Smoke alarms and disco smoke machines


Guest DiscoKid

Recommended Posts

Guest DiscoKid

I am just setting up as a mobile disco and am concerened about using smoke machines and setting off smoke alarms. Is there any way I can use my smoke machine depending on what type of alarms are fitted or will the smoke trigger all alarms?

Many would just say, don't use the smoke machine but it gives a venue atmosphere and customers are not very happy if I have not been able to provide them with what they would class as an atmospheric disco event.

Link to comment
Share on other sites

Check out http://www.nodj.co.u...e-machine.shtml Safety and usage information which says,

The smoke can activate smoke detectors and this is something that you should check with the venue first. Many venues have more advanced smoke detectors that allow this type of smoke, but some don't and the venue staff will be able to tell you if it's OK to use a smoke machine.

Which is pretty good advice, it all depends on which type of smoke detectors are being used, the type of smoke, the amount of smoke, the size of the room, and the potential temperature of the room. As I have said it all depends, even steam from a shower can activate a detector head if the conditions are right.

Link to comment
Share on other sites

  • 2 weeks later...

The sensors in a smoke alarm will degrade over time. This along with years of exposure to dust and contaminants will cause detector performance to falter. Thus smoke alarms should be replaced periodically in accordance with manufacturers’ recommendations. Whether isolating a zone will up speed this process up is debatable and I would suggest you contact the manufacturer for their recommendations.

As to isolating a zone this is not a good practice, you could be removing the protection of a concealed area. I would suggest you consider changing the affected detector heads with a more suitable head that is not sensitive to the smoke machines. Your fire alarm engineer should be able to assist you with this.

Link to comment
Share on other sites

  • 1 month later...

In my opinion answer is no if a smoke detector has been installed as required by the fire risk assessment then replacing it with a heat detector will reduce the response time, to a fire alarm, putting lives in danger.

Have you considered bringing in a fire alarm specialist to look at the problem and maybe s/he could provide a solution.

Link to comment
Share on other sites

  • 2 weeks later...
Guest sparky

Hi I have just had a fire officer refuse heat detectors in a niteclub install even tho we have advised him of the issue of the smoke machine setting off the devices.

Any solutions other than throw out the smoke machine.

Thanks

Link to comment
Share on other sites

Hi, I would agree with the fire officer. Fixed temperature heat detectors activate at around 90 degrees c. Some fire panels have a "fire delay" option perhaps yours has. The idea of it is that the panel indicates fire but the sounders are delayed for a short time so you can investigate the cause.

Link to comment
Share on other sites

I am trying to find an answer but it may take some time assuming one exists. I have come across a detector called Advanced Multi-Criteria Fire Detector and you could check it out and see if it solves the problem.

Check out http://www.esmagazin...s-system-sensor and www.systemsensor.com/pdf/COPTIR-performance-report.pdf another make by Honeywell http://www.notifier....adv-sensing.htm

Link to comment
Share on other sites

The Fire Alarm System has to be an addressable type system and,

I think the best solution would be replacing the offending heads with advanced multi-criteria fire detector heads (4 sensors) if the control panel is compatible and you are prepared to accept the higher cost/availability. (Like System Sensor or Honeywell Notifier IntelliQuad)

Another solution would be to program all the offending detector heads and program them to reduce their sensitivity, or build-in a simple key switch to the system that automatically isolates the required affected detection heads. At the same time, provide various visual and/or audible warning that the system is in a 'partially disabled' state.

The problem with smoke machine fog is that it is hard to control it at a level that will definitely not affect your 'adjusted less-sensitive' detectors. You end up still getting some, if as not as many, unwanted alarms. It is far more practical to temporarily totally isolate automatic detection in the smoke machine affected areas during those times those areas have people present.

A further safety requirement would be to conduct a fire risk assessment for when the smoke machine is in use and also produce a Permit to Work system covering the use of smoke machines, part of the sign off procedure is to reinstate the fire alarm system.

Any fire, in the area that involves the fog from the machine, would soon be discovery by the persons present or the staff dedicated to fire watching in this area.

Link to comment
Share on other sites

  • 3 months later...

Have a look at the ASA detector from Cerberus PRO. I believe a company in Glasgow has fitted them in a very busy night club in Edinburgh and they have worked really well without false alarms. Importantly they have not been switched to a heat detector or have time delays or other tricks of the trade applied - they are genuinely smoke detectors but very clever!

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...