  1. I am assuming the original staircase serves the first and second floor; therefore I think you would be considered dealing with a building of three storeys, according to the guide and would need to opt for the Grade A and Grade D systems. Otherwise you would have to argue that it should be considered a two storey building because it is a flat and a maisonette I am not sure you could get away with it.

    Check out HOUSING – FIRE SAFETY Guidance on fire safety provisions for certain types of existing housing.

     

  2. According to ADB all doors in a domestic property should be FD20 fire doors, but very few manufacturers test to the FD20 standard, they use FD30 fire doors instead and it is consider substantial  well fitting existing doors meet the FD20 standard. Because you are fitting new doors they should be FD20/30 doors

  3. This is a question for a BCO/AI but to my understanding you have to have at least one metre of level going before you step down and in your case you will, if the door opened outwards you would require a metre landing to achieve the metre level going.

  4. You need to speak to the Responsible Person ( Freeholder or the person who is responsible for the FRA) and find out his/her views. Most deliver services usually have facilities to say what should they do if you cannot receive the parcel, consider leaving it with a neighbour. 

×
×