  1. To calculate the maximum occupancy you need more that just the width of doors you need to take in the location, travel distances and the layout of the area in question. Consequently you need to have a competent fire risk assessor to do a survey or detail plan of the area in question showing the full layout.

  2. You need a more detail description of the the fire alarm system. From what you have said you have a  three storey building converted into self-contained flats and this requires Grade A: LD2 coverage in the common areas and a heat alarm in each flat in the room/lobby opening onto the escape route (interlinked); and a Grade D LD3 coverage in each flat (non-interlinked smoke alarm in the room/lobby opening onto the escape route) to protect the sleeping occupants of the flat.

    If a fire breaks out in the flat the grade D alarm will warn the occupants to evacuate the flat if the flat is empty then the heat detector will actuate the heat alarm near the front door and set off the grade A alarm warning the whole building. If the fire is in the common areas then the grade A alarm will warn the building.

    This means you do not need smoke filtering from a flat front door to actuate the grade A alarm therefore the flat front door needs to be a FD30s fire door. A FD30s fire doors needs intumescent seal and a cold smoke seal which will prevent the common areas filling with smoke during the cold smoke stages of the fire.

    You said I just need to know if the fire doors to each floor need smoke seals or not, well the do need smoke seals as well as the intumescent seals.

  3. If there is a cross corridor FD30s door across the corridor at the point the dead end starts then I would consider it meets the guidance.  Anywhere the corridor  has an alternate MoF escape and is within the travel distances then fire doors would not be required. 

  4. If they were fire doors, then slamming shut would eventually damage the door, which would render them useless and outside pressure could be applied getting them sorted out however as these will most likely not be fire doors, being entrance doors then I am afraid  it is up o the landlord to sort out, keep at them.

  5. On 13/08/2021 at 09:03, tim1619 said:

    Hi all,

    I have recently completed my Fire Certificate and have been asked to conduct a fire RA at my local rugby club.

    Your first statement concerns me we haven't had fire certificates for more than 20 years the only recorded information is the FRA and not always. Open Fire safety risk assessment: 5 step checklist  after you have completed item 3 conduct a means of escape plan which should identify all passive and active fire prevention which will identify any fire doors you require including all necessary fire protection required. Next item 4, record your FRA also determine the degree of hazard so the RP knows the order they need rectifying of each item.

    Check out these quides https://www.firesafe.org.uk/fire-risk-assessment/     Small and medium places of assembly they may help.

×
×