  1. Without a risk assessment and rationale it's not advisable. That isn't to say it's impossible - several premises are designed for delayed evacuation of certain areas, e.g. larger shopping centres have their security control rooms made of materials with enhanced fire resistance and several similarly enhanced escape routes to allow continued occupation during an alarm so as to monitor and manage any incident and evacuation.

  2. Without seeing the premises and finding out a lot more specific information I can't give you specifics, however there are many potential options, too many people fixate on Evacuation Chairs which are not always the most appropriate answer.

    You would also have to budget for staff training and maintenance, you can't just buy them and stick them on the wall, it's quite a big job to correctly implement the use of mobility aids.

  3. No, they are making it up as they go along and I would suggest you put this information to your local Fire & Rescue Service's Protection/Technical Fire Safety department (they all have different names for what used to be the Fire Prevention Department these days!) who would be very interested and no doubt follow this up for you.

  4. As a one off they would be right as they use paraffin which has a relatively high flash point and isn't readily ignited as a pool, but if it is a regular thing there will be a potential build up over time of paraffin soaked into the wood, which would increase the overall risk of fire and increase the intensity and rate of spread of fire generally (as oppose to only during the performance).

    Most correctly insured fire eaters would have as an insurance clause suitable extinguishers, fire blanket and safety assistant (not necessary dedicated but a member of the troupe not performing at the same time as the others and alternating) on hand and risks should be reasonably low.

    Some means of protecting the wood from spills of paraffin to prevent accumulation may be wise.

  5. Not at all. Only CO2 extinguishers require hydro testing in the UK & EU, all the other types, being lower pressure, are specifically exempted from pressure vessel safety regulations.

    (A technical exception to this is if they are renovated by being shotblasted and repainted, but this isn't usually done with non CO2 types anymore as new equipment prices make it not cost effective)

    They do require testing by discharge every 5 years as part of an Extended Service.

  6. If the door was a compliant fire door in the past then assuming the block meets the other fire safety conditions for flats and based on the size of the premises it would be acceptable now under the current guidance.

    If it's not compliant it will be her door and if she refuses to change it then they should be reported to the local authority for enforcement under the Housing Act.

  7. For decades in the past  it was a Building Regulation requirement for certain  internal doors in dwellings (especially flats) to be self closing fire doors, but for a long time now that requirement has been removed and they just need to be fire doors. Most of the time the chains were cut or doors propped so it was considered pointless and better to allow free swing and educate to close at night.

  8. Doors to the outside don't need self closers, internal doors often do. Those inside the flats don't anymore, but the front doors into internal common areas do and have done for a very long time - if your conversion is of a former house it may have been done not in compliance with Building Regulations if they have never been fitted.

    Concealed closers are allowed if to BSEN 1154 & correctly installed - whilst most aren't it is possible to get ones that are.

  9. It doesn't even still meet the 1965 standards if the compartmentation has been breached and the original fire doors in poor order - breaching both the legal requirement to maintain in effective working order and to protect means of escape and mitigate the effects of fire.

    To determine if it's a legal requirement to modernise go through this tree:

    image.png.78da8d68d143668dcd86409de0fc341e.png

  10. Powder would still be appropriate in your premises and still fully within the guidance in BS5306-8 on it's use. It is the best extinguisher for running fires and has a rapid knockdown. You do need to be aware of the damage potential though.

    Certain solvents are known as polar solvents and destroy the foam blanket of standard foam extinguishers so you would need to consult the Material Safety Data Sheets for the materials you use as this may rule out the use of foam (Polar solvent resistant foam extinguishers are available but very expensive)

    The Class B rating on water mist is so poor that the extinguishers cannot be officially marked as suitable for these fires and wouldn't suit your risks. If you don't have polar solvents then there is a Foam Mist extinguisher (https://www.firedepot.co.uk/firechief-multimist-6l-foam-mist-extinguisher).

    If you did use normal foam spray (not mist) then as it stands in the UK you would need CO2 for any electrical risks (most foams aren't marked for electrical fires here)- it's also good for minor spot fires if you do welding as it's non damaging.

×
×