  1. Yes, I agree its an issue for me too.

    I have some evidence of fire resistance performance for a cylinder rim night latch and it refers to fire resistance performance tests.  In terms of compatibility, I would only install one where I can be certain the type of door is covered by the available test evidence including intumescent protection and location of the device. Even then I wouldn't recommend one due to issues with the self-closer often failing to overcome the resistance from the latch strike.

  2. This looks like an edge seal of intumescent material.  FD120 doors require a greater amount of intumescent edge sealing than lower rated fire doors.  Is there any mark, label or plug on the door enabling traceability to the door manufacturer?  If so it should be possible to answer your question by consulting them.

  3. You will find that third party certificated fire door leaves specify that CE or UKCA hinges to BSEN1935 are a requirement and often certificated too.  Doors fabricated from fire door blanks don't always specify TPC but might require CE or UKCA marking. Building Regulations Approved Document B (appendix C) requires hinges to have a minimum melting point of 800 deg C.   https://www.gov.uk/government/publications/fire-safety-approved-document-b  

  4. From your comments I am unsure whether you are referring to the hardwood door lipping or the intumescent strip?

    The hardwood lipping should be prized away from the door leaf only by just enough so that Cascamite adhesive can be applied to the surfaces that are to be mated. Then use small panel pins to secure the lipping whilst the adhesive dries. You can then either remove the pins afterwards or you can bury the head of the pins into the hardwood lipping and fill over the heads. 

    A loose intumescent strip can be secured to the edge of the door or the door frame reveal using small panel pins. https://www.ifsa.org.uk/ 

  5. Roller bolt type latches are not usually fitted to fire doors. Section 6 of the document 'Code of Practice: Hardware for Fire & Escape Doors' deals with latches and the many fire door related issues concerned with the different types.  The document is available online at http://firecode.org.uk/Code_of_Practice_hardware_for_fire_and_escape_doors.pdf

    Below is particular commentary on Roller Bolt Latches

    image.png.0421f7b8dd281863797ec7f28908f379.png

  6. Hi Richard,

    This is a common problem, installers don't always realise that fire doors have strict trim allowances. If the door has already been trimmed to its max, there's little point in trimming it further just to add timber back again. 

    If you can find a certification label on the door, that enables you to contact the door manufacturer for specific advice. 

    We provide various types of fire door related training but not specifically Responsible Person training for fire safety generally. https://www.firedoorscomplete.com/ 

  7. Based on much-reading of the differing data for many different types of timber fire door construction, I would opine as follows:

    1) Best practice is 6mm min thick lipping after planing-in. So 2mm residual thickness behind the intumescent seal when grooved into the door leaf edge. I have come across assessment reports permitting less than 6mm but I feel that shouldn't be relied on generally.

    2) Urea Formaldehyde based adhesive is suitable for adhering hardwood lipping to timber-based FD30 & FD60 doors.

    3) Cascamite is widely available from online outlets.

    PS. Check thickness of door stiles before trimming. There may be no point trimming them down just to fit thicker lipping, if they are already narrow?

  8.  "I was just under the impression that if this wasn't manufactured and tested this way then the void left by the magnetic locks would be too deep and long to have any suitable repair methods."

    It may be that the void can be filled with suitable timber and adhesive, or replacement may be necessary. Without seeing the door assembly first-hand, its not possible to say. There are some fire door-set and maglock system combinations that are suitably evidenced. Contact some fire door-set suppliers or ask the fire door inspector for assistance.

×
×