  1. No - a purpose built block can be almost any size without a fire alarm. Modern blocks will have smoke detectors to open smoke vents to stairs and long corridors/lobbies (which are often also connected to sounders and manual fire alarm call points even though they needn't be and shouldn't be) but not fire alarm systems for full escape.

    A common alarm system for full evacuation would usually be to the commercial fire alarm standard BS5839-1 with manual call points (break glass units), smoke detection to the common areas, heat detectors to the flat lobbies and alarm sounders to the common areas and flats lobbies, all connected to control and indicating equipment:

    xctmpTh77vZ.png

    This is different equipment to the residential fire alarm standard BS5839-6 which you would see in your flat, consisting of self contained smoke and heat detectors with integral sounders and fed off the mains with a battery back up and often (not always) linked together with bell wire or via radio link:

    fire-angel-pro-mains-powered-alarms.jpg

  2. Never said that they required maintained internally illuminated exit signs, just places of assembly. However by default all new installations seem to have them, usually a BCO/AI thing, so a requirement for Building Regs.

    A supermarket can, as I said, have a normal sign as long as there is EL nearby - or just use an exit box instead

  3. Depends if the boarding up was done legitimately with Building Control approval, if so brick it up! If unsure ask your Local Authority Building Control office for advise first.

    Exits through other premises aren't favoured these days so where other precautions can remove the need for them to be retained they are removed. Also if there isn't a legal easement to allow legal travel from one property to another it can be bricked up in any case.

  4. Glow in the dark signs do not excuse adequate lighting unless part of a full way guidance system and subject to constant exposure to light to stay 'charged' but they are a good selling point for the installers.

    A standard self adhesive vinyl or rigid plastic exit sign will suffice as long as it has a suitable emergency lighting fitting within 2m producing sufficient light output.

    Internally illuminated exit boxes are usually needed(& indeed were traditionally a legal requirement for decades)in places of assembly operating in the 'Maintained' mode. They are usually also installed by default in new installations.

  5. I'd be minded to upgrade the door and detection as it's directly onto a stair in a sleeping risk building - I wouldn't want to risk a vertical escape route. If it had only been onto a horizontal escape there may have been the possibility of adding detection only initially if it was modern boiler equipment that could accept smoke detection without false alarm risk and upgrading the door set later.

    Of course both is best as it's difficult to excuse only a single room upgrade as it should hardly be a capital expenditure.

  6. For many years a compliant installation would have had an EL fitting outside each final fire exit and to external stairs, but the 2017 update to the standards now includes cover to the external route to a place of ultimate safety. It's not automatically retrospective, but Fire Risk Assessments need to judge if the risk by not updating is tolerable or not- some places will need it, others not. 

  7. Is this on an ancillary accommodation level along with other plant, store rooms, staff rooms, etc or on a floor with bedrooms?

    This would influence whether you need to both upgrade the original notional fire door and add detection, although being on an escape route and in sleeping risk premises there is a leaning towards doing both. 

  8. Usually the leaseholder, but you need to check your actual lease. Where a leaseholder refuses to act then the local authority can take legal action against them under the Housing Act 2004.

    If the door is an original fire door (not current spec) and still in good repair then depending on the size of block and risk it may only require a modern self closer - one group of tenants were able to win a civil case against the freeholder who replaced all the doors with current FD30S doors beyond the terms of the lease - the original doors were not properly checked, were actually still in original good repair and didn't need a full immediate upgrade for the type of block.

  9. Or worse an electromechanical lock which would not be permitted on escape routes where it relies on the release of the electrical keep as they are known to jam under pressure. They are only suitable where from the inside the latch can be withdrawn without the keep release by the form of mechanical means such as a thumb turn.

  10. Simultaneous evacuation is a last resort in purpose built housing and is only to be used where a building has insufficient compartmentation to support stay put and it is not viable to upgrade it.. 

    For evacuation the common fire alarm system must extend into the flats with a minimum of a heat detector to the hallway with an alarm sounder so that the fire is discovered before it breaks into the common areas preventing escape and so that 85dB sound pressure is present outside the bedroom door so as to wake sleeping occupiers. In very poorly constructed premises the system would need to be even more comprehensive.

    Your premises sounds like it was built for stay put but you've had an unnecessary alarm system stuck in - I would ask to see the Fire Risk Assessment for the block.

  11. If it's a purpose built block of flats built after 1962 and the compartmentation is still OK then a communal alarm is not usually required and can be counterproductive. If the premises have a automatic smoke control system (vents, shafts, etc) then you will need to keep the system to operate these (unless the smoke vents have their own detectors) but can remove call points and sounders.

    If the premises are a conversion or in poor condition some form of site wide system may be required.

    A competent Fire Risk Assessment should determine if you can remove the system, I've allowed this in several sites in my FRA

     

     

  12. Is this a HMO, converted house or purpose built flats? First question would be does it even need the alarm (I'm guessing it's a conversion so requires the system but it's not unknown for OTT systems to be put in).

    If the system is required for the protection of relevant persons under the Fire Safety Order then it has to be maintained correctly so the call points and more importantly the detectors inside flats that are off the common system must be accessed for maintenance - even if you have to resort to legal action to effect entry under the lease terms. A very large apartment block in a major city that I dealt with in the past has this issue, but with domestic sprinklers - the valves for each flats system had been put inside each flat rather than a meter cupboard off the corridor so access for maintenance was difficult but the landlord/freeholder was facing prosecution if they didn't do this even if they could only get to force entry to do this via the courts (the sprinklers were also part of the communal fire strategy rather than just individual flat protection so the Fire Safety Order applied ).

    Even if a communal system is required it's an odd set up to have call points in the flats, as part of a FRA review I'd ask the design to be reviewed to see if the call points can be removed from the actual flats, meaning you only have to get in once a year to test the detector.

  13. Depends on the structural separation. You need to carry out a Fire Risk Assessment for a definitive answer, without carrying one out on site I can't give a definitive answer.

    Has the change of use of the flats had the correct planning and building control permissions?

    https://www.planningportal.co.uk/info/200130/common_projects/50/shops

    This would have in part looked at the issue (but not for the whole premises and not in place of an FRA)

  14. If the cavity barriers are suitably located and correctly constructed so a fire on the landing (unlikely anyway)cannot spread beyond the void above to threaten the adjacent flats from above then it's tolerable - the use of cavity barriers is the main protection anyway as fire rated ceilings in lieu of them are not considered good practice as they are more vulnerable

×
×