May 11, 20215 yr comment_20070 Hello everyone, I wonder if you could give me some advice. We are a block of 5 flats: 2 on the ground floor. 2 on the first floor and 1 on the top floor. We have a very simple entrance way with ceiling to floor windows and flights of stairs up to each floor where there is also ceiling to floor windows....so lots of natural light during the day and lots of borrowed light from very bright street lights at night time. What are the regulations/requirements for emergency lighting please? Many thanks in advance. Lucy Report
May 15, 20215 yr comment_20109 If you can prove that the level of borrowed light will provide the necessary level and availability during all relevant times, then emergency lighting should not be required. Report
May 16, 20215 yr comment_20120 You would have to check that the street lighting was on as required as local authorities are reducing the lighting up times for street lights and are bringing in LED fittings that cast their light differently to the old sodium lights and no longer provide sufficient light. It's a common retrofit, but the guidance does state that it's a low priority in small blocks and other issues take precedence. Report
October 13, 20214 yr comment_21971 Anthony B - pls could you confirm which guidance states that it's a low priority and other issues take precedence as we are a similar premises 3 floors, 8 flats. thanks Report
October 20, 20214 yr comment_22040 The existing (outgoing) fire safety in purpose built flats guide states this. It's draft replacement for small blocks (G-2) takes a similar approach, I'm not sure what it's replacement for large blocs will says although it's normally required for large blocks regardless of borrowed light, but secondary to issues such as fire doors (so they could be done later on in another budget period) Report
Join the conversation
You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.