Jump to content

Dead Ends


DanHenry

Recommended Posts

Basic question...

Office corridor, MoE one end and at midway point, meaning there is a dead end of maybe 12 metres. Four or five offices along the dead end. The two remedies I understand however, do you extend the solution the full length of the corridor or just within the dead end area to the midway point MoE? So for example detection on all office along the full length of corridor or just offices in the dead end part of corridor?

Thanks,

Link to comment
Share on other sites

If there is a cross corridor FD30s door across the corridor at the point the dead end starts then I would consider it meets the guidance.  Anywhere the corridor  has an alternate MoF escape and is within the travel distances then fire doors would not be required. 

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...