March 8, 201214 yr comment_1809 What are the requirements for door stops (part of the frame-usually nailed to the lining of the door) in FD30 doors? Assuming adequate intumescent seals are fitted into doors/linings does the door stop need to be of a certain thickness? I seem to get different information from my suppliers and a web research hasn’t made me any wiser Report
March 8, 201214 yr comment_1811 Fire doors were tested early seventies to BS 476 Part 8 and the frame door stops was 1 inch (25mm) with no intumescent seal. This could be achieved by fixing an addition 1/2 inch (12mm) glued and screwed to the existing door stop. In the late seventies intumescent seals were introduced and it was found that 25mm fire doors stops were were not necessary. In 1987 a new standard was introduced BS 475 Part 22 which tested not only the fire door but the frame as well (fire door sets) the frames had 12mm door stops and intumescent seals which passed the new test. Now we have certified fire door sets part 22 and older part 8 fire doors therefore if you are fitting a new fire door, it should be a part 22 certified fire door set. However part 8 fire doors can be acceptable and occasionally none fire doors can be upgraded depending on a fire risk assessment. Report
October 17, 20214 yr comment_22006 lots of different information on door stops but do the stops need to be hardwood or softwood glued then pinned or screwed just need to clarify 12 mm or over x 25 or wider Thanks ? Report
October 20, 20214 yr comment_22038 If you are fitting a new fire door then the door leaf manufacturers installation instructions or fire performance certification will state door frame and rebate stop requirements. If you are working on old fire doors and without the possibility of checking with the manufacturer work on 12mm minimum thickness so long as intumescent strips are fitted. If intumescent strips are not fitted, my advice is to fit them. FD20/FD30 = softwood or hardwood FD60 = hardwood only You can use pins or screws, but stops must be securely fixed. Report
October 31, 20232 yr comment_39309 In our housing association, due to the age of the buildings, there are instances where doors are not provided with intumescent strips and cold smoke seals, however, 25mm door stops are provided, which meet a recognised and accepted previous standard. Since the 25mm door stops are already present, can we wait to install intumescent strips and cold smoke seals until refurbishment of the doors? Report
November 1, 20232 yr comment_39332 It is understood that fire doors offer improved performance when fitted with intumescent edges seals and obviously smoke seals, so this would be a matter for your fire risk assessment. Report
November 2, 20232 yr comment_39360 The attached may be of interest Determination_on_the_suitability_and_sufficiency_of_a_fire_risk_assessment_in_a_hotel....pdf Report
May 14, 20242 yr comment_42797 Came here looking for advice Grateful for the info above Neil and Tom It is a small cost to fit the smoke seals, have just been picked up on it and having them all fitted, with upgraded hinges where necessary and thumb turn locks. Envirograph will supply a three coat intumescent paint system together with certificate (£18 per door). Total cost £85 per door inc cert, useful if doors cannot be easily upgraded (listed building) Report
February 13, 20251 yr comment_47314 Should an external firedoor frame have rebated or loose stops Report
February 19, 20251 yr comment_47485 In terms of security, a solid door frame section rebated to suit the door leaf would be better than planted. Report