Fire door gap

Featured Replies

Hi, I've had a builder replace a flat door with an fd30. It strips along the side of the door, but not at the bottom or top I think. Are these required? Also, when it was installed it had a 50mm gap at the bottom. I pointed this out and the builder added some material (assumed hardwood) to bring the gap to 3 mm; is that acceptable? 

 

Thanks for any assistance. 

 

Nick Batchelor 

Doors to flat entrances should be FD30(s).  This means fire and smoke seals should be fitted at the top edge and both vertical edges, the smoke seal should just about fill the gap between the door leaf and door frame without causing hindrance to the self-closing action.

The gap requirement at the threshold is 3mm maximum, for a fire door that should provide cold smoke protection.

On fitting a hardwood lipping to the door bottom edge to reduce the gap, this depends on whether or not this is permitted by the door manufacturers' installation instructions/product data sheet.  Check with the door manufacturer as to whether or not such work will void any fire performance certification applicable to the door leaf.

Edited by Neil Ashdown CertFDI
Additional info

Does every fire door need fire and smoke seals ? 

Not necessarily it depends on the type of fire door required if it is an FD30/60 fire door then a cold smoke seal is not required, if they are an FD30/60s type of fire door then they are. All fire doors to modern standards do require intumescent strips fitted to both sides and the top edge.

Thanks Tom but i'm still a little confused.  So what is the difference between FD30/60 fire door and FD30/60s type of fire door if one requires cold smoke seal and one doesn't ? 

The s suffix designates a fire door requiring a cold smoke seal (brush or fin), usually where escape routes need protecting. Both doors will seal in their frame after exposure to high temperature as the intumescent seal expands, but the door without a smoke seal will let cool smoke through for a period until the room reaches sufficient temperature to activate the intumescent.

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.