Jump to content

HMO Lacors Guidance


bob2813

Recommended Posts

I have always followed Lacors (2013 I believe this is the last revision/amend).

I have an HMO, with non maintained Emergency Lighting, mains supplied, with back up battery.

It states: monthly periodic flick tests performed and Logged by the manager or fire contact, with annual periodic tests certified by a competent person.

The competent person has contacted me to say he has an update to guidance that states: every six months a 1 hour test to be performed by manager/fire contact (in addition to above tests).

I will ask him how he has been informed of this update, and should it superseed the Lacors Guidance.

Thanks.

 

Link to comment
Share on other sites

Question is - before I challenge his competence, is he correct, I cannot find any reference online to such an update.

I am not sure if HMOs are his main line of business, and in the past have had sightly conflicting information from him on very minor issues, which has had to be fact checked.
As as an aside, should my engineer be expected to folllow the 'letter of the law', he's competent, but not a Barrister in the Law.

Link to comment
Share on other sites

Thank you for that extract.

My Lacors Guidance (which I believe is current),  s32.8 references BS 5266-8: 2004 (BS EN 50172: 2004) Emergency Escape Lighting Systems, however I understand that is the guidance I should follow, unless an amendment is made and published for the Lacors Guidance to cover updated documents.

So I see no 6 month 1 hour test mentioned.

I am currently following the Lacors/BS5266 maintenance guidance, so can't see and of my procedures are missing anything.

I will have to go back and ask my competent person where he is getting his information from.

What he is suggesting makes sense - the extra test can't be a bad thing, but unless its guidance I should legally follow, then it shouldn't apply, and neither should I follow it, do I interpret the situation correctly.

Link to comment
Share on other sites

On 03/08/2023 at 18:22, bob2813 said:

I have always followed Lacors (2013 I believe this is the last revision/amend).

I have an HMO, with non maintained Emergency Lighting, mains supplied, with back up battery.

It states: monthly periodic flick tests performed and Logged by the manager or fire contact, with annual periodic tests certified by a competent person.

The competent person has contacted me to say he has an update to guidance that states: every six months a 1 hour test to be performed by manager/fire contact (in addition to above tests).

I will ask him how he has been informed of this update, and should it superseed the Lacors Guidance.

Thanks.

 

Utter rubbish to get more work - the 6 monthly 1 hour test requirement was removed in 2004!

Link to comment
Share on other sites

18 hours ago, AnthonyB said:

Utter rubbish to get more work - the 6 monthly 1 hour test requirement was removed in 2004!

Was it ? umm, thats helpful to know, my Competent Person is saying I could do the test, so their is no financial incentive for him, and we have worked together for years and I trust him not to rip me off, although I am aware - wool and eyes - can happen.

This thread states that BS5266: 1999 had it, but it was removed in 2005, not 2016, bit not that is matters, important point is that is was removed.
It reads "Six monthly test of self contained and central battery systems by simulation of a failure of the normal lighting supply, for a continuous period of one hour. During the test check all luminaries for proper function."
https://forum.iosh.co.uk/posts/t85842-Emergency-Lighting---6-Monthly-Test

Why was it removed ????


 

Link to comment
Share on other sites

Because it dated back to old battery technology (such as when wet lead acid central battery systems were common) and gives no benefit. Current battery types are actually damaged by part duration testing and it was found that by hour testing cells soon developed a memory effect and would prematurely fail 3 hour tests - a nice earner for test and install company's but a unnecessary large cost to end users

Link to comment
Share on other sites

  • 4 weeks later...

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...