Guest Jamie Posted October 24, 2020 Report Posted October 24, 2020 I have an entry fire door which closes with a double chain closer. The door closes very slowly and does not close completely. I have also noticed an intermittent "clunk" from the interior of the door about 10-20 seconds after the door has been closed. I'm guessing this could be the chain bunching up as the door closes, but would be grateful for any advice; particularly whether I should be tightening or loosening the adjusting screw on the frame plate on the right. Quote
Tom Sutton Posted October 27, 2020 Report Posted October 27, 2020 Fire doors should have approved self closing devices to BS EN 1154: 1997 and as far as I am aware all chain types do not conform, consequently you need to change it. Quote
Neil ashdown Posted October 27, 2020 Report Posted October 27, 2020 Some chain closers do conform to BS EN1154 and have controls for adjusting the closing speed and the latching action. The self-closing device in the picture looks similar to the Perkomatic by Samuel Heath. Look for a manufacturers mark on the self-closing device and contact them for the adjustment instructions. Quote
Tom Sutton Posted October 28, 2020 Report Posted October 28, 2020 Neil the only similar type of door closer that I am aware of is the perko powermatic, which dosent use chains, which conforms to BS EN 1154:1997, could you PM me, detail of others that I could research. Quote
Guest Rory Posted October 3 Report Posted October 3 Did you ever find out about these chain closers the reason I ask is I don't want the standard top of door closer in a residential setting for adults with complex needs due to the risk of them using this as a point for suspending themselves for suicide any advice appreciated Quote
Neil ashdown Posted Monday at 11:48 Report Posted Monday at 11:48 Samual Heath at https://concealeddoorclosers.com/powermatic-r100-concealed-door-closer/ New Star at https://www.new-star.co.uk/products/agb-eclipse-self-concealed-hinge-with-door-closer?_pos=1&_psq=self-closer&_ss=e&_v=1.0 Contact them and the door manufacturer to check suitability for your type of door, fire rating and end use. Quote