risk of failure would likely be at the top edge and meeting edges).

    The doors would be manufactured to the same specification as those that were fire tested.

  6. Hi Tony,

    All good thanks 🙂

     

    Q1)  I have been looking at our companies documents on on our fire door survey sheets it requests frame thickness. What does this refer too and how would it be measured please. Again we have no certificates or O&M manual for this door.   A1) The door frame thickness and material is important so that it complies with the certification for the fire door leaf but clearly without certification to refer to you can't check it.  If there's a Certification label or plug on the door leaf you may be able to trace the door leaf to the manufacturer and obtain the certification.  The thickness of the door frame is commonly minimum 30mm thickimage.png.be0038d60afffe926eba82c644f71621.png

    Q2) I have also noticed on one of our double leaf sets. Around the frame it has 1 x 20mm intumescent seal. Where the door meets on the closing edge it has 1 x 10mm. Surely this is in correct? Again we have no certificates or O&M manual for this door.    A2)  Usually there would be one 20mm intumescent seal in the meeting edge of the main leaf or possibly one 10mm seal in both meeting edges but offset, not opposing eachother. Again you need the door leaf certification to find out the exact specification. 

     

  7. This might help  http://firstglass.ie/wp-content/uploads/2019/03/Pilkington-Pyroshield-Pyroshield-2-Comparison.pdf

    Wired glass has traditionally been cut from larger sheets (thus no marking) and used for glazing of fire doors and screens where fire protection is required. The glass will crack in a fire but its fire rating is provided by the wire holding the glass together and this type of glass can be found widely in timber fire doors and glazed screens. In recent years the products have been improved - see Pyroshield 2 (above link) and Pyrostem https://www.pyroguard.eu/all-products/pyrostem/   

    The GGF guide provides best practice guidance for selecting products and installing them where 'fire rated glazing systems' are required.

  8. Hi Mike, Strebord doors with Euro and oval cylinders up to 1400mm up which is good, but as you say it depends on the evidence for the door.  But not for cylinder rim night latches, nada.  Unfortunately.

    If you find one please let me know, that would be really useful. Thanks  🙂

  9. These days cylinder rim night latches are not fitted to fire doors.  There are three main reasons: 1) Lack of availability of fire rated cylinder rim night latches.  2) The installation height for a night latch is usually higher on the door than permitted by the fire test evidence for the fire door leaf.  3) The lock cylinder requires a large diameter hole through the door and this may adversely affect the fire resistance performance of the door. 

    However, its possible that the existing door and lock combination was accepted by Building Control at the time of installation. 

×
×