May 10, 201313 yr comment_5520 can a fire escape door be fitted with a self closure arm? due to the fact it is left open and not shut often? Report
May 10, 201313 yr comment_5523 You need to clarify what you mean by fire escape door, is it the final escape door to the outside of you premises or is it a fire resistant door. (FD/FDs) If it is a final escape door then there is no reason why you cannot fit a self closer. If it is a FD/FDs door then it has to have an authorised self closer fitted check out http://www.firesafe.org.uk/fire-door-fitting-and-ironmongery/ for more information. Report
July 9, 201312 yr comment_5616 Is it possible to put a glass window into a fire exit door to allow light through? Report
July 10, 201312 yr comment_5618 As the window is to let light through I would imagine we are discussing a FINAL fire exit door leading to outside the premises and I am assuming the door is not fire resistant therefore the glass panel does not need to be fire resistant. There could be a situation were the glass panel needs to be fire resistant but there is no reason why you cannot provide a glass panel in that door. A point to consider is security and glass panels are easy to break though by an intruders. Report
August 16, 201411 yr comment_6549 Can final exit doors have self closing mechanisms fitted to keep the door closed. Some final exits are a normal exit route out of the building. If they can do they have to be fire rated Report
August 17, 201411 yr comment_6561 All final exit doors are an exit routes out of the building and do not need to be fire rated but there are exceptions, protecting an external fire escape for instance. You can fit a self closer providing the door is easily openable from the inside. Check out http://www.firesafe.org.uk/fire-door-fitting-and-ironmongery/ Report
April 10, 201511 yr comment_7355 Hi, My hotel was 'broken into' last week because one of my guests had left the fire door open (they often do). I would like to fit a door closer to the door so that it remains secure. Am I allowed to fit a door closer to a fire escape door? Thanks, Jon Report
April 10, 201511 yr comment_7356 A door closer is not normally required on final exit doors but in your case I can see why you need one and providing it does not interfere with with the use of the final exit, then I cannot see any reasons why you shouldn't fit one. Report
October 9, 201510 yr comment_8020 I am looking for advice about external fire doors of my tennis club which are currently fitted with push-bars for ease of escape. The doors a primarily an exit route rather than containment. Due to recent security problems we are looking at allowing fob access through these doors to access the toilets when otherwise the club would be shut. However, we are concerned that the doors could be left open carelessly. Is there any kind of device which could effect self-closing of such doors but which would not affect the ease with which people could escape from the building in an emergency? Report
October 10, 201510 yr comment_8034 The simple answer is to fit a standard self closer which is not going to prevent people escaping in the event of a fire, see attached image, but I do not know if it can be opened from outside, with self locking, unless you dispense with the second and third point of locking? You could also consider a magnetic lock with the door fitted with a self closer. Check out http://www.safelincs.co.uk/briton-571-touch-bar-panic-device/ Edited October 10, 201510 yr by Tom Sutton Report
April 13, 201610 yr comment_8769 Hello just rented a flat with a fire door off the kitchen on to a fire escape only to find that the glass is split in half and the bottom of the door is being held with masking tape what do you advise Report
April 14, 201610 yr comment_8776 Is this an external fire escape or an internal fire escape? If it is an internal fire escape then it most probably a FD30 door and would need to be repaired to a full half hour standard. If it is an external fire escape then it would depend at what level it leads onto the external fire escape, if it is the top level it may not need to be a FD30 door, if any of the other levels it most probably would and in any case it would need repairing for security if nothing else. Report
July 23, 20187 yr comment_12348 A fire arm closure has been removed from the top of an internal fire door at my sports club, and replaced with a sound triggered door guard is this breaching fire safety regulations ? When the door guard is triggered the door doesn't fully close. Report
July 23, 20187 yr comment_12349 Hi Linda To use a Dorgard (a fire door retainer), you still require a fire door closer. The Dorgard only holds the fire door open against the pressure from the door closer. When the Dorgard hears the fire alarm it releases the fire door and allows the door closer to shut the door. Harry Report
August 13, 20187 yr comment_12462 Can you have a fire exit door in a toilet? This is for a commercial property where space is limited. Thanks Report
August 14, 20187 yr comment_12472 You wouldn't normally design that in a building, but I have seen it done in existing buildings where historically it was the only and lowest risk way of adding a second exit. Report
June 17, 20196 yr comment_14432 We had four fire exit doors, two external and two internal. One of the internal fire exit doors has been taken off the alarm system and is considered a fire door. My query is, does it require a self closing mechanism, as I know fire doors have to be kept shut. At the moment this "fire door" doesnt shut by itself. Thanks Jake Report
June 18, 20196 yr comment_14439 If it is a door to the outside it doesn't automatically need one, if it's between two internal areas it is more likely to need one - generally of part of a protected route or a compartment wall Report
June 20, 20196 yr comment_14456 On 18/06/2019 at 22:52, AnthonyB said: If it is a door to the outside it doesn't automatically need one, if it's between two internal areas it is more likely to need one - generally of part of a protected route or a compartment wall Its an internal one yeah, it still has a push bar. Do you think it should be replaced with a proper fire door? Report
June 20, 20196 yr comment_14458 1 hour ago, AnthonyB said: Without seeing the layout of the building I can't be certain Here's the fire route Report
June 23, 20196 yr comment_14466 If those are compartment walls (as they could be) you would expect a self closer. Report
August 3, 20205 yr comment_17659 Hi we are in the process of purchasing a freehold flat with a UPVC kitchen door leading to the external fire escape. We are level 1 of 3 storeys. Is this legal? Many thanks Report
August 6, 20205 yr comment_17675 If the external fire escape serves all floors then it is likely that the kitchen door needs to be an FD30s fire door so you will need to find out if it meets a fire resisting standard. Report
October 23, 20205 yr comment_18301 Due to covid i need to get fresh air into a large room which has no windows.jave 4 final exit doors. Can i keep these open ? Or could i put adjustable vents in them to provide a fresh airflow Report