November 15, 20187 yr comment_12976 We are required to fill the gap between the inner and outer door frame , the inner door frame being part of the fire-rated door system , the outer being a timber frame around the opening in the concrete or brickwork which are installed by the builder. Shop drawings show maximum gap allowed as 10mm and intumescent foam literature says to apply between 10mm to 20mm . No problem with that . the problem is that sometimes we have gaps of 3 to 5mm and we cant get the intumescent foam into such a tight gap . Are we still required to fill these narrow gaps even though they are behind the architrave ? Some are saying if the gap is narrow and is filled by timber frame then this is ok and no need to fill. Report
November 15, 20187 yr comment_12978 Most cheaper off the shelf FR foams are not tested for use in frames regardless of the claims on product literature, loads of places have had to rip this out and start again or if lucky been able to trim it down and suitable mastic or plaster over it. Search for Blue 60 a foam specifically intended to serve your purpose Report
November 16, 20187 yr comment_12980 Hi Michael, Because gap sizes can vary so much you may have to use more than one fire stopping method. First of all, I should say that this subject is dealt with in detail by 'BS 8214:2016 Timber based fire door assemblies Code of practice'. Generally, for gaps up to 15mm you should completely fill the gap to the full depth of the door frame with tightly packed mineral wool. Make allowance though for a 10mm deep capping of intumescent acryilic sealant on both sides. The sealant should cap the mineral wool for a 10mm depth between the frame and the wall and not just to cover the surface of the gap. Intumescents are gap fillers and need surfaces to expand against under pressure, if applied to just a flat open surface they will just foam and fall away so they need to be inside the gap. This should be done all around the door frame to wall gap on both sides. Where the gap is up to 20mm, follow the same method as above but use tightly fitted 15mm timber or MDF architraves to overlap both frame and wall by at least 15mm. For small gaps such as 3mm to 6mm where use of mineral wool is impractical you should fill the gap as deep as is practically possible with intumescent acrylic sealant. For especially large gaps line the opening with continuous solid timber and fill any remaining gaps as above. Blue 60 is a new-ish product specially for timber fire door frames but minimum and maximum gaps apply to its use and the dedicated packers supplied with the foam must be used. So use in accordance with the product data sheet. Hope this helps. Report
December 4, 20196 yr comment_15909 Hi. If fitting a new fame into a brickwork opening and there is a gap of say 30mm either side. Would it be ok to use fire rated foam or can I use fire rated plaster. Any answers greatly received Report
December 4, 20196 yr comment_15913 LABC usually require fire grade Rockwool stuffing suitably sealed in, there is also an intumescent foam designed for frames called Blue 60, which if used within manufacturers instructions and parameters will also suit. Pink aerosol fire foam is a waste of time as it doesn't work for 99% of the things people ignorantly use it for - it's actually only tested and OK for a very finite number of situations, usually very narrow and deep linear gaps between a concrete wall & floor slab and not much else (regardless of the complete fantasy on most cans and supplier websites) Report
December 5, 20196 yr comment_15915 The requirements for sealing the gap between the fire door frame and surrounding wall are set out in 'BS 8214:2016 Timber-based fire door assemblies: Code of practice' https://shop.bsigroup.com/ProductDetail/?pid=000000000030332501 Report
July 3, 20206 yr comment_17438 Does the gap between the frame and substrate require sealant if there is an architrave already installed. this is when the internal door has already been installed. Report
July 6, 20206 yr comment_17446 Yes. The architrave should not be relied upon to provide fire resistance. Report
April 8, 20215 yr comment_19767 Hello, I have a question regarding the fire door frame fitting? The instructions state that mineral wool be used to pack out the door frame gap up to 20mm. My gap varies between 10 and 15mm. Can timber packers be used to secure the frame and then mineral wool be pushed in around the packing? I can't imagine getting a secure enough fixing using the mineral wool alone. If so should the wood packers be full frame width? Or cut down to mut the wool and sealant around them. Help very much appreciated as the suppliers technical help is lacking! Report
April 10, 20215 yr comment_19790 Yes, timber packers should be used at all fixing points so that you can get a secure fixing. They can be full width of the door frame. Ensure the mineral wool is tightly packed to fill all gaps and leave no voids then cap the wool on both sides with a 10mm depth of intumescent mastic. Report
April 23, 20215 yr comment_19916 Can I use batt behind a door frame where the gap is 15mm to 20mm then intumescent mastic? Report
April 27, 20215 yr comment_19938 Refer to BS 8214:2016 Timber-based fire door assemblies - Code of practice for details about how to seal the gap. Report
May 11, 20215 yr comment_20065 Hi there. I have a large number of F60 doors which need fitting to the clients specification. That is every door needs an acoustic/ fire sealant between the frame and the opening. The packers also need to be F60 spec. Unfortunately the only product on the market we have found is the Blue 60 packers which have only been tested with the Blue 60 foam. I can used hardwood wedges with a fire rated sealent however what I can't do is use the thosands of pounds worth of blue 60 PACKERS we have on site as it hasn't been tested if we include the sealent into mix Do you have a suggestion for the way forward? Report
May 11, 20215 yr comment_20074 I can't because the architects have specifically asked for acoustic fire sealant between the frame and the openings. And since the combination has not been lab tested if would fail to get certified. Report
May 12, 20215 yr comment_20080 So the issue appears to be certification of the work. Normal practice would be to completely and tightly pack the gap with mineral fibre and then seal to a 10mm min depth to both sides with the Fire Acoustic Sealant. Refer to BS 8214:2016 for minimum requirements. If the architect will not allow the use of Blue 60 and the dedicated packers in place of the sealant/fibre combination, then you have two options: 1) Ask the Blue 60 manufacturers what evidence of fire performance is available for use of Blue 60 in full accordance with the fire test evidence but with an additional depth of Fire Acoustic Sealant to both sides. Note, we are saying 'in full accordance' so that the sealant is an extra-over to the fire stopping requirements. Clearly door frame material type, depth of foam and gap size is a major factor here. 2) Use mineral fibre and fire acoustic sealant in accordance with BS 8214:2016. Report
January 6, 20224 yr comment_23183 what are your thoughts on using the mastic for the full depth of the joint in place of the BS 8214 recommended mineral wool with mastic capping arrangement? This is for gaps up to 20mm where the doors have suitable architraves. Report
January 7, 20224 yr comment_23208 Does the fire resistance performance test evidence for the mastic product support that use? Report
May 25, 20224 yr comment_26159 BS 8214 notes 9.4.1 General In order to maintain the fire resistance of a fire-resisting wall or partition when fitted with a door assembly, the sealing between timber-based door frames and the supporting construction should be in accordance with Table 2 to Table 5 as appropriate for the fire performance required. But is this the fire resistance for the door ie 30min or the fire resistance of the wall ie 60min i have the doors fire certificate which refers back to BS 8214 and none of the tables show fire resistance of the gap, just the door performance Report
June 8, 20224 yr comment_26649 Have you checked the manufacturers fire door test report if in doubt go for the highest level. Report
June 13, 20224 yr comment_26815 In terms of the requirements of BS 8214 the fire rating applies to the door. Report
June 27, 20224 yr comment_27316 Good morning all, I'm working on a building with alot of traffic throughout the day, The doors are fairly new and most if not all are retrofitted to old frames, the gaps between the frame and wall mainly on the head exceeds over 30mm I have been asked to fill theses gaps with blue60 and then intumescent sealant, I know that the maximum gap is 20mm, the client is the one that asked for this to be done, should I go ahead with job or should I say I'm not doing it and the doors with the gaps over 20mm needs to be replaced which is the right way to go Report
June 29, 20224 yr comment_27405 The max gap depends on the sealing method employed. Contact the product distributor to find out the max gap/min depth and suitable substrates for the Blue60 system https://blue-60.co.uk/ Report
August 16, 20224 yr comment_28635 Hi, what is the best way to infill gaps of 40/50mm around an existing door frame? Report