Suspended ceilings in escape routes.

Featured Replies

I have a couple of questions about false/suspended ceilings in escape routes.  Regarding a 30 min protected escape route, how can you tell if a suspended ceiling is FR30? and if it is, why would you need to check above for a breach from, for example, a room off the corridor into the corridor? (with this room also having a FR SC) I've added the picture for clarity and the space above the ceiling is less than 800mm. Any info on suspended ceilings would be helpful, TIA.

False ceiling.png

Most suspended ceiling systems are not fire resisting so unless there is evidence beyond reasonable doubt that it is you check above for the required fire resisting construction.

  • Author
On 13/03/2023 at 21:16, AnthonyB said:

Most suspended ceiling systems are not fire resisting so unless there is evidence beyond reasonable doubt that it is you check above for the required fire resisting construction.

 

Perhaps the suspended ceiling is covered in B2 of ABD, fire spread linings, class 0, 1 etc. I'll have a look.

 

 

  • Author

Thank you.  So, in the illustration, the suspended ceiling does not form part of the 30 minute corridor, however, it is likely to be class 0 as regards to a fire spreading lining? could we say? 

Why would you want 30min fire resisting false ceilings in the accommodation or the protected route? The floor above should be appropriately protected from immediately below the underside with all services run within the same compartment as the accommodation. To do otherwise would require service penetrations into the accommodation from the void to have the same fire resistance as that required by the floor. As is often the case, the services will use the void above the corridor and tee off to the accommodation through the cavity barriers thus requiring the openings to be maintained at 30min. 
Irrespective of the fire resistance of the ceilings, unless the walls of the protected corridor go to the underside of the storey floor above, cavity barriers will be required. Their integrity must be maintained where services pass through otherwise they may as well not be there and any service penetration of the false ceiling in the protected corridor would compromise the corridor. 
I have seen these so-called fire resisting ceilings installed as a quick fix only to find that soon after installation the tiles have been removed or hold down clips discarded. Poor design in my estimation! 
 

  • 2 weeks later...
  • Author
On 15/03/2023 at 22:08, Lyledunn said:

Why would you want 30min fire resisting false ceilings in the accommodation or the protected route? The floor above should be appropriately protected from immediately below the underside with all services run within the same compartment as the accommodation. To do otherwise would require service penetrations into the accommodation from the void to have the same fire resistance as that required by the floor. As is often the case, the services will use the void above the corridor and tee off to the accommodation through the cavity barriers thus requiring the openings to be maintained at 30min. 
Irrespective of the fire resistance of the ceilings, unless the walls of the protected corridor go to the underside of the storey floor above, cavity barriers will be required. Their integrity must be maintained where services pass through otherwise they may as well not be there and any service penetration of the false ceiling in the protected corridor would compromise the corridor. 
I have seen these so-called fire resisting ceilings installed as a quick fix only to find that soon after installation the tiles have been removed or hold down clips discarded. Poor design in my estimation! 
 

Thanks for the response. I didn't make myself clear, the example I saw was not accommodation, and did indeed have service penetrations from the room into the corridor, only noticed when a tile was lifted. My concern with the suspended ceiling is/was, if there's a fire in the corridor, how will the suspended ceiling react? potentially it could collapse. What do you think? 

The corridor is the thing being protected not the accommodation. There may be ignition sources in the corridor, such as electrical services but there should be no fire load that would compromise the route. There would be no reason to have a suspended ceiling in the corridor lest it provides protection to the floor above in which case no services should be brought through it. 
 

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.