  1. Better to change the door frames to suit the new doors.

    If that's not possible either order custom made fire doors from a competent supplier or if you have the necessary knowledge, skills and experience you could purchase fire door blanks and fabricate the doors yourself in accordance with it's relevant technical manual. 

  2. Better to change the door frames to suit the new doors.

    If that's not possible either order custom made fire doors from a competent supplier or if you have the necessary knowledge, skills and experience you could purchase fire door blanks and fabricate the doors yourself in accordance with it's relevant technical manual. 

  3. Look for any marks, certification labels, plugs or other signs on the door so that you can trace it to its manufacturer.  Then you can obtain the door data sheet or installation instructions and that document will tell you what type of intumescent seals are required and how they should be positioned. 

    If you can't trace back to a manufacturer consult a fire door specialist with all the available information about the doors, so that they can advise appropriately. 

  4. Smoke seals to fire doors are necessary for fire doors opening onto escape routes and in locations where sleeping accommodation exists. Of course there are other areas where they might be necessary too. Consult Annex C of the Building Regulations Approved Document B for information.

    Compression type batwing seals or those held in a carrier and fitted to the door frame stop might work better.

    image.png.d1064b7e14bcb9f8799cbd7964cf1ad6.png

  5. From what you say, this door appears to be a timber-based Nominal Fire Door or Notional Fire Door.  That being the case, lipping the top and bottom edges with suitable hardwood and using urea formaldehyde based adhesive would be a suitable repair. Planing the hanging edge by 1mm would also be a suitable repair. 

    An alternative repair for the threshold gap could be to install a threshold plate to the floor, under the door. 

  6. Because its a Nominal fire door there is no evidence of fire performance for the door. Because their is no evidence there is no way of checking whether or not glazing is permitted and to what specification. Therefore it remains a Nominal Fire Door but check the glass for evidence of fire resistance, such as a mark in the corner of the panel and check that beads, gaskets and fixings appear to be suitable.

    Always do your utmost to make sure that it really is a nominal fire door and not a certificated or evidenced fire door but with the certification/evidence marks removed or obscured. Also, still carry out an inspection for fire safety order compliance purposes.

  7. The document Hardware for Fire & Escape Doors available at  http://firecode.org.uk/Code_of_Practice_hardware_for_fire_and_escape_doors.pdf    contains some very useful information about hinges including Critical Recommendations at section 2.2. The information therein should enable you to decide an appropriate course of action. 

    For metal faced timber-based fire resisting doors it will be necessary to consult the technical manual for the 'specific fire door leaf' to find out what is permitted in terms of fire resistance performance. eg  image.png.1d5a4a5910fb444fd5460355948bbf66.png

  8. The recommendation is 2mm to 4mm.  More than 4mm could be an issue affecting the restricted spread of smoke and potentially premature failure of the door in a fire.  Less than 2mm could mean that the door fails to self-close and latch correctly (eg. due to binding on a smoke seal), therefore inspect each door to make sure any tight gaps do not affect the ability of the door to self-close completely. 

  9. No but assuming the door/frame is timber, stainless steel would be best.  Before you go ahead make sure the groove for the seals is clean and consistently of the right depth and width to match the seals.

×
×