  1. Hi Susie

    In line with BSI standard BS EN 50291-1:2018 a CO detector must not alarm at low CO levels for a specific period of time.

    So, for example at a relatively low CO concentration of 30 to 50ppm the alarm must not go off for 120 minutes and in actual fact it does not have to go off at all!

    At just over 50ppm it is not allowed to sound alarm for 60 minutes but will have to sound alarm within 90 minutes.

    Odd, I know!

    If you have low level carbon monoxide presence in your building (let's say 40ppm), your CO detector will take at least two hours before alarming! So when you disable the alarm this clock starts ticking again and you will not hear the alarm sounding for quite a while.

    It is therefore not a great idea to disable a CO alarm. The CO alarm probably did what it is supposed to do and warned you about CO presence.

    If you would like to see the actual CO concentrations, especially at low level exposure, I would recommend getting a digital CO alarm. The Fireangel CO9D has both a display for readings over 10ppm as well as peak reading display, so you can see what the highest reading was in the last few days.

    Harry

  2. Hi

    TO SET THE PERSONAL CODE

    1. Press the # button.
    2. Press the green code change button located on the back of the safe door
    3. Enter your personal 3 to 6 digit code and press # button to set.
    4. The lock will emit a tone and the LCD will display IN. to confirm the new code.
    5. To change the code follow the same procedure with the door and lock in the open position.

    This lock can be programmed with an 8 digit master code;
    which cannot be removed, but can be edited. Consider carefully
    if you require this function before entering a second code.

     

    TO SET THE MASTER CODE

    1. Press the # button
    2. Enter 0,0
    3. Press the green code change button.
    4. Enter the selected 8 digit master code.
    5. The lock will emit a tone and the LCD will display IN. to confirm the master code.

    test before you close the door

     

    Harry

  3. Hi John

    Please make sure there is no other alarm in the vicinity. It would be unusual for the alarm to beep every 5 minutes. It is only beeping every 40 seconds when eg the battery is low, so there is probably a different alarm with low battery nearby. Maybe a carbon monoxide alarm.

    Harry

  4. Hi

    If this carbon monoxide alarm is a Fireangel CO9D alarm with digital display, it records peak carbon monoxide (also shortened to 'CO') levels which can be queried by pressing the Test button. It displays the highest recording and then resets itself. Your alarm is telling you that it recorded 227ppm which is high.

    I would avoid using the gas dryer until you have found out whether it is leaking any CO gas into the building.

    Harry

  5. Hi Elisa

    I assume this is in a domestic property. I would expect either the alarms being too old (please check the replacement date on them) or there being a tiny spider or a bit of dust in the alarm. It helps sometimes to use the vacuum around the openings of the alarm to resolve this.

    If you let me know the model of the alarm or send a photo via this platform I might be able to help better.

     

    Harry

     

  6. Hi,

    Maybe it was a short term spike. If it was a Fireangel digital CO alarm you can get a peak reading by pressing the test/mode button. This should hopefully also show zero.

    Certain chemicals can also set off a CO alarm (new floor screed, vented car/boat batteries being charged etc).

    Check the replacement date as well to make sure the alarm is not overdue for replacement.

    What model alarm do you have?

     

    Harry

     

×
×