  1. The door to be upgraded would require inspection by a competent person before recommending upgrading products and materials.
  2. In the UK, various materials are used for the core of a fire resisting door. The most common is timber and/or chipboard but some composite fire doors have a core of foam within a timber frame. Metal fire doors are also available. British Standards for fire doors are for fire resistance performance tests rather that construction materials. Refer to BS 476 part 22 : 1987 and BSEN 1634-1 : 2014
  3. Any door in a shared wall between a garage and dwelling house should be a self-closing FD30(s) fire resisting door.
  4. In terms of compliance with the British Standard, that would not be a suitable solution. If it's a new fire door leaf refer to the data sheet for details and if its an existing fire door fitting a threshold plate to the floor may be the easiest way to resolve the problem.
  5. In the case of timber-based fire doors, the certificate of approval and data sheet (or equivalent documentary evidence of fire resistance performance) for that particular fire door leaf will set out the requirements for the door frame. Usually softwood with minimum sectional dimensions of 70mm wide x 30mm thick plus the thickness of the rebate stop. Eg:
  6. Escape provision would be dependent on Building Regulations where they apply. Where they don't apply, the Fire Risk Assessment should deal with the issue. In terms of cutting the top of a fire door at an angle, this is very likely to affect its fire resistance performance. Always check with the door manufacturer before cutting!
  7. Try these guys. https://www.thebuildinginspector.org/
  8. You are correct there are issues surrounding lipping min & max thicknesses, type of adhesive and density of timber. A good maintenance training course will deal with these issues. Also, if the door is in scope of a 'third party product certification scheme' such work may cause the certification to be void. Mind, it already is when the gaps are too large! Best practice would be to remove the door leaf and door frame, adjust the door frame to suit the door leaf and re-install the door assembly compliant in all dimensional requirements including all gaps and alignment.
  9. https://app.livestorm.co/abloy/electrical-locking-fire-and-escape-doors?type=detailed&utm_campaign=974623_ELS 07%2F07%2F2022 Webinar e-shot&utm_medium=email&utm_source=ABLOY&dm_i=545M,KW0V,1FZFPN,2GR0Y,1
  10. The doors should be latched and the slave leaf bolted. The installation instructions for the door leaves will provide the information about whether the doors are suitable for a double leaf configuration and about the latch you need.
  11. The utility room becomes part of the house therefore fire and smoke compartmentation including a self-closing fire door with restricted smoke spread would be required between the utility room and the garage.
  12. The relevant British Standard, BS 8214, states "A typical gap to achieve good fire performance is between 2mm and 4mm". Excessive door leaf to door frame gaps could cause failure of the door to meet the required fire resistance performance.
  13. https://buildingcontrolalliance.org/wp-content/uploads/2017/04/BCA-GN-9-Fire-Doors-in-Dwellins-1-Jan13.pdf https://www.jbkind.com/uploads/pdfs/JBK_Fact_Sheet_FD20_and_FD30.pdf
  14. Engage or consult a competent fire door inspector https://afdi.org.uk/category/find-a-fire-door-inspector/
  15. The max gap depends on the sealing method employed. Contact the product distributor to find out the max gap/min depth and suitable substrates for the Blue60 system https://blue-60.co.uk/
  16. Is this a flat entrance door? If so does the flat entrance door open onto a communal area inside the building? Does the door belong to you or does it belong to your landlord?
  17. I don't believe there is one, contact the Door & Hardware Federation for advice https://www.dhfonline.org.uk/
  18. refer to the topic here:
  19. Different countries and geographical zones have different Standards. Which country will you be working in?
  20. There is no straight answer! As far as I know fire doors with plugged holes have not been subject to a fire resistance test but there are some issues to consider: 1) If you plug a hole in a certificated fire door the certification for the door will be void because such work is outside the scope of the certification. 2) If you plug a hole in a fire door you should do so in the knowledge that the work you do must not adversely affect the fire performance of the door. 3) Some fire doors are made from timber so if one has a hole in it and you need to plug it, timber is a good material to use.
  21. Doors with these self-closing devices will be subject to increased stress levels at the hinges. Therefore, whilst not an absolute requirement, installing more durable hinges would be good practice.
  22. In terms of the threshold gap for fire doors and compliance to BS 8214: 2016, there is no distinction between doors with top & bottom pivots and doors with butt hinges.
  23. This would depend chiefly on whether smoke seals would provide a benefit to life safety at this location. So its a fire risk assessment question.
  24. Hi Phoebe, For fire resistance purposes the max gap is generally 10mm, so you could fit a threshold plate to the floor to reduce the gap and then fit a flexible seal to address the cold-smoke spread issue. BS 8214: 2016 sections 9.5.3 and 12.3 refer.
  25. The applicable Standard is BS 8214: 2016 which recommends a maximum of 4mm and minimum of 2mm.
×
×