LUX Level - Emergency Lighting

Featured Replies

Hi All,

A common theme running in FRA reports for our properties (same assessor) is that LUX level reading should be taken to ensure suitable illumination to aid escape.

We have our emergency lighting maintained, drain down test, monthly 'flick test' etc. Is there an expectation that we need to bring in a LUX meter & record measurements?

Thanks

  • 3 weeks later...

This should have been done when the EL was installed and they usually over exceed the required standards but as you are being challanged then I would retest the system and get a written report to prove the case.

  • 1 month later...
  • Author
On 24/04/2022 at 08:52, Tom Sutton said:

This should have been done when the EL was installed and they usually over exceed the required standards but as you are being challanged then I would retest the system and get a written report to prove the case.

Thanks Tom,

It appears to be a 'blanket' statement by the same assessor on numerous properties, especially with non led lighting installed.

I have asked to conduct a visual check during the darker hours to check there is sufficient illumination, although not a LUX level reading, as you mention it was installed to the standard!

On 08/04/2022 at 16:45, Tonyc8310 said:

Hi All,

A common theme running in FRA reports for our properties (same assessor) is that LUX level reading should be taken to ensure suitable illumination to aid escape.

We have our emergency lighting maintained, drain down test, monthly 'flick test' etc. Is there an expectation that we need to bring in a LUX meter & record measurements?

Thanks

This is not a requirement of BS5266 under general testing and maintenance regimes. What the Assessor should of asked (if he or she had reason to) was for the RP to confirm the emergency lighting system delivered the correct light levels to aid escape. At which point the RP can refer to the original design specification and the photometric survey which should of been done at that time. A common mistake with lesser competent designers is the increase LUX level for certaina reas of the building, for instance, around critical firefighting or alarm systems.

  • 2 weeks later...
  • 2 weeks later...
On 09/06/2022 at 19:29, delboy said:

If there is a Stay Put policy in place in a PB block, is this necessary??

Its emergency lighting not fire lighting, there may be other power failure causes where someone needs to safely navigate the stairs, also even in stay put premises there is often a need to evacuate other than the fire flat.

That's why both regulations and guidance require it's provision as well as it being subject to a system of maintenance and being fit for purpose.

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.