Do you need fire door seals on final exit door?

Recommended Posts

Guest BarryAve

Can you please advise me if fire door seals should be fitted to a final exit fire door, as logic tells me no, because if the seals swell in heat the door would not open and trap people in a fire.
Also could you please advise me if there is a minimum width of an final escape door.
Regards
Barry

Share this post


Link to post
Share on other sites

You are right about the door seals on final exit doors, but not for the reason you stated it is because final exit door do not need to be fire resistant. The heat required to operate the seals nobody could exist in the area so they would not be trying to get through the door. The width of the door depends on the number of people who would be required to use it in an emergency. For more information on means of escape got to http://www.firesafe.org.uk/basic-means-of-escape-from-fire/

Share this post


Link to post
Share on other sites

I agree fully but as a general rule, final exits doors usually do not need to be FR and there is bound to be other exceptions to the rule.

Share this post


Link to post
Share on other sites
Guest Charlie

Hi quick question with regards to fire exits. Do they have to have smoke seals? Also does the glass have to be fire rated glass? 

Share this post


Link to post
Share on other sites
Guest Red Adair

Quesion please?

Does it matter if final exit doors are not a good fit if they open directly into a place of safety and there are no other considerations?  For example, have a gap at the bottom?

Also, could I have the legal reference please for the requirement for the intumescent/smoke seals  on final exit doors if opening below an escape staircase?

Thanks,

Share this post


Link to post
Share on other sites

Final exit door do not need to be fire resistant door in most cases, therefore the gaps are not specified. Any final exit doors within certain distances of an external fire escape need to be FD30 fire doors, Check out https://www.firesafe.org.uk/regulatory-reform-fire-safety-order-2005/ depending if it is an office, shop, factory etc look at the appropriate guidance.    

Share this post


Link to post
Share on other sites
Guest peter

I work in a school and in the kitchen there is a fire exit door that leads to open space, does this need to be a fire rated door ?

Share this post


Link to post
Share on other sites

Not unless there's an external escape stair nearby or an external escape pathway that you can only get to safety by passing the door and would be within a metre or two max if it.

Share this post


Link to post
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...

×
×
  • Create New...