  1. Some composite flat entrance fire doors from that period had metallic faces with timber stiles and rails and the core filled with foam.  In my experience these types of doors do not carry any marks and the hinges (as apart of the door-set) or evidence of certification but they may still be fire doors.

    If you require confirmation of likely fire performance, you could engage a fire door inspector that has wide experience with composite fire doors. 

  2. Assuming removal of the Aquamac seal and then moving the hinges inwards into the door frame jamb would resolve the issue. Do that, as it should not cause the door certification to be void. The reverse side of the hinge blades should not be visible. 

    Obviously an alternative seal will be required but these are available.

  3. I am informed that there is no relevant Standard for this type of lock and that therefore CE or UKCA marking is not possible.  If you can trace the fire door to its certification or its manufacturer you should be able to check what type of locks are permitted.

  4. Depends where the door is located. A) Is the door inside the flat/house?   B) Is it a flat entrance door?   C) Is it a door from inside the house to an integral garage?

    Refer to Code of Practice: Hardware for Fire & Escape Doors section 3 'door closing devices'.   http://firecode.org.uk/Code_of_Practice_hardware_for_fire_and_escape_doors.pdf

    If it's B or C it should be a 'controlled' self-closing device.

  5. Make sure the hinges are correctly fitted, that the hinge blades do not protrude and therefore are not causing the door leaf to stand proud of the door frame. Reinstall as necessary.  image.png.fd17378fa260b61c3ac91e951f280bdf.png

    Also, are the door frame rebates sufficient to accommodate the thickness of the door leaf and not causing the door leaf to stand proud of the door frame? Remove and reinstall the planted rebate stops as necessary.

  6. Yes it is. If you are using softwood (redwood or whitewood) for the door frame you can use the same materials for the packers / folding-wedges. But obviously, hardwood or hardwood plywood is more resistant to compression.

  7. 2018 is very recent in terms of timber-based fire door Standards.  It may well be the case that the door manufacturer's fire performance certification requires that the hinges be UKCA or CE marked to the correct fire rating and durability rating in accordance with BS EN 1935: 2002. 

    Similarly, the same door certification may require that the lock/latch-set has intumescent protection and the security viewer too.

    Contact the fire door surveyor, they should be able to provide the product certification details for the door and the specification for the hinges and intumescent protection gaskets. 

  8. Whilst there is currently no legal requirement for fire door installers & maintainers to possess a dedicated qualification, competence is necessary. The Regulatory Reform (Fire Safety) Order 2005 requires those that provide fire safety related services to be ‘Competent Persons’.  Regulation 7 of the Building Regulations covers workmanship and materials. Subsequent to the Hackitt Report there are industry led working groups looking at what competence should look like in the future and you may find the report ‘A Higher Bar’ interesting at   https://www.cic.org.uk/shop/a-higher-bar-achieving-a-competence-led-built-environment  It is expected that in future regulated qualifications may become either a mandatory requirement or at least a strong recommendation.

     

    However, there is currently no mandatory requirement for fire door installer & maintainer training but many clients such as housing associations, healthcare organisations and education providers now require that those that install or maintain fire doors have a qualification or certification as proof of competence to perform those works.

×
×