August 29, 20169 yr comment_9169 Hi Please could you advise if there is any Government legislation relating to cleaning kitchen extraction regularly to prevent fire hazard from the build up of grease? Kind regards Christina Report
August 30, 20169 yr comment_9190 Article 10 and Schedule Part 3 - Principles of Prevention. Whilst not explicit (few things are, the legislation sets out broad requirements, not the detail of how to achieve them), the cleaning of duct work would be a means of avoiding or combating fire risks as required by the legislation. There are plenty of destroyed workplaces that prove the need for such precautions. Report
September 1, 20169 yr comment_9195 When you have it carried out it's a good idea to have it certified in accordance with TR/19. They will also be able to advise you on frequency and how to do it properly. Such as low 2-6 hours (12 months) moderate 6-12 hours (6 months) and high usage 12+ (3 months). This is also evidence to satisfy the above article. Report
September 2, 20169 yr comment_9200 May give some idea what is required http://ductdevil.com/TR19 HVC Sample.pdf and http://ductdevil.com/TR19%20HVCA%20Internal%20Cleanliness%20of%20Ventilation%20Systems.pdf Report