A suitable system of maintenance is required by the legislation, your FRA should determine the frequency. The Government never intended the cash cow of every inspection being a full in depth check - this is detailed in the guidance to the Fire Safety (England) Regulations. Usually where the doorset has been established by specialist inspection to be fully compliant the wear & tear checks can follow the style of the FS(E)Checklist and can be done in house although some basic training is recommended. Professional checks would still be of use if there have been any alterations or changes, any issues found on the in house checks where 'seek professional advice' is the result and every few years as a backstop
-
Panelled FD30s doors - minimum thickness
AnthonyB replied to strugglinauthor's topic in Fire Doors and Accessories
Fire doors are seen as a cash cow and many smaller blocks are suffering from unnecessary burdens to the lease/common holders due to incorrect advice on doors that does not follow Government guidance. In many of these blocks the original fire doors remain suitable as long as in good order and the only critical issues are related to doors not self closing properly/at all or doors replaced by non fire rated doors. -
Sounds like you may need to use a professional risk assessor if you aren't sure - but in essence travel distances and exit capacities are different issues. If you have two or more exits (that meet the 45 degree rule or are separated by fire resisting construction) you can use the Travel distances listed for more than one direction of escape (but be aware that initial dead ends where you can only go one way must meet the single distance up to the point that routes diverge). Then you need to ensure the number and width of exits is enough for the occupancy - you always discount the widest exit for this just in case the fire blocks access. The extract in the above reply is fro Approved Document B, a design guide under the Building Regulations for new premises - existing ones should use this - https://www.gov.uk/government/publications/fire-safety-risk-assessment-offices-and-shops Useful extracts:
-
Possibly, but without seeing it for myself I can't be definitive.
-
You (well the block freeholder or commoners) are legally required to have a fire risk assessment which will address this. Fire doors will be required to the front doors of flats opening into the single internal shared stair, however if these are the original flat fire doors and ironmongery and in good working order they will not need replacement - usually the main fault with these is no self closer or one that doesn't work fully (usually as it's a single chain closer) and this can be replaced with a modern EN1154 closer to overcome this. If a door has been changed from the original fire door and is no longer a fire door then this would need replacement. Internal doors within flats are not covered by the legislation affecting the block. For your block only one guide applies & that is here- https://www.gov.uk/government/publications/making-your-small-block-of-flats-safe-from-fire
-
Firstly it's up to 4mm usually and there has been no change in building regulations affecting flat front doors and in any case the Building Regulations do not retrospectively apply to existing buildings unless being altered. Official guidance for front doors in flats allows varying standards of door dependant on the size and layout of the block - there is a fair chance no doors need replacing.
-
Discounting the widest if there is any slight chance you are going to have over 60 persons going through a doorway it needs to open outwards. Panicking public, especially if intoxicated will head en masse to the exit they came in and history is littered with the bodies of the hundreds who have crushed up and died against inward opening doors
-
Usually, yes unless secured in the open position at material times, especially as most guests will go back out that way even if they pass a fire exit on the way.
-
If it's not boarded then the shop fire alarm will need detection throughout and sounders into the flat. The flat's system wouldn't normally need a smoke alarm at the foot of the stairs, but would require one to the stair head & internal hallway plus ideally one to the principal habitable room and a heat alarm to the kitchen
-
-
Is it a bolted leaf not normally in use? If so it's a bit OTT. If its a closer fitted in use leaf then there is slightly more justification. Technically they are right but it's not risk proportionate, won't affect life safety & won't be enforced
-
If it already has the boarding you don't need to add more. A 60 minute suspended ceiling grid may be an option, but only if there is no risk in the void
-
As above, it's very ill informed & wrong to say they are illegal. HV fires from a H&S point of view are not safe for first aid attack with any type of extinguisher unless electrically dead in any case. Of note should be the fact that live 11kV transformers are sometimes protected by water mist/emulsifying sprinkler heads! A Powder P50 is an option, they were never banned for indoor use & in the latest revision of BS5306-8 any mention against not using powder indoors has been removed.
-
Do interlocked chairs impede fire evacuation?
AnthonyB replied to a topic in Fire Safety in Village Halls
They can be - these guides are published under Article 50 of the Fire Safety Order where not following them tends to prove the law was breached in any enforcement action or prosecution, so unless you have robust justification as to why you haven't followed them and how your alternative measures still provide equal safety then you are in trouble - ignoring them just because they are a guide won't cut it -
Fire door inspecting at a business with over 200 doors
AnthonyB replied to Robbie's topic in Fire Exits
It's not a month in any guidance, but 6 months for thorough examination (3 months if high traffic). Monthly is only for a brief cursory check as part of general monthly fire safety housekeeping walkthroughs -
Guidance would be used as the benchmark as to what would meet the functional standards of the law. If you don't follow it you must be able to demonstrate why your alternative regime still affords an equal level of safety in relation to the risk and it must be more than 'it's too much trouble', ;we don't have the time' or 'it costs too much'. Remember that whilst 'guidance' that "where in any proceedings it is alleged that a person has contravened a provision of articles 8 to 22B or of regulations made under article 24: (a)proof of a failure to comply with any applicable guidance may be relied on as tending to establish that there was such a contravention" Deviation is possible (Sainsbury's justifying weekly fire alarm test for example) but requires a lot of work to establish why it's justifiable.
-
Your fire risk assessment, a legal requirement in ALL premises should address this. It all depends on the fire separation between the chip shop & apartment - if it can be proven to be 60 minutes fire resistance then you won't need the building wide fire alarm system, just the Part 6 Grade D smoke/heat alarms to the flat and (if required, it may not need it in this case)a separate Part 1 system just to the Chip Shop
-
I have four questions: 1. Has anyone seen, or recommended, FD30S doors to be installed to rooms within flats? No, the requirement where a flat was built to Building Regulations has never been FD30s, originally it was fire check doors, then FD20 doors and currently FD30 doors. 2. Is an upgrade to FD30S the correct recommendation for all flat entrance doors, converted and purpose-built, regardless of where the government guidance says it is not necessary? It's not necessary or proportionate, the guidance was written to balance adequate safety with not burdening home owners with excessive costs (from £800-£3000) 3. I have also read fire risk assessments, and seen fire safety advice on company websites, that suggest an 8mm or 10mm gap at the bottom of an upgraded FD30S door, but I read this as <4mm without a threshold seal or <3mm with a drop seal. Which is the correct line? One for our resident fire door expert Neil, but if it's upgraded to achieve a notional FD30S I would expect that to include the threshold gap using a drop down seal or hardwood lipping 4. I know advice can change with risk assessment, but Is there a definitive guide on fire doors in converted flats? Or a summary that pulls together all of the guidance for converted flats and purpose built flats? A replacement for the LACORS guide is under preparation (& has been since about 2019, but was in hiatus for several years) and is by the authors of the Purpose Built Flats guide so will be in the same vein and use the same principles and thus not be as conflicting This has been discussed before and I have read almost all of the previous posts without forming a clear idea of what would satisfy any enforcing authority. The guides have status under Article 50 of the Fire Safety Order such that following them would see a premises 'deem to satisfy' the requirements of the legislation as long as correctly applied for a particular scenario
-
Take the door and frame out, skip them, move the bed in, fit a new certified FD30S doorset (frame, door & ironmongery all compatible and installed to manufacturers specification & test certificate), job done. Whilst not to current building regulations if a new build or new conversion, as an existing door set official guidance for the fire regulations (separate legislation) will tolerate 'notional doors' and 'upgraded notional doors' in certain circumstances and whilst the Perko single chains are known to have been a poor choice for decades aren't specifically excluded if still shutting a door flush (only rising butt hinges are) so the door may have been acceptable for existing purposes - but it doesn't look in the best of conditions and if having to complete building work to get the bed in it's time to modernise!
-
Existing Notional Fire Door Remedial Work or Replacement?
AnthonyB replied to nigelh's topic in Fire Doors and Accessories
Your block is not a new build - it is completely wrong and against both Government guidance (which if you follow is proof you are legally compliant with the legislation under Article 50) and the recognised fire risk assessment methodology PAS79 to try and apply Approved Document B, a guide for the design of new buildings not assessing existing ones, retrospectively. I know who they are and I know the standard of their work, feel free to take this offline - PM me or email me. -
Fire Resistance for different purpose groups
AnthonyB replied to Paul B's topic in Fire Risk Assessments
Not really, it's a single compartment building due to size, depending on void contents and the risk assessed fire alarm category you might need detection up their, but for life safety it's not proportionate -
I wouldn't expect AOV even on a new build with that layout as the stair is remote from the risk. Compliant at the time of the build hasn't been acceptable as an automatic get out for fire safety since 2006 (it's not the same as Building Regulations that retain the hard stop on backward application) and the risk assessment determines whether the existing precautions still provide an adequate level of safety (some are proven to be now ineffective), some part modernisation or mitigation is needed, or, full modernisation is required. A good example is the guidance around fire doors in blocks of flats - sometimes original notional doors can remain, sometimes they need modernising with intumescent seals & smoke brushes and in some cases whole door sets need replacement with certified new ones. Based on the risk as presented (but with the caveat I've not been there and only have your description) I don't see a need for retrospective smoke control either!
-
PAS9980 addresses this (particularly the new version in draft if published as it stands) with very small buildings like this being low risk, but if in doubt ask a competent FRAEW assessor as to their thoughts, although a full FRAEW is unlikely to be required