April 24, 201511 yr comment_7391 Hello, I hope you could are able to help me. I would like to find out if there is any protocol on where the fire blankets should be kept in the kitchen area of a commercial property? Many thanks, Kristina Report
April 24, 201511 yr comment_7399 Fire blankets should be available for immediate use at all times and should be located · in conspicuous positions on brackets; · where they will be readily seen by persons following an escape route; · most suitably, near to room exits; · in similar positions on each floor, where floors are of similar appearance. Fire blankets should not be located, · where a potential fire might prevent access to them; · in concealed positions behind doors, in cupboards or deep recesses; · where they might cause obstruction to exit routes; · in positions in rooms or corridors away from exit routes unless they are necessary to cover a particular hazard. The position and type of a fire extinguisher should be indicated on a sign so that, if the extinguisher is removed, this can be identified during a safety inspection, and a replacement ordered. Report
May 21, 201511 yr comment_7500 Fire blankets are only really intended for small equipment using cooking oils (chip pan & similar) and a rule of thumb is that if your Class F risk involves more than 3 litres of oil or a container over 300mm diameter then you really should have the required number of F-rated Wet Chemical or Water Mist extinguishers (or even a fixed system for the larger ranges) Report