  1. Ask which British Standard the FRA is referring to - it's not unknown for them to be quoting wrongly!

    The maintenance intervals is BS7273-4 will be taken as the benchmark in any legal case or audit. It is possible to have a different regime of testing, but only if it can be demonstrated that it provides an equal level of safety proportionate to the risk. Sainsburys did this with their fire alarm testing, but had to do a lot of data analysis to prove their point (helped by their detailed records, otherwise they would have been stuck.)

    The intervals mirror fire alarm intervals, although the weekly test there isn't of all call points, just different ones in rotation, perhaps a similar regime with your green releases would be easier to implement

  2. Yes. With stored pressure extinguishers you cannot 100% ensure they will work or are in safe condition just by the annual basic service.

    The discharge test, strip down and internal examination is the only way of detecting defects affecting safety or efficacy. Stuck gauges on leaky valves, internal corrosion, detached diptubes, etc.  Also the extinguishing agent deteriorates with age and requires renewal to maintained efficacy.

    Before end disposal we often use 5+ year old extinguishers on training courses (where failure to operate is less of an issue and we take more than we need) and it's not as uncommon as you might think where they fail or do not perform as well as designed.

    The user servicable P50 range (available from Safelincs) does have the benefit of a 10 year interval between tests and you can do the annual check in house.

  3. Probably coincidence. There has been no change in legislation or risk assessment guidance (other than specific guidance for premises with cladding issues). What has happened is that many housing providers have urgently reviewed their fire safety management and risk assessments and issues that crop up as a result are being addressed.

    It may be that your evacuation procedure has been changed as a result of your FRA so the full width is required to accommodate the evacuation of all flats as once rather than just the flat of fire origin initially, or that they deem the equipment an unacceptable ignition risk in what should be a fire/ignition sterile area.

     

  4. As Tom says. If the Government Guides lead to an untenable situation then Fire Engineering is sometimes an option as is the correct use of BS9999 (in whole not cherry picking sections) - but the later does't always work out. I used BS9999 to try and design out installing a third stair in a conversion of a mill into offices due to excess travel distances, but the upgrading in floor fire resistance, shafts and provision of fire service rising mains associated with a BS9999 design ended up making the traditional benchmark approach easier and cheaper!

  5. Not necessarily, the legislation is not intended to be unduly burdensome and guidance is provided for responsible persons to conduct their own FRAs.

    Having said that whoever does the FRA needs to be competent. In simple premises it could be the RP using the guides, where more complex the RP or an employee would need to have suitable training as well as the guides. Where the RP or their employees are not suitably competent then a suitable external contractor should be used, preferably one with third party certification such as BAFE SP205 or Warrington FIRAS.

    Regardless of whoever does it you will need an FRA for the common parts of the block 

  6. BS8214:2008 has been withdrawn, sadly councils are often poor at keeping up with standards even where responsible for fire safety enforcement and BS8214:2016 is the current edition.

    A fire door is only as good as it's frame and surrounding construction - the whole doorset must be compliant. Go to the BWF website to find a certified installer of fire doors/doorsets so you will be assured it's OK.

    We use Ventro for all our fire door work- http://www.ventrogroup.com/

     

  7. A dead end is simply a corridor (or similar) where you can only go in one direction, if you go down the other end you end up against a brick wall.

    Either it is protected by fire doors and walls to the rooms off it or the whole area is protected by automatic fire detection

    image.png.2b763e894597217270713470f489a4ba.png

     

    image.png.ce5623d8d7e2a435139beec7225a10d3.png

  8. As Tom says BS9999 cautions against using it in FRAs in the first place (unless the property was designed and built to it) and against cherry picking which is not accepted.

    If the premises can meet the whole document in terms of it's design, build and management it's OK to use.

    You have to go by the narrowest point as if you over occupy based on the higher widths elsewhere you will get a potentially fatal pinch point (as was the case in the layout of the Station Nightclub where many of the 100 dead got stuck in a crush)

  9. The 1 hour/3 hour requirements are a bit of a throwback to the early days of emergency lighting when both types of fitting were available (both self contained and central battery) and technology was such that central battery systems were more common as they were the easiest way of getting 3 hours duration, self contained fittings technology was such that 1 hour was what you could easily manufacture using the technology. Therefore most applications in single stage evacuation premises would be 1 hour and the standards only asked for this as it was considered sufficient for the occupancy and risk.

     

    Technological advances soon meant that fittings could be produced with 3 hours duration that were the same size and almost same price as the old 1 hour fittings and to avoid duplication in manufacture 1 hour fittings were dropped by the majority of manufacturers several decades ago (you can still get them if you search hard). The standards however have not been updated to reflect the change in technologies available.

     

    As such virtually all fittings installed are of 3 hours duration, regardless of the minimum duration required for different Purpose Groups.

     

    BS 5266-1: 2016 has the following PPM regime:

     

    Functional operation should be checked at least every month.

    Testing for full rated duration should be performed on each luminaire at least annually.

    As the full rated duration of emergency lighting fittings is now almost universally 3 hours, as it is so long since 1 hour units were widely available and used, then it is correct to expect full duration tests.

     

    The 6 monthly partial duration test was removed in part due to the deleterious effect on NiCad battery cell life as most systems use this technology compared to back in the late 20th century when there were a lot of lead acid battery central systems and other battery technologies and full discharge cycling is recommended for this battery type. (With Lithium Ion batteries as used in phones the opposite is actually the case)

     

    The point over loss of service during recharge times is correct, hence on weekday operation premises it's best to schedule tests for Fridays. In premises with wider hours of operation then testing should be either at times of minimal risk (low occupancy, summer, etc) or alternate testing of units should be carried out.

     

    Testing a 3 hour system for 1 hour falls outside of BS recommendations and will have a deleterious effect on fittings (eventually the safety factor will be lost as they will eventually last for less and less than 3 hours down to 1 hour) and would not normally be accepted although it can be considered on a case by case basis

  10. Up to risk assessment - some places with similar issues use magnetic locks linked to the fire alarm in addition to the push bars.

    If the exit is serving less than 60 persons and there is suitable staffing to manage the fact that there would be two actions instead of one to open the door then it's not impossible to justify.

    Consideration should be given to whether the risk to the absconder from their ease of escape is greater than the risk from the exit no longer being panic proof and that in any case the risk from the latter is not itself intolerable.

  11. CO2 doesn't decay and of all the types of extinguisher they are the type most likely to still work if left sitting in a corner unchecked and unused for years.

    They can leak, usually from a cracked neck or defective neck or valve seat O rings, but this is rarer than in once was (it was an issue with early aluminium cylinders in the 60's, 70's and early 80's)

  12. No problem, saves me typing it out again!

    The environment, occupancy/persons at risk and fire risks all are part of the factors to consider - most places I deal with they are removed/not installed, but there are exceptions.

    Powder is often installed in general commercial premises for Class C (gas) risks, overlooking completely the fact that tackling a class C fire other than by simply shutting off the gas supply is a specialist and potentially hazardous job and that the staff in these premises are not trained or equipped to do so (all 'general' fire safety training including extinguisher courses trains staff not to extinguish a gas jet fire) - the BS acknowledges this and so boiler rooms and gas intakes etc don't really need powder at all...

  13. 3 hours ago, JardCrocker said:

    Hi...i am a new user here. As per my knowledge often they will check 25% of the alarm, each service, so by the time 12 months have passed everything will have been checked, That is also why is some places you will see devices with small coloured dots stuck on them. its so they know which device was tested in which quarter.

    Whilst you still may opt to do four 25% services a year it's not been required for a long time. Currently you need to cover 100% of the system within twelve months over a minimum of two visits not exceeding 6 months. Many sites now only have two 50% visits a year

  14. Nope, you are getting mixed up with BS5306-3 for extinguishers which has a +/- 1 month for basic & extended services.

    BS5839-1 states service visit intervals should not exceed 6 months or the system will be deemed to be non compliant. Quarterly servicing hasn't been a minimum requirement for a very long time now.

  15. Certain environments will require specific training and a standard online course may be unsuitable - e.g. Care  Homes where the fire risks, evacuation strategies and staff duties are far different from those in normal premises.

    You need to check the contents of the course against the procedures, roles and responsibilities in your premises. Some organisations offer sector specific versions of their courses (e.g. https://www.i2comply.com/firesafetyschooltraining.aspx?gclid=Cj0KCQiAlpDQBRDmARIsAAW6-DOGEoE6febQAlNY1d_mjDNs9kUlP1OZgOztu-fYPRVYu5B71YI08F0aAkE-EALw_wcB & http://www.healthandcare.co.uk/online-health-and-safety-training-courses/fire-safety-for-schools-online-health-and-safety-training-with-certification.html)

    However you may find you could use a general course supplemented by information on local procedures, although sector specific is obviously preferred. 

  16. The stairwell is required to be what is a protected route, which should have at least 30 minutes fire resistance from a fire on any of the floors and itself be fire sterile so a fire does not start within it. This is why there are thousands of buildings in the UK, including new builds, with only one stair and all safe and legal.

    The FRA should check that this situation is OK - as well as limits on travel distance and required exit widths there are limits on occupancy on a particular floor - as you are using the area as offices you require 6sq.m. per person and you could be overloading the floor

  17. In a building of the size you are in there should be no reason to not be able to add the detector to your existing panel (unless it's something very weird and obsolete with no spares made), you are unlikely to have exceeded your zone device limits or loop loadings, this wasn't accompanied by a quote to put in a whole new system to achieve this by any chance?

    If the detection is only required to give a local warning (e.g. an inner room situation) then you could use BS5839 Part 6 Grade D (mains & battery back up) domestic smoke alarms with radio link bases, although strictly speaking you should be extending the BS5839 Part 1 commercial system.

    If a more wider warning is needed then you have no option but to extend the commercial system.

    By across the escape route do you mean you have to pass through the room to exit? IT room detection is usually recommended for property protection only and not statutory life safety compliance unless the building overall needs a high level of cover (note that normal offices don't require detection at all unless multioccupied and then usually only to limited areas)

×
×