Guest Jonathan
Posted

Have just moved into a rented property that has an internal front fire door with intumescent strips. 
 

I am discussing with the landlord with a view to increasing top of door frame to allow standard single bed to fit due to the very sharp angle to get up flight of stairs. Door height at lowest point is 1950mm whereas the bed stands upright at 1990mm.
 

The perhaps most contentious point is whether the fire door needs to be replaced entirely with new hinges to take up the new height or if a joiner can cut/add fire door to it and re-insert intumescent strips around new piece. 
 

Also I believe the existing door is not certified any more when first installed because it appears that a locksmith has drilled and not fully filled a hole above the lock, thus compromising fire door rating? 

Guest Notable fire door
Posted
7 hours ago, Neil ashdown said:

Unable to comment without seeing this door. Probably, you need a replacement fire door assembly / set.  Or another way of getting the bed into the flat. 

No other way of getting our expensive bed into the property. Had even tried to take it through the front door of neighbouring flat but the sharp angle doesn’t allow us to turn the bed to go up short flight of stairs. I have uploaded some photos if it helps? 

IMG_7119.jpeg

IMG_7118.jpeg

IMG_7117.jpeg

IMG_7116.jpeg

Guest Exploring all options
Posted
2 hours ago, Mike North said:

Perhaps the most cost-effective solution might be to consider purchasing a new bed that can easily fit through the door.

This is a 2-bed property on 3-floors so a standard single bed should fit. The bed is relatively new and expensive hence looking at all options. Even the landlord is exploring options because the door will deter some tenants that seek a large property. 
 

I have had one joiner saying he could add to the door, move frame etc at a cost much less than the bed! I need to be certain what can be done. 

Posted

If the door needs to a fire resisting and cold smoke restricting, self-closing door then the joiner ought to make sure their work ensures that the finished door complies with 'BS 8214: 2016 Timber-based Fire Door Assemblies - Code of Practice'.

Posted

The door is not compliant with the current regulations, a Perko closer cannot be used on a fire door, it is incapable of overcoming the door latch.  The doorbell cable does not appear to be fire stopped.  It is doubtful that the handles are fitted correctly.  The door does not look like a fire door, is it solid construction?

Guest Door not compliant
Posted
4 hours ago, Mike North said:

The door is not compliant with the current regulations, a Perko closer cannot be used on a fire door, it is incapable of overcoming the door latch.  The doorbell cable does not appear to be fire stopped.  It is doubtful that the handles are fitted correctly.  The door does not look like a fire door, is it solid construction?

As a decorator / PM I’ve come across a few fire doors in my time. It’s a solid heavy door with intumescent strips all around. But I have seen far better fire door sets! 

Whether the door assembly / set is certifiable I am doubtful and this is a point I put to the Landlord because I am keeping in mind to share the cost but if the door is not compliant & should be, then there will be no contribution from me. I’m also informed by the agency’s joiner that the hinges are not fire-rated and the top hinge is not in the correct place. 

Posted

Take the door and frame out, skip them, move the bed in, fit a new certified FD30S doorset (frame, door & ironmongery all compatible and installed to manufacturers specification & test certificate), job done.

Whilst not to current building regulations if a new build or new conversion, as an existing door set official guidance for the fire regulations (separate legislation) will tolerate 'notional doors' and 'upgraded notional doors' in certain circumstances and whilst the Perko single chains are known to have been a  poor choice for decades aren't specifically excluded if still shutting a door flush (only rising butt hinges are) so the door may have been acceptable for existing purposes - but it doesn't look in the best of conditions and if having to complete building work to get the bed in it's time to modernise!
 

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...