  1. Have you tried hinged covers or alarmed covers yet?

    Unless the Watch Commander is actually from the fire safety department and not just a local station their go ahead is meaningless - I was chatting with a client about  situation where non enforcement officers had given the OK to a situation that was actually dangerous and against all guidance and when the client challenged this with the actual specially trained enforcement officers whose remit fire safety is they agreed it was completely unacceptable and reversed the OK.

    As the fire service no longer have a role in specifying fire safety requirements under current legislation your own fire risk assessment should detail what is needed and why  it's legal - fire officers come and go and saying 'x said it was OK' is no defence against future action. If they made the wrong decision they have no liability - it's your organisation that would still carry the can.

    If the covers don't work there are several other options available. What height were they thinking of moving them to? As it won't readily work as I've seen CCTV of children using chairs or each other to get to fire safety equipment supposedly 'out of reach'

  2. On 24/08/2022 at 20:32, Ali said:

    I live in a maisonette with my own front door and no communal area. However our building is an L shape and in the corner are 3 studio flats with communal area and stair case. All of us in the maisonettes are being asked to pay 108 for the fire assessment and health and safety assessment. I do not think I should be charged this and wondered if someone can answer this for me please

    in the five years I have owned the flat this has never come up before. And we do not pay service charges 

    help please 

     

    This isn't a fire safety matter, more one of property law for which you should consult a specialist lawyer. Are you leasehold or freehold?

  3. 18 hours ago, Hayfever said:

    Of course I understand the rational for this clause, but where green boxes are used to secure a final exit, surely having the external door unlock when the fire alarm operates is a security risk
     

    If intruders create smoke and introduce it into the building at 2am or on a Sunday,, all final exits open and they are in

    There is scope not to have this link in places of detention, certain healthcare scenarios, etc but the default for normal premises is to interface as life is considered more important in the regulatory framework. It's up to the Responsible Person to ultimately decide as legally they carry the can. 

  4. As is sadly too common the service (sales?) engineer has taken a gem of truth and bent it to suit their revenue needs.

    - Fluorosurfactants are now regulated with older versions of foam prohibited (but no extinguisher with these, if serviced and refilled or replaced correctly over the years should still be in service) and the current versions (less damaging, but still persistent enough to be a problem) to be withdrawn, however the timeline isn't out yet.

    - Fluorine free foam extinguishers will come in to replace these, whilst available in Europe for some time they aren't yet on the UK market, but foam will still be an option in future

    - Whilst a small number of water additive extinguishers and some F class extinguishers (usually the ABF rated foams and some ABF rated Wet Chemicals, but not the AF rated ones) do contain fluorosurfactants increasing numbers do not and these would not automatically be affected by any foam replacement timeline.

    - Hydrospray (which is a Chubb Fire trademark) or as generically called Water with Additive extinguishers are not a drop in replacement for Foam or Wet Chemical as they are only suitable for Class A (solids) fires not the Class B (liquid) fires that foam is mainly for or the Class F (cooking oils) fires Wet Chemical is intended for, so is a very poor & even dangerous suggestion for a replacement

    - That having been said, foam has been over sold for decades and many situations don't need it. Unless you have a contained Class B risk you don't need foam and a 6 litre plain water spray provides comparable Class A & 35kV protection to a 6 litre foam

    - A chemical free alternative to Wet Chemical for Class F fires is Water Mist

    - A foam alternative for Class B fires doesn't exist where the risk is contained and in depth (hence why new foams have been developed to replace the current ones) but for shallow, spill and running fires Powder is effective as is CO2 for small indoor risks. Water Mist also has an unofficial Class B rating for small risks (similar to that of CO2)

  5. That is up to the Fire Risk Assessment. A competent assessor would consider layout, occupancy numbers, occupancy type, premises type, number & width of exits, travel distances etc. and be able to decide if this is OK - it's not a simple yes/no as it could be either.

  6. Your fire risk assessment should address this although the standard benchmark guidance would allow this for the shop based on a travel distance under 18m (measured around furniture, fixtures and fittings from the rear of the shop, not a straight line unless it's open plan enough to allow it) and the shop not having over 60 persons in it.

  7. Technically not as the traditional benchmark has a 750mm absolute minimum and BS9999 has an 800mm absolute minimum even though it builds in flexibility. However in existing legacy builds a bit of common sense is required (especially as it's not that far below and the PAS79 FRA methodology allows a bit of leeway) and so the risk assessor should look at the premises, precautions, risk profile and see if they are comfortable justifying the situation in their FRA and that the Responsible Person is happy to accept this.

  8. On 08/08/2022 at 18:20, Guest Med said:

    Hi

    I was asked to wire a magnetic door lock into a fire alarm system, I know that it has to be wired to the fire alarm panel but the company who installed the magnet door lock has mentioned that it can be wire to the nearest call point via an electric interface devise or I/O, is that true? if yes can anyone give me some more info please?  

    The interfacing needs to meet BS7273-4 which most lock/security companies seem to be oblivious of. If you aren't qualified to work on fire alarms you shouldn't really do it.

    I can't attach the standard for copyright reasons, but this extract from building regulations summarises requirements:


    Electrically powered locks should return to the unlocked position in all of the following situations.
    a. If the fire detection and alarm system operates.
    b. If there is loss of power or system error.
    c. If the security mechanism override is activated.


    Security mechanism overrides for electrically powered locks should be a [Green] Type A call point as described in BS 7273-4. The call point should be positioned on the side approached by people escaping. If the door provides escape in either direction, a call point should be installed on both sides of the door.

    image.jpeg.0c8d9b709579dfb5ea698d1e35483ffd.jpeg

    Fire Alarm connections

    1 - Conventional system using control panel's relay
    image.png.7d346434c7230ae76ac572eb4381ca3c.png

    2 - Addressable system using i/o unit on the loop (also requires programming on the panel, not just a physical job)

    image.png.f23d6973eb78fd9226d295bbf951220c.png

  9. The older versions of the standard used to refer to 6 monthly, but as Neil states the current version has shied away from giving advice on intervals and in effect is based on the risk.

    Inspection differs of course - there are user level competence checks of the more basic aspects of a doorset which may be expected to be part of general in house fire safety inspections which are often weekly or monthly and then the more thorough time consuming checks by competent specialists which can vary from 3 - 12 monthly.

  10. On 12/08/2022 at 09:00, Guest manager said:

    morning,i run 54 bedroom home spread over 3 floors,i dont have external fire escape stairs,does the  law reqiure that we do

    It sounds like you don't have a current Fire Risk Assessment carried out by a competent person otherwise you would already have the answer to this - contact a qualified competent fire safety professional to carry out an FRA.

    External stairs were traditionally used where there were not sufficient internal stairs for escape in an existing building or as a cheaper way to add required exit stairs for emergency use only in a new build than a fully enclosed stair.

  11. As it seems to be a building other than a dwelling then the window escape is not an option and it seems the wrong version of Approved Document B is being applied. It reads like a dead end corridor with rooms off for which travel distances are OK based on your info and the only other thing you need is one of the two below solutions:
     

    dead end AFD.jpg

    dead end FR.jpg

  12. On 19/08/2022 at 09:58, Guest Nathaniel said:

    At a place of business I work at, the staff entrance has always been designated as a fire exit in all the years I have been there. To enter when premises is closed to the public, we call a number and a manager let’s us inside. To exit, we press a button and the door opens for us to leave. There is signage on the outside of the door saying it is a fire exit. Recently management have decided it is not a fire exit and is being manually locked whilst the building is still occupied. Is this legal?

    Not without a fire risk assessment that is suitable and sufficient and by a competent person justifying why means of escape is still acceptable without it, usually based on the guidance here: https://www.gov.uk/government/collections/fire-safety-law-and-guidance-documents-for-business

  13. The problem is that you have specified a mix of domestic (BS5839-6) and temporary construction site equipment (no standard compliance) for a finished non residential building and building control are correctly applying the requirement for a commercial grade alarm to BS5839-1 from Approved Document B to the Building Regulations (see below graphic). The construction site call points wouldn't meet the Health & Safety (Signs & Signals) Regulations 1996 either as these require fire alarm signals to have two power sources (not mains only or battery only)

    As a small office you don't need detection so they only require the system to have manual call points and sounders off a control panel (Category M).

    Of course you could simplify things even more (& reduce costs) by not providing any fire alarm as the pod is so small and the following provisions from ADB can apply:
    General provisions

    1.1 All buildings should have arrangements for detecting fire and raising the alarm. In most buildings, fires are detected by people, either by sight or smell, and therefore often nothing more is needed.

    1.2 In some small buildings/premises, the means of raising the alarm may be simple (for example, a shouted warning). In assessing appropriate solutions, warnings need to be heard and understood throughout the premises.

    Conventional Fire Alarm Schematic

  14. The relaxation only applies where:
    a. The top storey of the building is a maximum of 11m above ground level.

    b. No more than three storeys are above the ground storey.

    c. The stair does not connect to a covered car park, unless the car park is open sided

    d. The stair does not serve offices, stores or other ancillary accommodation. If it does, they should be separated from the stair by a protected lobby or protected corridor (minimum REI 30) with a minimum 0.4m2 of permanent ventilation, or be protected from the ingress of smoke by a mechanical smoke control system.

    e. Either of the following is provided for the fire and rescue service.

                                           i. A high-level openable vent with a free area of at least 1m2 at each storey.

                                           ii. A single openable vent with a free area of at least 1m2 at the head of the stair, operable remotely at the fire and rescue service access level.

×
×