Meady Posted May 28, 2021 Report Share Posted May 28, 2021 Please can someone tell me if all hatches to lofts / voids which form part of ceilings along means of escape (protected corridors and stairs) need to be fire rated or not? We cannot see anything in ADB Vol 2 which specifically mentions this so any steer would be much appreciated! ? Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted May 29, 2021 Report Share Posted May 29, 2021 The walls, floor, vertical shafts and ceiling all form the protected route and should achieve the required fire resistance. Not everything will appear in guidance or regulations you have to use common sense and your experience. For instance if the hatch to a loft is in a staircase then you need to conduct a fire risk assessment to ascertain the hazard of a fire in a flat or loft space spreading to the staircase and making it impassable. Quote Link to comment Share on other sites More sharing options...
Meady Posted May 30, 2021 Author Report Share Posted May 30, 2021 That's great - thanks very much Tom. Quote Link to comment Share on other sites More sharing options...