Please can anyone give us some advice?

Grade D1/D2 alarms - do they have to be mains powered (with battery back up) or can they be 10-year, sealed, lithium battery powered only?

BS5839-6 seems to suggest that they must be mains powered in some way with options for battery back-up depending on D1/D2.  But can wireless radio-linked devices suffice as a suitable alternative in the guidance?

Link to comment
Share on other sites

Hi Meady

here an overview of the BS5839-6 standard and the grades.

D1/D2 can be interconnected with RF but power-supply has to be by mains power. 

Deviation from the mains power supply requirement would have to come from the specifier. BS5839-6 is a standard, not the law, so if it can be justified, deviations are allowed when specifying the grades for a property.

Harry

 

Link to comment
Share on other sites

On 13/07/2022 at 17:50, Meady said:

Please can anyone give us some advice?

Grade D1/D2 alarms - do they have to be mains powered (with battery back up) or can they be 10-year, sealed, lithium battery powered only?

BS5839-6 seems to suggest that they must be mains powered in some way with options for battery back-up depending on D1/D2.  But can wireless radio-linked devices suffice as a suitable alternative in the guidance?

By definition a Grade D alarm is powered by a 240V supply, the 1 or 2 defining if the back up supply also required to each alarm is a sealed tamperproof battery/cell or a user replaceable battery.

If you only have the built in power supply and no mains then it is only a grade F alarm (which can only be used in a rapidly decreasing number of situations) being a F1 or F2 again  depending if the (sole) power is from a sealed tamperproof battery/cell or a user replaceable battery.

Link to comment
Share on other sites

On 18/07/2022 at 11:17, Harry said:

Hi Meady

here an overview of the BS5839-6 standard and the grades.

D1/D2 can be interconnected with RF but power-supply has to be by mains power. 

Deviation from the mains power supply requirement would have to come from the specifier. BS5839-6 is a standard, not the law, so if it can be justified, deviations are allowed when specifying the grades for a property.

Harry

 

Hi Harry - thank you, that is a great help! ?

Link to comment
Share on other sites

On 18/07/2022 at 20:03, AnthonyB said:

By definition a Grade D alarm is powered by a 240V supply, the 1 or 2 defining if the back up supply also required to each alarm is a sealed tamperproof battery/cell or a user replaceable battery.

If you only have the built in power supply and no mains then it is only a grade F alarm (which can only be used in a rapidly decreasing number of situations) being a F1 or F2 again  depending if the (sole) power is from a sealed tamperproof battery/cell or a user replaceable battery.

Hi Anthony - thank you, I think you've made it clear that we need to be going along the 'D' route.  The 'F' style alarms worry me due to the risk of people simply knocking them off the ceilings if they go off! Thanks as always for your advice - genuinely appreciated.

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...