January 16, 20188 yr comment_11326 Hi - I am trying to establish whether one of our landlords needs to do weekly testing and also the frequency of testing for the alarm panel and emergency lighting. They own a 2 storey Victorian property which has been converted into 3 separate dwellings (bedsits) the tenants only share the communal corridor. Many thanks. Helen Report
January 17, 20188 yr comment_11336 Fire alarm - weekly testing using different call points in rotaton; 6 monthly service by a competent person with 100% of the system tested over a 12 month period Emergency lighting - monthly function ('flick') test of all fittings; annual duration (usually 3 hours) test of all fittings. (Don't be conned into a 1 hour part duration test at 6 months, it hasn't been required since 2004 and only wears out the lighting quicker) Report
January 18, 20188 yr comment_11339 Could you give the details of the type of fire alarm are you talking about. Report
January 18, 20188 yr comment_11342 I've assumed that because there is a panel referred to that it's a Part 1 or Part 6 grade A system Report
January 19, 20188 yr comment_11346 I fully understand that AB but what I do not understand why a Grade A in a two storey premises I do not think Lacots would agree. Report
January 19, 20188 yr comment_11348 From my experience regardless of AD B, LACORS, LGA Guide, etc residential of various flavours seems to invariably get a Part1 or Grade A system regardless of the set up! Could have been a requirement of the BCO or AI too! Report