March 15, 20179 yr comment_9935 If it's vacant then you don't necessarily have to test it as long as you have a suitable risk appropriate alternative for those rare occasions of occupancy. All non essential power (sometimes including lighting) is often isolated to reduce fire risks (and the bill) so fittings will be discharged. Torches are acceptable as emergency lighting in certain circumstances. It's all down to the risk assessment - vacant premises FRA's are different beast to those for occupied premises and are often carried out as part of Health & Safety Liability Audits for fully vacant space Report
April 29, 20179 yr comment_10118 Further to this topic, is it necessary for emergency lighting in a house used as a holiday let? I have a 150 year old ex-miners cottage and it does not seem 'reasonable' (the governments oft used qualifier on much of the Fire Regulation requirements) or cost effective to install so much intrusive tech in a small stone cottage. If it is, would the plug in 'torch' type lighting suffice? Report
May 1, 20179 yr comment_10123 All holiday lets are covered by the The Regulatory Reform (Fire Safety) Order 2005 and you should study the following leaflet which should provide all the guidance you need, https://www.gov.uk/government/publications/do-you-have-paying-guests. If you require guidance on individual fire safety issues check out, http://www.firesafe.org.uk Report
May 15, 20179 yr comment_10172 Dear fountain of all fire safety knowledge, I'm looking in to the fire safety regulations for a school and the fire risk assessment (Jan 2016 - i'm aware we are well overdue) mentioned only about the testing of the Emergency Lighting. When I spoke to our certified electrician, he informs me that they can fix the emergency lighting system (some of it is testable, portions aren't - very old Grade 2 listed building) but all of the fire safety signage in that building will need to be illuminated. Is this the case or can some of it be photoluminescent? I've looked everywhere on the internet to try and find a definitive version - so I thought i'd ask the fountain of all knowledge. Many thanks Paul Report
May 15, 20179 yr comment_10173 The all emergency lighting has to be tested according to BS EN 50172:2004 or BS 5266-8:2004, those portion that are not then they need to be modified so they can. All the fire safety signage in that building will need to be illuminated, but that does not mean illuminated exit boxes, providing there is an EL luminaire near to the sign that is capable of illuminating the sign then that is acceptable. Illuminated exit boxes are only required where the normal lighting is dimmed to a very low level like theatres or cinemas (temporary or otherwise). Photoluminescent signs may be acceptable is certain areas dependent on the FRA. Check out http://www.firesafe.org.uk/emergency-lighting/ and http://www.safelincs.co.uk/emergency-lighting-guide/ Report
August 29, 20178 yr comment_10721 We currently occupy a rented office. Who is responsible for providing the emergency lighting for the building? Report
September 4, 20178 yr comment_10739 You are responsible for a fire risk assessment and determining if you require EL as you are both an employer and a person having control of all or part of a premises by way of your lease. Most rented office suites have their own meter and distribution board which you are responsible for - the lighting is under your control as a result including the EL need Report
September 8, 20178 yr comment_10758 Hi, questions reference borrowed lighting; 1) if the 'street lighting' is on the same phase as the 'premise lighting' and there is a power failure to the street lighting and/or area, then the premise has no emergency escape lighting. Is this acceptable when considering designing emergency lighting systems 2) there are different lux levels, required at the points of emphasis within a premise i.e. centre line of an escape route and say, a manual call point. How is the photometric data gathered and designed around borrowed lighting, when most certainly shadows will form in areas not covered by windows. Report
September 8, 20178 yr comment_10759 Your points are valid and why every revision of BS5266 reduces the acceptance of borrowed lighting more & more and if you have an escape route and open area that at any time of use would require you to switch the electrical lighting on there is a good chance you will need emergency lighting. Report
January 30, 20188 yr comment_11400 Hi all, Is it a legal requirement to provide emergency lighting outside a building e.g in the car park? Report
January 31, 20188 yr comment_11422 For many years a compliant installation would have had an EL fitting outside each final fire exit and to external stairs, but the 2017 update to the standards now includes cover to the external route to a place of ultimate safety. It's not automatically retrospective, but Fire Risk Assessments need to judge if the risk by not updating is tolerable or not- some places will need it, others not. Report
February 11, 20197 yr comment_13510 I work in an outdoor education centre. We have sleeping accommodation too. I always thought that our system was a 1 hour system, as the centre is not that large and evacuation is quite quick. We conduct a monthly check of all lights and are slowly replacing old lights/batteries etc. On our last annual inspection, they did a full 3 hour test; during which quite a few failed; as they would. My main questions and comments are: if a system is designed to stay illuminated for 3 hours then surely they have done there job and will fail at 3 hours. This test seems to not make sense to me? Who stipulates how long we need them to last? Are we able to work with the testing company to ask them to test for shorter? Appreciate any comments Report
February 13, 20197 yr comment_13536 A 3 hour fitting has to be tested to and meet it's full rated duration. If it's lasted less than that it fails, you replace it. Fittings aren't that expensive these days, e.g. https://www.safelincs.co.uk/eden-led-emergency-bulkhead-light/ The relevant standard BS5266-1 requires sleeping accommodation to have fittings with a three hour duration. Report
October 24, 20196 yr comment_15573 must an emergency light in the electrical cupboard (where meters are stored) need to be flick tested each month? residential block of flats thanks Report
November 24, 20196 yr comment_15840 Before discussing Emergency lights should we not discuss normal artificial light and lighting standards, most lights are poorly maintained and effectively only work properly for the first period of their installation. Maintaining lights surely should include , cleaning and changing covers or damaged parts , yet when . An emergency light is only there to provide COVER when the other lighting fails, so it is only part of an emergency system , at other times general light should be MAINTAINED at a level as to not add risk and this should include the fact these are electrical items that need respect and that emergency lights have a secondary supply and therefor a greater risk of creating a problem , Report
November 26, 20196 yr comment_15858 The normal lighting is used daily and any defects or low standards will be known quickly and under the Health and Safety at Work Act they will be required to correct the situation. The emergency lighting will only operate if the normal lighting fails, so there is no way of knowing if it is defective until it is tested or maintenance and is subject to The Regulatory Reform (Fire Safety) Order 2005. This forum is a fire safety forum not a health and safety forum so we tend to concentrate on emergency lighting. Report
February 25, 20206 yr comment_16516 Do I need emergency lighting in temporary offices Construction site if they are only occupied by the day? Report
February 25, 20206 yr comment_16522 Possibly. Easiest way to tell is to switch all the lights off and see how easy it is to see your way out, you usually need the equivalent light of a full moon on a clear night to safely see your way out (this is where the original EL lighting levels came from!). Consider the available light at the start and end of the day (when it's darkest), time of year and the impact of overcast weather. Having done this you may conclude you are fine. If not then depending on the size of the offices and number of people you may need either emergency lighting - or torches! Report
July 25, 20205 yr comment_17603 Regarding the 18th Regs., when rewiring a public building with a multitude of external windows, is it mandatory to install emergency lighting, which of course will require illuminated Exit signs or is overhead led fittings with integrated emergency lighting satisfactory? Report
July 28, 20205 yr comment_17623 You need to check the fire risk assessment that will tell you if emergency lighting is required. Assuming the building is not a place of public entertainment which usually requires maintained illuminated exit signs they are not required in non maintained systems providing any fixed exit signs are well illuminated by the emergency lighting. Report
December 18, 20205 yr comment_18810 We have a small 2m x 2m tin shed housing a compressor. The shed is not manned except for the odd checks. It has a light and socket. Would this normally require an emergency light. It would have to be a very dark night for you to not be able to walk out/ exit a 2m2 shed Report
December 18, 20205 yr comment_18823 You've established you may not need EL for escape purposes - the other reason is for safety. Could someone be doing work on or around the equipment such that a sudden loss of light could result in accident/injury? If so you need EL to avoid injury and safely shut down the plant if required. Report
May 5, 20215 yr comment_20009 Hello, Please can you give some advice. I have just has a CQC telephone interview for the dental surgery i work in regarding emergency lighting. The surgery is 1 room with the dental chair and equipment in, with a small waiting area just outside. Its at the front of a residential property on the ground floor with a large window with 4 opening windows. Outside the house is a streetlight. The house is on a residential street. This is the only area patients would use for their visit. The layout is, from the main front door, an entrance porch, then the waiting area is immediately to the left, off of that is the surgery. there is a separate entrance to the rest off the house off the entrance porch. Can you possibly advise what kind of emergency lighting we would need? The practice only operates for a few hours in the afternoon on selected days, and there are always 2 clinical staff when patients are being treated. There is a fire extinguisher in the surgery and the decontamination are is in a different part of the downstairs Many thanks for any help you can offer. Kaye Everett Report
May 6, 20215 yr comment_20016 Risk assessment guidance suggests in the smallest premises (which being a couple of ground floor rooms this would fall into) that sometimes torches are sufficient. Power failure is not exclusive to fire and you have to consider also the impact of a sudden loss of power on any procedures in progress. Even if it is determined that 'proper' emergency lighting is required you may find that a simple LED bulkhead (e.g. https://www.safelincs.co.uk/eden-led-emergency-bulkhead-light/) in each room and the entrance foyer (3 of in total based on your layout) may suffice, wired off the normal lighting circuit if installed as non maintained (lit only on power loss or, if it has to be on it's own circuit (usually due to a lack of a readily available permanent live in the ceiling cables to each light from the switch) installed as maintained (always lit) Report