Can I have a fire corridor inside my building?


Guest Tom

Recommended Posts

Hi,

 

Just wondered if anyone can help. I am having some difficulty with negotiating rights over a secondary means of escape of my bar/restaurant so am looking into alternatives. Have had a fire safety officer down to take a look who was helpful but that was a little while back and the situation has changed since then.

 

I'm struggling to find any definitive information as to whether putting in a 'fire corridor' would allow me to utilise the space at the back of my unit, therefore keeping the escape route down to 18 metres travel distance (the beginning of the corridor)? Or is the distance to a protected fire corridor irrelevant as it is still within the building and there is some distance to travel inside the corridor? I have had conflicting information from different sources.

 

I know they have to be 45 degrees apart but am I right in thinking this being protected might solve this problem if it is protected with the right materials? Any help on the matter would be great. Please see pic below, any questions please ask! The unit is 33 metres long so need two means of escape so that my capacity is large enough to make it viable.

Burton Road Rough Layout (1).jpg

Link to comment
Share on other sites

The fire corridor would have to be less than 12m to avoid the need for an additional FD at the midpoint.

You would be constrained by the width of the new corridor as to the occupancy capacity (discounting exits BR 2019 2.21 – 2.23)

Can you not utilise the exit by the men’s toilet?

It could be argued that the design is purely to try and circumvent the building regs.

Link to comment
Share on other sites

  • 2 weeks later...
On 28/09/2021 at 13:29, Mike North said:

The fire corridor would have to be less than 12m to avoid the need for an additional FD at the midpoint.

You would be constrained by the width of the new corridor as to the occupancy capacity (discounting exits BR 2019 2.21 – 2.23)

Can you not utilise the exit by the men’s toilet?

It could be argued that the design is purely to try and circumvent the building regs.

Why would you need to divide the corridor? Division only required where alternative escape routes could be compromised. Note swing of doors should be in direction of travel, unless less than 60 occupancy. Even then, effort should be made to avoid such a situation. You might get a better outcome through BS9999 which if properly employed can allow some valuable trade-offs. Your travel distance is from the furthest point, even should it be a store or loo.

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...