Foam extinguishers on Electrics


Guest Sean

Recommended Posts

Hello, looking at some AFFF Foam extinguisher and some advice states passed die-electric test to 35kV ( 35,000 volts) but lots of advice states "Safe up to 1000v at 1 metre"  Which is it, 35000 or 1000 

Link to comment
Share on other sites

If we were anywhere else in Europe they would all say "Safe for direct use on electrical equipment up to 1000v at 1 metre" after passing a safety test that ensures a suitable resistance in the discharge stream when sprayed on a metal plate with 35,000V running through it because the manufacturing standard EN3 says this.

The UK trade doesn't like this as it stops them selling extra extinguishers for electrical fires (really!) so many brands omit the 'safe for direct...' phrase and just rattle on about a 35,000V conductivity test (which will mean nothing to most users) even though the same manufacturing standard is used, although some models (Water Mist, P50 Triclass) do follow the correct 'safe for direct use...' marking. Others vary batch to batch!

The 1000V is partly to give a margin and partly because there are general hazards with high voltage fires such that only specialist personnel should be dealing with them  

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...