  1. That's because a compliant risk assessment requires a lot of information - a relatively short example is in here https://assets.publishing.service.gov.uk/government/uploads/system/uploads/attachment_data/file/422175/9449_Offices_and_Shops_v2.pdf
  2. I'd agree, if it's the original hard wired kitchen device it will be a heat alarm, not a smoke alarm - look here for the differences in appearance https://www.safelincs.co.uk/smoke-alarms/
  3. Your tenant is wrong - the Grade A communal system need only provide a heat detector and sounder in the hallway of each flat to support the full evacuation strategy required as a pre 1990's flat conversion. The self contained Grade D system already in the flats is there for the individual flat occupiers protection from a fire in their demise and if installed previously is likely to have been to the minimum standard of the time, LD3, which would only require a smoke alarm in the hall. New installations in flats would usually be LD2, as would upgrades for existing and this is when you would get a heat alarm in the kitchen linked to the hall smoke alarm (not the common system) Both Grade A & Grade D systems are common as wireless linked systems which might be an option.
  4. Did the person telling you that you would be shut down work for a furniture or fire treatment company? You wouldn't get a Prohibition Notice for that and it's not even checked during routine audits. Some guidance is here https://www.fira.co.uk/images/FIRA-Contract-Flammability-Guide-2011.pdf
  5. Yes, external emergency lighting has been required for decades and has always been subject to the same testing regime as other emergency lights as set down in BS5266. Either your previous company wasn't doing a proper job (quite possible, sadly) or they were fine before.
  6. I'm used to houses of more than one storey and flats in blocks, the latter using the protected hall approach and requiring the requisite doors as per Table C. At the end of the day it's a Building Control matter and LABC or your AI will decide how to interpret the guidance. Mostly the internal doors are FD20 doors, which is usually an FD30 blank without the intumescent strips. Every new build flat I've been to has this set up.
  7. Yes, it refers to a fire being sensed by a human (sight/smell/heard/felt) with them subsequently raising the alarm in a manual manner, which in a very small single storey premises may be a shout or a whistle/horn/gong and in larger buildings activation of a manual call point in an electrical fire alarm system.
  8. It's perfectly legal and if you are in flats the door should already be like this anyway. https://www.ironmongerydirect.co.uk/search?query=mortice thumbturn https://www.ironmongerydirect.co.uk/browse/locks-latches-and-security/filter/%24s%3Deuro cylinder thumbturns?fi=c
  9. You will find your answers here: https://assets.publishing.service.gov.uk/government/uploads/system/uploads/attachment_data/file/832631/Approved_Document_B__fire_safety__volume_1_-_2019_edition.pdf In the old days often only kitchen and living room doors were fire doors, now they all have to be other than the bathroom. They don't, however, need self closers or intumescent strips.
  10. It's purely a convenience factor - for use in high traffic areas where the doors being closed would hinder circulation leading to the doors being wedged or damaged (the later particularly where trolleys of goods are pushed through). The hold opens will ensure the doors can always shut when they need to be.
  11. Your agent is applying the 'zero tolerance' approach detailed in Government fire safety guidance as it is the easiest to implement and leaves no ambiguity as to what can be placed in the common areas. However the guidance does offer an alternative which is ‘managed use’. This approach allows strictly defined use of common parts and limits the items allowed, to control fire load and ease of ignition. It includes strict conditions on where such items can be kept. For example, a ‘managed use’ policy might permit residents to: • place pot plants and door mats outside their front doors • have framed pictures and notice boards on walls • store bicycles, prams and mobility scooters in places that are out of the way and not likely to cause obstruction. It's not popular with agents as it requires a lot more hands on management and a bigger liability risk, but I have assessed premises where it has been effective due to the residents being proactive in monitoring compliance themselves.
  12. They are not there to aid in escape, and as they are fire extinguishers their very purpose is to fight a fire! The clue is in the name.... From the Government Guidance: It is not normally considered necessary to provide fire extinguishers or hose reels in the common parts of blocks of flats. Such equipment should only be used by those trained in its use. It is not considered appropriate or practicable for residents in a block of flats to receive such training. In addition, if a fire occurs in a flat, the provision of fire extinguishing appliances in the common parts might encourage the occupants of the flat to enter the common parts to obtain an appliance and return to their flat to fight the fire. Such a procedure is inappropriate The common parts are your escape route and as such are constructed such that they will be safe from fire for considerable time and should not have a fire starting in them (unless someone has broken the law and introduced fire risks into this area). A typical water or foam extinguisher is unsuitable for most fire risks in flats, which are usually of cooking or electrical nature. Communal circulation areas are (or should be) fire sterile forming part of the protected escape route for the building and should only include basic carpeting and wall coverings that would not be involved in a fire, if at all, until well after conditions in the area would be fatal to human life. You would be best placed in removing them and making a saving in the residents service charge budget that can be better spent on other things.
  13. As it's a private dwelling the internal door requirements are not retrospective, fire safety legislation does not cover these areas. (If used as a HMO or similar this would be different)
  14. Fixed ladders are not normally accepted as means of escape under regulations and guidance, however an exception is made for areas that are infrequently used or only resorted to by small numbers, usually under 5, and only staff no public. So it's not out of the question - bear in mind this assumes all users are fit and able bodied.
  15. No, if not communal they are not subject to the Fire Safety Order. The only aspect of your flat that is relevant is that bordering the common areas such as the front door and any communal ducting passing through.
  16. If it's new build the designers may have used BS9999 instead of ADB as it can reduce the number of exits and stairs needed - it may also be fire engineered. The design fire strategy will give you the answers you seek.
  17. https://www.local.gov.uk/sites/default/files/documents/fire-safety-purpose-built-04b.pdf
  18. Not sure if you have already looked but this is pretty much the guide for existing flats https://www.local.gov.uk/sites/default/files/documents/fire-safety-purpose-built-04b.pdf
  19. Normally windows don't have a fire safety role in the common areas of flats as smoke control is provided in other ways - so they aren't addressed by BS9991 or ADB as they aren't a fire safety feature. The openability of windows only becomes a concern when there are no openable vents, AOV's or smoke shafts.
  20. In small existing older blocks of certain configurations openable windows can replace the automatic vents or openable vents that would normally be required for smoke control.
  21. Is this a suite within a larger building or a self contained premises - depending on size and layout you may not actually need anything to meet minimum legal requirements.
  22. Most carts of this nature have a cheap ABC Powder extinguisher, usually around the 600g- 2kg size range. It's rather messy in use and a cleaner (but more expensive) alternate is the 1.4l Water Mist extinguisher. https://www.safelincs.co.uk/ultrafire-redline-1kg-abc-dry-powder-fire-extinguisher/ https://www.safelincs.co.uk/1-litre-water-mist-fire-extinguisher-ultrafire/
  23. You need to commission a fire risk assessor to carry out a full FRA. However, based on the information the premises seem small enough in scope for the 'Do you have paying guests' guidance to apply which is more sympathetic than the standard Sleeping Premises guidance and allows the use of a Grade D residential smoke alarm system throughout instead. https://www.gov.uk/government/publications/do-you-have-paying-guests
  24. AnthonyB

    Mr

    You will be likely to be subject to Building Regulations and so your proposals and plans should go to Local Authority Building Control who will advise what you must do. In any case you need a Fire Risk Assessment. If you could upload a sketch plan of the layout I can give some pointers. Guidance sources: https://assets.publishing.service.gov.uk/government/uploads/system/uploads/attachment_data/file/422175/9449_Offices_and_Shops_v2.pdf https://assets.publishing.service.gov.uk/government/uploads/system/uploads/attachment_data/file/832633/Approved_Document_B__fire_safety__volume_2_-_2019_edition.pdf
  25. AnthonyB

    "MES"

    I assume you mean the Gloria brand of fire extinguishers? What type and size is it as the markings vary. It's likely to be the manufacture month and year, although as you are supposed to be having them serviced every year it shouldn't be an issue if being done properly...however....it would be unusual to see an extinguisher this old (if not CO2) still in service if being correctly serviced unless you have a traditional fire protection firm that is taking the extinguishers out of the building every 5 years to discharge, internally inspect and refill rather than just replace with new.
×
×