October 28, 201312 yr comment_5814 Could you please advise whether all call points have to be the same ? we have a mix of old and new points and our new contractor has said they need changing and must be the same. Can you please advise if this is the case. Many thanks Report
October 29, 201312 yr comment_5819 I have checked BS 3859 -1- 2013 and cannot find any recommendation that require manual call point need to be the same design. There are many recommendations height from the floor, must be easily distinguishable, unobstructed but nothing about the same design. Fire escape signs do state you must not mix different designs but not manual call boxes, ask the contractor to quote the section that require this. Report
October 29, 201312 yr comment_5821 BS5839 currently require that; The method of operation of all manual call points in a system should be that of type A as specified in BS EN 54-11. All call points should be identical unless there is a special reason for differentiation. Report
October 29, 201312 yr comment_5822 Thanks CWEENG I missed it completely you are absolutely correct. Report
October 29, 201312 yr comment_5823 I cant help but wonder. Deborah Hunt, are you asking do all the Manual Call Points have to be identical? (You say a mix of old and new) I would say it depends what you call old and new. Manual Call Points should have a "plastic element" that when pressed activates the alarm. If you still have call points with glass Then, yes these should be changed, BUT if you have differant brands of manual call point, each with a "Plastic element" then so long as they look similar I can not see them being a problem. (Apart from picture size) The above are similar, but NOT identical (Apart from size) If it looks like the one above that has glass, then yes, ideally these should be changed. Report
Join the conversation
You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.