We are designing a three storey, timber frame house that needs FD30(s) fire doors but we are also fitting an MVHR system which needs a 10mm ventilation gap under the doors which conflict with Building Regulations.

We have looked around for doors and spoken to many companies and all have not come across this before. MVHR in 3 storey cannot be new?

One company suggested we use a sprinkler system.

Any ideas would be welcome!

Link to comment
Share on other sites

Where did you get, you require FD30s in a dwelling house my reading of Approved Document B (Fire Safety) Vol 1  Appendix C, table C 1, only the door between a dwelling house and an  integral garage requires a FD30s fire door with self closer. 

As FD 20 are not readily available so you could use FD 30 fire doors and this could allow you some options regarding the ventilation.

11.   In a dwelling house:                                                           Euro                   BS 476 p 22
 
 a. between a dwelling house and a garage.                        FD 30 S a(2)       FD 30 S(2) 
 b. forming part of the enclosures to a protected
     stairway in a single family dwelling house                       E 20                    FD 20 
 c. within any fire resisting construction in a 
    dwelling house not described elsewhere in this table.    E 20                   FD 20 
 

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...