You may be right? If you post a picture of the seal somebody may be able to identify it? You say the fire doors are less than two years old, so you should be able to check this with the installer, supplier and manufacturer??
-
If the gap is more than the widely accepted '4mm rule' then there is greater risk that the door will fail to meet its intended fire resistance performance. Make sure your fire risk assessment deals effectively with this non-compliance issue.
-
Re edging nominal fire doors
Neil ashdown replied to Barney057's topic in Fire Doors and Accessories
It is permissible to fit hardwood lippings to timber-fire resisting doors. Make sure the lipping is the correct type of hardwood, to the correct minimum and maximum dimensions and use the correct adhesive to suit the type of door core. Obviously, don't add a new lipping on to an existing lipping! -
These plain seals can go in the door or frame, they are intumescent fire seals. These combined intumescent fire and smoke seals can go the door or frame. Batwing type smoke seals can be fitted in the corner of the rebate, against the stop. They are not intumescent so use them with the intumescent fire only seals. Smoke seals are also available to fit to the stop on the push side of the door, these are not intumescent so use them with the intumescent fire only seals.
-
Making good a fire door after cutting into it
Neil ashdown replied to a topic in Fire Doors and Accessories
Use a small hand held bottle router with a trimmer bit. Failing that sand off the surplus. Make sure you use the correct adhesive for lipping the door leaf. -
It depends whether the door must also provide restricted smoke spread as well as fire resistance. Where there is a restricted smoke spread requirement the maximum gap is 3mm (refer to BS 8214:2016). For timber based fire doors and where there the is no such smoke requirement the maximum gap is generally between 6mm and 10mm, depending on the evidence of performance for the particular fire door. So it is very unlikely that a gap of more than 10mm will be compliant for any timber-based fire door. Where the 3mm gap requirement for restricted smoke spread cannot be met due to floor conditions, a threshold smoke seal / threshold plate will be required to close the gap accordingly.
-
Fire Door for Entrance to Private Flat
Neil ashdown replied to Flat Owner's topic in Fire Doors and Accessories
Composite fire doors are currently available for sale. With regard to the Government tests there's more information at https://www.gov.uk/government/publications/fire-door-testing-grp-composite-test-results -
space between fire door frame and opening
Neil ashdown replied to a topic in Fire Doors and Accessories
Yes. The architrave should not be relied upon to provide fire resistance. -
Making good a fire door after cutting into it
Neil ashdown replied to a topic in Fire Doors and Accessories
The contractor doing the remedial work to the fire doors does not have to possess any particular certification or qualifications BUT they must be COMPETENT. Refer to Article 17 and article 18 of the fire safety order. http://www.legislation.gov.uk/uksi/2005/1541/article/17/made http://www.legislation.gov.uk/uksi/2005/1541/article/18/made -
Fire Door Self-Closers - Angle of Release
Neil ashdown replied to Pacman's topic in Fire Doors and Accessories
? -
Fire Door Self-Closers - Angle of Release
Neil ashdown replied to Pacman's topic in Fire Doors and Accessories
Yes! When inspecting the self-closing function of a fire door, the inspector should check that the door self-closes from any opening angle.......fully-open to only-just-open. Suitable self-closing devices will have adjustment for latching action as well as closing speed. Any binding of the door on the floor covering, door frame, seals or latch strike plate etc. should be resolved before adjusting the controls of the self-closing device. For the self-closing device to function correctly it is necessary to install the closer-body at the correct position in relation to the door leaf for the required power-size (minimum size 3 for a fire resisting door) and install the closing-arm assembly in the correct location and arm configuration. This might be useful from 'Code of Pactice: Hardware for Fire & escape Doors' at http://www.firecode.org.uk/Code_of_Practice_hardware_for_fire_and_escape_doors.pdf -
Making good a fire door after cutting into it
Neil ashdown replied to a topic in Fire Doors and Accessories
Hi Adam, A drop seal will not be a substitute for a hardwood door lipping, in most cases. If you are installing a new fire door the installation instructions will state the maximum gap allowed at the threshold. This is usually somewhere between 6mm and 10mm from the bottom edge (the timber edge not the seal) of the door to the floor surface or threshold plate. It is necessary to comply to maintain the door's fire rating. Most fire doors are also required to provide smoke protection (at ambient temperature), in which case the maximum threshold gap is 3mm. If 3mm cannot be achieved due to floor conditions, then a static threshold seal or drop-seal will be required to close the gap, but the gap between the door bottom edge and the floor surface must still not exceed the door manufacturers requirements (eg. 6mm to 10mm). If the door is not new and the specific gap requirement unknown, work on a maximum gap of 10mm for a timber-based fire door and 3mm where smoke protection is required. If the gap is more than 10mm use a floor mounted threshold plate or suitably lip the door bottom edge with hardwood to reduce the gap accordingly. Then add a suitable threshold seal to provide smoke protection where necessary. See image below............... -
Flat fire door for private entrance
Neil ashdown replied to Nibarb's topic in Fire Doors and Accessories
Hi Andrey, Is this similar to the layout for your flat? But with just two bedrooms, one living room and one kitchen? -
Flat fire door for private entrance
Neil ashdown replied to Nibarb's topic in Fire Doors and Accessories
Reference to the document 'Fire Safety in Purpose Built Blocks of Flats' at https://www.local.gov.uk/fire-safety-purpose-built-flats will enable you to decide on the fire rating requirements for your internal doors. The requirement for the flat entrance door will be FD30(s) minimum and must be fitted with a suitable self-closing device. -
Fire Doors on Flat Conversion?
Neil ashdown replied to TopperUK's topic in Fire Doors and Accessories
In order for the doors to be installed as compliant, its better to replace the door frame for a number of reasons. A major one being that some timber-based fire doors have very limited scope for trimming the edges to fit existing frames. -
If the door is an entrance door to your flat and opens onto a common area inside the building, its most likely that the door you need will be rated FD30(s).
-
Does my front door need a lock without key?
Neil ashdown replied to a topic in Fire Doors and Accessories
Just to add that, there is a requirement that the lock-set is fire rated and installed in accordance with the fire door manufacturer's requirements. -
Use this search facility to find a fire door inspector https://fdis.co.uk/find-an-inspector-2/ Enter your post code to find local fire door inspectors.
-
Is it ok to rout a fire door to fit a seal
Neil ashdown replied to nwpattesting's topic in Fire Doors and Accessories
It is acceptable to router a groove in the top and vertical edges of the timber-based fire door leaf or leaves. The groove should be central to the leaf thickness except at the meeting edges of double door leaves where two offset seals may be a requirement. Do not fit a seal to a slave leaf that has flush bolts at its meeting edge, fit the seal to the main leaf instead. The groove must be only just large enough to accept the seals as a tight fit. Take care to make sure the groove is only just deep enough to suit the seal thickness as the seal must be flush with the door leaf edge. If you can find a BWF Certifire label (see below) on the door leaf you can refer to the CF certification data sheet for details about the type, configuration and size of seals required. If the groove will damage the BWF Certifire label, carefully remove it and reposition it alongside the groove. -
Are specific fire door gaps a legal requirement?
Neil ashdown replied to a topic in Fire Doors and Accessories
The standard for timber-based fire doors is BS 8214 and section 9.5.2 says: "Failure of fire resisting doors under test is very often due to burn-through at the operating gap between the door leaf edge and the door frame. A typical gap to achieve good fire performance is between 2mm and 4mm". So the question is: can you justify acceptance of gaps of slightly more than 4mm? 1) Are you happy to make a note in your Fire Risk Assessment that the fire doors have been inspected and that some of the gaps are non-compliant, but that you find this acceptable in certain circumstances? 2) Has the C.O.W. checked that the cold smoke seals are effective? An excessive gap will affect the smoke restriction performance of some types of cold smoke seal. 3) Could such non-compliancies have any impact on the safety of persons at the building in a fire? Post-Grenfell some flat entrance doors were tested by the Government and found to fail at 15 minutes rather than the required 30 minutes. This non-compliance was considered sufficient for the government to require that some fire door manufacturers cease production until further investigations were completed. -
Large single pocket fire door - DIY?
Neil ashdown replied to David Baker's topic in Fire Doors and Accessories
The requirements to comply with Building Regulations can be found at https://assets.publishing.service.gov.uk/government/uploads/system/uploads/attachment_data/file/832633/Approved_Document_B__fire_safety__volume_2_-_2019_edition.pdf Appendix C deals with fire doors and states that they must meet the required fire resistance requirement when tested to BS 476 - 22 or EN 1634 - 1. Therefore, as I understand the requirements, your bespoke design will need to be supported by documentary evidence. Fire door manufacturers will be able to provide you with maximum leaf dimensions and suitable configurations but I am not aware of a single leaf door that meets your specification. https://www.eclisse.co.uk/classic-double-fire-rated-pocket-door-system/ -
Fire doors in a domestic 3 storey house
Neil ashdown replied to a topic in Fire Doors and Accessories
Clearly, keyless egress is a useful life protection measure in an emergency scenario. If you need to open the door in an emergency and the key is not to hand that could increase the risk to life safety. However, my understanding is that in England & Wales, the Fire Safety Order 2005 does not apply inside your own private home. Check at http://www.legislation.gov.uk/uksi/2005/1541/contents/made and you could check Building Regs at https://www.gov.uk/government/publications/fire-safety-approved-document-b Or you could retain the keyless egress but use a security chain to help restrict the door being opened, when it shouldn't. -
I would advise you to consult a local building regulations expert on this matter. In the meantime, this may be useful? https://www2.gov.scot/resource/buildingstandards/2016Domestic/chunks/ch03.html But check for recent updates!
-
Fire Door - need a self-closer?
Neil ashdown replied to MysteryMan's topic in Fire Doors and Accessories
I would advise you to consult a local building regulations expert on this matter. In the meantime, this may be useful? https://www2.gov.scot/resource/buildingstandards/2016Domestic/chunks/ch03.html This may be useful? http://www.doorfingerprotector.co.uk/ -
Detail below illustrates accepted method for door frame / lining extension to suit wider walls. Generally, FD30 door frames may be softwood minimum density 450kg per cu mtr and for FD60 hardwood 640kg per cu mtr (at 15% moisture content). Generally door fame thickness minimum 32mm plus the rebate stop by 70mm minimum width. Hope this helps.